52630_A0 BV-optimized
Certificate number: 52630/A0 BV
File number: ACI 4010/030/006
Product code: 5301H
This certificate is not valid when presented without the
full attached schedule composed of 7 sections
Roxtec sealing system: Roxtec SPM seal series in Aluminium divisions
SOLAS 74, as amended, Regulations II-2/9.3.1
IMO Res MSC.307(88) (2010 FTP Code)
This certificate will expire on: 24 Sep 2023
At BV GOTHENBURG, on 24 Sep 2018,
Magne MOLLER
BV Mod. Ad.E 530 June 2017 This certificate consists of 3 page(s)
1. PRODUCT DESCRIPTION :
“Roxtec SPM seal series for steel and copper pipes in Aluminium divisions”
The Roxtec SPM seal series consists of :
  • circular rubber seal (in sizes 39-279 for steel pipe and in sizes 39-157 for copper pipes), and,
  • circular front and rear steel fittings (bolted compression plates)
The Roxtec SPM seal is neither welded, neither bolted to the division (maintained through expansion to the division with the
bolted compression plates).
The Roxtec SPM seal shall be fully insulated on both sides for bulkheads, and at least on underside for decks.
The pipe itself is insulated on both sides and/or one side with length and thickness as shown on Insulation drawings (see below
table & §2).
Tests carried out with mineral wool Paroc Marine Wired Mat 100 (density 100 kg/m3).
Penetration Pipe Pipe Outer Seal size range Insulation drawing
type material diameter
| SPM seal series | Steel Pipe | 8 to 222 mm | 39 to 279 | Blkhd: S1529741, rev A, dated 2018-01-25 |
| (Deck & Blkhd) | (Deck & Blkhd) | Deck: S1529743, rev A, dated 2018-01-25 |
| SPM seal series | Copper Pipe | 8 to 111 mm | 39 to 157 | Blkhd: S1529742, rev A, dated 2018-01-25 |
| (Deck & Blkhd) | (Deck & Blkhd) | Deck: S1529746, rev A, dated 2018-01-25 |
  1. DOCUMENTS AND DRAWINGS :
  • Insulation Drawings S1529741, rev A, S1529743, rev A, S1529742, rev A and S1529746, rev A, all dated 2018-01-25
- Information Drawing S1502970, rev D, dated 2015-04-10
3. TEST REPORTS :
3.1- Test report in Aluminium bulkhead : N° RS-17/B-209/E, dated June 2, 2017, from CTO, Poland.
3.2- Test report in Aluminium deck : N° RS-17/B-210/E, dated June 2, 2017, from CTO, Poland.
All test reports being as per IMO FTP Code 2010 Annex 1 Part 3.
4. APPLICATION / LIMITATION :
4.1- The fitting aboard to be the same as used for the test.
4.2- Not for use in tank boundaries.
4.3- Alternative non-combustible mineral wool : The fire tests were conducted with mineral wool type Paroc Marine Wired Mat
100 (density 100 kg/m³); any type approved A-class insulation of similar type giving at least an equivalent insulation
performance can be used.
4.4- Approved for use as steel or copper pipe penetrations in A-0, A-15, A-30 and A-60 class aluminium divisions (with
insulation arrangement as per § 1 & 2).
5.1-The SPM seals are to be supplied by Roxtec International AB in compliance with the type described in this certificate.
5.2-This type of product is within the category HBV of Bureau Veritas Rule Note NR320 and as such does not require a BV
5.3- Roxtec International AB has to make the necessary arrangements to have its office and production site(s) recognised by
Bureau Veritas in compliance with the requirements of NR320 for HBV products.
The product or packing is to be marked with manufacturer name, type designation and fire technical rating.
7. OTHERS :
7.1- It is Roxtec International AB’s responsibility to inform shipbuilders or their sub-contractors of the proper methods of
7.2- Watertightness and Gastightness for SPM seals: Inspection report N° N1419WS4, dated June 21, 2016 and N° N141805A,
dated December 20, 2016, both from DNV-GL:
• Tested watertightness : 1,5 bar during 60 min.
• Tested gastightness : 1 bar during 30 min.