18-LD1770428-PDA-optimized
Model(s): Roxtec S Series Frames in Steel Divisions
Product Design Assessment (PDA) 18-LD1770428-PDA 11-JUN-2019 10-JUN-2024
Multi and single pipe penetrations in Class A0, A15, A30 and A60 bulkheads and decks. Penetrations of
watertight and gastight steel bulkheads and decks up to the specified pressure.
“Roxtec pipe sealing system with multidiameter technology” consisting of Roxtec S series frames (S, SO,
SF, SFO, SR, SK, SKR, SRC r20&r40 and BTB) in sizes 1-8 and combinations thereof, bolted or welded
on to the steel sections, filled with Roxtec (standard, Ex or EMC) halogen free insert modules.
Assembled with Roxtec Wedge Kit (Standard, Ex or EMC).
a) Maximum tested size of steel and copper pipes: 50 mm OD for steel Pipe and 54 mm OD for Copper
Pipes
b) Maximum tested size of Bundle pipes/ multi core tubes (in stainless steel and copper versions): 50
mm OD for steel / 20 mm OD for copper
c) Maximum tested frame size:
02/13/2024 12:50:45 AM Copyright 2019 American Bureau of Shipping. All rights reserved. Page 1 of 4
Certificate Number: 18-LD1770428-PDA
1) Single - 8x1 ( One frame of size 8)
2) Multiple Frames - see Below
For decks up to A60 rating, two frames of size 8 arranged vertically and seven arranged horizontally,
designated S 8+8x7.
For bulkheads up to A60 rating, two frames of size 8 arranged vertically and ten arranged horizontally,
designated S 8+8x10.
d) Minimum Tested Frame Size 1x1 ( size 1 Frame)
e) Class A-0, A-15 and A-30 shall be insulated as class A-60 and in addition the division is to be
insulated at least 200 mm around the penetration
f) Not for use in tank boundaries
g) For detail information about insulation arrangement, please see ABS approved drawings specified in
the Notes, Drawings and Documentation section of this Certificate.
h) Unit Certification is not required for this product. If the manufacturer or purchaser requests an ABS
a) All seal types should be installed in accordance with manufacturer’s instructions in accordance with
approved drawings: S1534291, S1011073, & 1011074.
b) Watertight bulkheads or decks for pipe penetrations are to be examined and tested as per ABS
Marine Vessels Rules 3-7-1/Table1.
penetration system has to comply with the requirements given in SOLAS Ch. 11-1 Reg. 13.2.3 (2014
Consolidated Edition). This approval of penetrations passing through watertight bulkhead is not to be
construed as a substitute for flag Administration’s approval for the purpose of SOLAS (2014
  1. CTO Fire Test Report Number RS-17/B-395/E dated 30 October 2017 and RS-18/B-485/E dated 10
December 2018
  1. SP Fire Test Report Numbers P602999 and P603000 (Both dated 23 January 2007)
  2. Multiple sizes, reference fire test reports 6P02516 dated 29 August 2016 & P402000 dated 29
November 2004
4) Roxtec sealing system, Roxtec product sheet
5) Roxtec Ex sealing system, Roxtec Product sheet
  1. DNV Watertight and Gastight Test Report MLM020133, dated 26 February 2002, MLM 020400 Dated
25 March 2002
Drawings:
Drawing No. S1534291 Revision: A, S- Series Frames With Steel Pipes A- Class Steel Bulkhead/ Deck
02/13/2024 12:50:45 AM Copyright 2019 American Bureau of Shipping. All rights reserved. Page 2 of 4
Drawing No: S1011073 Rev - , S- Series Cu- Pipes Insulation A- Class Division
Drawing No: 1011074 Rev. - S- Series Bundle Pipes Insulation A- Class Division
This Product Design Assessment (PDA) Certificate 18-LD1770428-PDA, dated 11/Jun/2019 remains
valid until 10/Jun/2024 or until the Rules or specifications used in the assessment are revised (whichever
occurs first).
This PDA is intended for a product to be installed on an ABS classed vessel, MODU or facility which is in
existence or under contract for construction on the date of the ABS Rules or specifications used to
evaluate the Product.
Use of the Product on an ABS classed vessel, MODU or facility which is contracted after the validity date
of the ABS Rules and specifications used to evaluate the Product, will require re-evaluation of the PDA.
Use of the Product for non ABS classed vessels, MODUs or facilities is to be to an agreement between
the manufacturer and intended client.
ABS Marine Vessels Rules 2019 1-1-4/7.7, 1-1-A3, 1-1-A4, 4-6-2/9.7, 4-8-4/21.13.1
ABS Mobile Offshore Units Rules 2019 1-1-4/9.7, 1-1-A2, 1-1-A3, 4-2-1/11.15, 4-3-3/5.13.1
SOLAS (Consolidated Edition 2014) Chapter II-2 Reg. 9.3.1
A8706-1 RDIMS#1961446 dated 15 November 2006
Print Date and Time: 13-Feb-2024 12:50
02/13/2024 12:50:45 AM Copyright 2019 American Bureau of Shipping. All rights reserved. Page 3 of 4