Doc_75513_1-optimized
CERTIFICATE OF FIRE APPROVAL
This is to certify that
The product(s) detailed below will be accepted for compliance with the applicable Lloyd’s Register Rules and
Regulations for use on offshore installations classed with Lloyd’s Register, and for use on offshore installations
when authorised by contracting governments to issue the relevant certificates, licences, permits etc.
| Address | Box 540 |
S-371 23 Karlskrona
Type CABLE PENETRATION (HYDROCARBON FIRE TEST)
| Equipment Description | Fire Resisting Circular Multiple Cable Penetration – Type: “Roxtec R frames” for |
restricted applications in H-60 and H-120 Class steel bulkheads and decks
Specified Standard IMO Fire Test Procedures Code, Annex 1, Part 3
EN 1363-2 Hydrocarbon Time Temperature Curve
Date of issue 7 March 2016 Expiry date 6 March 2021
| Certificate No. | SAS F160139 | Signed |
Fire & Safety, MTES
Lloyd’s Register EMEA
LR427.2013.12
Sheet No 1 of 3 Name S. Abraham
Surveyor to Lloyd’s Register EMEA
A Member of the Lloyd’s Register Group
Note:
This certificate is not valid for equipment, the design or manufacture of which has been varied or modified from
the specimen tested. The manufacturer should notify Lloyd’s Register of any modification or changes to the
Page
2 of 3
71 Fenchurch Street, London, EC3M 4BS Document number
Telephone 020 7423 2416 Fax 020 7423 2053 SAS F160139
Email med@lr.org Issue number
DESIGN APPRAISAL DOCUMENT
Date Quote this reference on all future communications
6 May 2016 MTES/SFS/TA/SA/WP25742200
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. SAS F160139
APPROVAL DOCUMENTATION
Danish Institute of Fire and Security Technology, Test Report No. PG11087 dated 12 February 2003.
Danish Institute of Fire and Security Technology, Test Report No. PG11088 dated 18 February 2003.
Det Norske Veritas, Malmo, Watertightness and Gastightness Test Report Nos. MLM 010238 dated 30
August 2001.
1. When used in conjunction with H-60 and H-120 Class bulkheads and decks, when insulated with
approved arrangements suitable for the required rating on the fire hazard side (restricted applications)
2. For applications in H-0 and H-0 (400°C) Class steel bulkheads and decks, penetrations are to be fitted
with the same or equivalent H-120 Class insulation arrangements as those used in the fire tests
(including any insulation fitted on the penetration itself in the tests) for a minimum distance of 450mm
around the penetration, on all fire risk sides in bulkheads and decks and insulation should be extended
to cover the full side(s) and the end face(s) of the steel frame, with an overlap of at least 20mm from the
steel edges
3. The above mentioned H-120 Class insulation arrangements should be additional to any thermal or
acoustic insulation, but may include any fire rated insulation (e.g. H-60) already fitted on the bulkhead
or deck and/or on the penetration itself, such that the total fire rating is H-120
4. Frame types: R frames
5. Frame sizes: 70-200
6. Consisting of: circular steel sleeves (welded or bolted) with R-type (EMC versions included) halogen
free rubber frames and filled with Roxtec halogen free insert modules, mounted to the non-fire exposed
side in steel bulkheads and non-fire exposed side (top side) in steel decks
7. Production items are to be manufactured in accordance with a quality control system which shall be
maintained to ensure that items are of the same standard as the approved prototype
NOTES
1. The penetration types R 70 and R 200 were subjected to gas overpressure with a value of 4.0 bar for a
duration of 30 minutes, as detailed in report Nos. MLM 010238.
2. The penetration types R 70 and R 200 were subjected to a hydrostatic pressure test for 60 minutes at 6.0
bar without any leakage, as detailed in report Nos. MLM 010238.
Page
3 of 3
S-371 23 Karlskrona
Fire & Safety, MTES
LR427.2013.12
Saji Abraham
Senior Specialist
Statutory Fire & Safety