TYPE APPROVAL CERTIFICATE
No. LAB180318CS/002
This is to certify that the product identified below is in compliance with the regulations
herewith specified.
| Description | Devices for the passage of electric cables through A or B |
|---|---|
| Class divisions | |
| Type | Roxtec S Series - Steel Deck |
| — | — |
| Applicant | ROXTEC INTERNATIONAL AB |
| ROMBVAGEN 2, P.O. BOX 540 | |
| SE-37123 KARLSKRONA |
SWEDEN
| Manufacturer | ROXTEC INTERNATIONAL AB |
|---|---|
| Place of manufacture | ROMBVAGEN 2, P.O. BOX 540 |
| SE-37123 KARLSKRONA |
SWEDEN
| Reference standards | IMO Res. MSC.307(88)-(2010 FTP Code) |
|---|
Issued in Genoa on December 19, 2018. This Certificate is valid until December 18, 2023
RINA Services S.p.A.
Enrico Cabella
This certificate consists of this page and 1 enclosure
RINA Services S.p.A.
Via Corsica, 12 - 16128 Genova - Italia
Tel. +39 010 53851
Fax. +39 010 5351000
TYPE APPROVAL CERTIFICATE
No. LAB180318CS/002
Enclosure - Page 1 of 2
Roxtec S S eries - S teel Deck
Product description
Devices for the passage of electric cables having diameter ranging from 10 up to 86 mm through A Class decks. The
transits are composed of a steel frame having thickness of 10 mm fillet welded to the deck plate and filled with EPDM
halogen free material packing system; on the upper part it is installed one module fitted with a screw expander. The
deck is insulated by means of two layers of mineral wool (certified non combustible in compliance to 2010 FTP Code)
50+30 mm thick and having density of 125 kg/m3.
Reference documents
Roxtec drawings enclosed in SP Test Reports No. 6P02249 dated 17 August 2016, No. 6P07563 dated 20 December
2016, No. 6P10022 dated 7 March 2017 and Research Institute of Marine Engineering Test Report No. 09-346 dated 11
December 2009.
Tests carried out
Tests as per SP Test Reports No. 6P02249 dated 17 August 2016, No. 6P07563 dated 20 December 2016, No.
6P10022 dated 7 March 2017 and Research Institute of Marine Engineering Test Report No. 09-346 dated 11
December 2009 issued according to IMO 2010 FTP Code and IMO Res. A.754 (18).
General conditions for the approval
a) The initial conditions verified by RINA at the time of the approval are to be maintained
b) Any changes to the initial conditions are to be promptly communicated to RINA, which reserves the right to repeat the relevant
assessment
c) This certificate will no be valid if the manufacturer makes any changes or modifications to the approved equipment, which have not been
notified to, and agreed with RINA
d) RINA personnel are to allowed to witness during the performances of activities, upon their request
e) The activities are to be carried out in compliance with the RINA Rules and/or other applicable Rules
f) Should the specified regulations or standards be amended during the validity of this certificate, the product is to be reapproved prior to it
being placed on board vessels to which the amended regulations or standards apply.
RINA Services S.p.A.
Via Corsica, 12 - 16128 Genova - Italia
Tel. +39 010 53851
Fax. +39 010 5351000
TYPE APPROVAL CERTIFICATE
No. LAB180318CS /002
Enclosure - Page 2 of 2
Field of application
Fire resistant A-60 Class cable transits through A Class decks as per following table:
| TYPE OF TRANSITS | Fill | Cable diameter | ADDITIONAL | TRANSIT FIXING |
|---|---|---|---|---|
| % | INSULATION | AND NOTES | ||
| SRC r20 8x1 | 21 | from 10 up to 86 mm | No additional | Penetr. fix. to deck |
| insulation | plate in the middle. | |||
| SRC r20 2x1 | from 4 up to 18 | from 10 up to 86 mm | No additional | Penetr. fix. to deck |
| insulation | plate in the middle. | |||
| SRC r60 4x1 | 1 | 10 mm | No additional | Penetr. fix. to deck |
| insulation | plate in the middle. | |||
| S 1x1 | 3 | 10 mm | No additional | Penetr. fix. to deck |
| insulation | plate in the middle. | |||
| SRC r40 8x1 | 31 | from 31 up to 53 mm | Mineral wool, two | Penetr. fix. to deck |
| layers 30 mm thick plate on exposed side; | ||||
| each, density of 125 addit. insul. fitted on | ||||
| kg/m3, width of 100 | deck insul. side. | |||
| — | — | |||
| mm all around | ||||
| S 1x1 | 26 | 45 mm | Mineral wool, two | Penetr. fix. to deck |
| — | — | — | — | — |
| layers 30 mm thick plate on exposed side; | ||||
| each, density of 125 addit. insul. fitted on | ||||
| kg/m3, width of 100 | deck insul. side. | |||
| — | — | |||
| mm all around | ||||
| S 8+8x3 | 28 | from 21 up to 53 mm Min. wool, two layers Penetr. fixed to the | ||
| — | — | — | ||
| 30 mm thick each, deck plate on exposed | ||||
| density of 125 kg/m3, side; the additional | ||||
| width of 100 mm all insul. is fitted on deck | ||||
| around and on the | insulated side. | |||
| — | — | |||
| modules with a screw | ||||
| exp. | ||||
| S 8x1 | 31 | from 21 up to 53 mm | Mineral wool, two | Penetr. fix. to deck |
| — | — | — | — | — |
| layers 30 mm thick plate on exposed side; | ||||
| each, density of 125 addit. insul. fitted on | ||||
| kg/m3, width of 100 | deck insul. side. | |||
| — | — | |||
| mm all around | ||||
| SF 8x1 | 31 | from 21 up to 53 mm | Mineral wool, two | Penetr. fix. to deck |
| — | — | — | — | — |
| layers 30 mm thick plate on exposed side; | ||||
| each, density of 125 addit. insul. fitted on | ||||
| kg/m3, width of 100 | deck insul. side. | |||
| — | — | |||
| mm all around |