LAB220921CS-001-optimized
No. LAB220921CS/001
divisions
Type Roxtec SPM
ROMBVAGEN 2, P.O. BOX 540
SE-37123 KARLSKRONA
Place of manufacture ROMBVAGEN 2, P.O. BOX 540
SE-37123 KARLSKRONA
Issued in Genoa on July 30, 2021. This Certificate is valid until July 29, 2026
No. LAB220921CS/001
Enclosure - Page 1 of 5
Roxtec S PM
ROXTEC SPM ON BULKHEAD
Circular pipe penetrations named SPM, composed of highly elastic EPDM rubber and fittings of stainless steel and
having diameter ranging from 39 mm (type SPM 39) up to 279 mm (type SPM 279). The bulkheads are insulated by
means of two layers of mineral wool 30 and 50 mm thick and having density of 100 kg/m3. The division insulation
covers also the transits that may be fitted with additional insulation, laid upon the bulkhead insulation, consisting of
mineral wool discs having the same thickness of the bulkhead insulation and /or mineral wool cylinders equipped with
steel wire.
Fire resistant A-60 Class metallic pipe penetrations through steel bulkheads as per following tables:
COPPER
TYPE OF TRANSITS - PIPE ADDITIONAL INSULATION TRANSIT
DIAMETER FIXING AND
NOTES
Transits from SPM 39 up to SPM Mineral wool disc having width of 100 mm and mineral wool Seal fitted on the
81 - pipe diameter from 12 mm up cylinder having length of 400 mm and thickness of 50 mm exposed or
to 45 mm unexposed side.
Transits from SPM 81 up to SPM Mineral wool disc having width of 200 mm and mineral wool Seal fitted on the
138 - pipe diameter greater than 45 cylinder having length of 600 mm and thickness of 50 mm exposed or
mm up to 92 mm unexposed side.
Transits from SPM 138 up to SPM Fitted on both sides and composed of mineral wool disc Seal fitted on the
279 - pipe diameter greater than 92 having width of 200 mm and mineral wool cylinder having exposed or
mm up to 220 mm length of 700 mm and thickness of 100 mm unexposed side.
No. LAB220921CS /001
Enclosure - Page 2 of 5
STEEL
TYPE OF TRANSITS - ADDITIONAL INSULATION TRANSIT FIXING AND NOTES
PIPE DIAMETER
Transit SPM 41 - pipe No additional insulation Seal fitted on the unexposed side.
diameter 12 mm
Transit SPM 41 - pipe No additional insulation Seal fitted on the exposed side. The
diameter 16 mm seal fitted on the unexposed side
satisfy only the requirement of the
A30 Class
Transits from SPM 39 up to Mineral wool cylinder having length of 300 mm Seal fitted on the exposed or
SPM 81 - pipe diameter and thickness of 50 mm unexposed side
from 12 mm up to 45.4 mm
Transits from SPM 81 up to Mineral wool disc having width of 200 mm and Seal fitted on the exposed side.
SPM 138 - pipe diameter mineral wool cylinder having length of 400 mm
greater than 45.4 mm up to and thickness of 50 mm
92 mm
Transits from SPM 138 up Fitted on both sides and composed of mineral Seal fitted on the exposed or
to SPM 279 - pipe diameter wool disc having width of 200 mm and mineral unexposed side.
greater than 92 mm up to wool cylinder having length of 500 mm and
220 mm thickness of 100 mm
Roxtec drawings included in SP Reports No. 5P03451 dated 3 November 2015, No. 5P08346 dated 21 December
2015, No. 5P05990 dated 16 November 2016, No. 5P07565 dated 20 December 2016 and DBI Report No. PGA10870A
dated 13 December 2016.
Tests as per SP Reports No. 5P03451 dated 3 November 2015, No. 5P08346 dated 21 December 2015, No. 5P05990
dated 16 November 2016, No. 5P07565 dated 20 December 2016 and DBI Report No. PGA10870A dated 13 December
2016 issued according to IMO 2010 FTP Code - Annex 1 - Part 3.
Enclosure - Page 3 of 5
ROXTEC SPM ON DECK
having diameter ranging from 39 mm (type SPM 39) up to 279 mm (type SPM 279). If the deck is insulated by means
of a layer of mineral wool having thickness of 50 mm and density of 100 kg/m3, the transits are to be fitted with
additional insulation having density of 100 kg/m3, consisting of mineral wool cylinders equipped with steel wire placed
in contact with the deck insulation. In case of deck insulated by means of two layers of mineral wool (first layer 50 mm
thick and density of 120 kg/m3 and second layer with steel wire, 30 mm thick and density of 125 kg/m3) the additional
insulation, consisting of discs of the same insulating materials of the deck and mineral wool cylinder equipped with steel
wire having density of 100 kg/m3 may be required.
Fire resistant A-60 Class metallic pipe penetrations through steel decks as per following tables:
STEEL - deck insulated by means of one layer of mineral wool
TYPE OF TRANSITS - PIPE ADDITIONAL INSULATION TRANSIT FIXING
DIAMETER
Transits from SPM 41 up to SPM 81 - Mineral wool cylinder having The transits may be bolted to the deck on
pipe diameter from 12 mm up to 45.4 length of 300 mm and thickness the side exposed or the side unexposed to
mm of 50 mm the fire.
Transits from SPM 81 up to SPM 138 - Mineral wool cylinder having The transits may be bolted to the deck on
pipe diameter greater than 45.4 mm up to length of 400 mm and thickness the side exposed or the side unexposed to
92 mm of 50 mm the fire.
Transits from SPM 138 up to SPM 279 - Mineral wool cylinder having The transits may be bolted to the deck on
pipe diameter greater than 92 mm up to length of 600 mm and thickness the side exposed or the side unexposed to
220 mm of 100 mm the fire.
COPPER - deck insulated by means of one layer of mineral wool
DIAMETER
Transits SPM 41 pipe diameter 12 Mineral wool cylinder having length of 400 mm The transits are to be bolted
mm and thickness of 50 mm to the deck on the side
exposed to the fire.
Transits from SPM 41 up to SPM Fitted on both sides and composed of mineral The transits are to be bolted
279 - pipe diameter greater than 12 wool cylinder having length of 700 mm and to the deck on the side
mm up to 222 mm thickness of 100 mm exposed to the fire.
Enclosure - Page 4 of 5
STEEL - deck insulated by means of two layers of mineral wool
TYPE OF TRANSITS - PIPE DIAMETER ADDITIONAL TRANSIT FIXING AND NOTES
INSULATION
Transits from SPM 39 up to SPM 69 - pipe No additional
diameter from 8 mm up to 36 mm insulation
Transits SPM 81 - pipe diameter 45 mm No additional
insulation only the requirement of the A30 Class
COPPER - deck insulated by means of two layers of mineral wool
TYPE OF TRANSITS - PIPE DIAMETER ADDITIONAL INSULATION TRANSIT
FIXING AND
NOTES
Transits from SPM 39 up to SPM 41 - pipe Mineral wool cylinder having length of 400 mm Seal fitted on the
diam. from 8 up to 16 mm and thickness of 50 mm unexposed side.
Transits from SPM 41 up to SPM 138 - pipe Mineral wool disc having width 100 mm and Seal fitted on the
diameter greater than 16 mm up to 92 mm mineral wool cyl., 100 mm thick and length of 800 unexposed side.
mm
Transits from SPM 138 up to SPM 196 - pipe Mineral wool disc having width 100 mm and Seal fitted on the
diameter greater than 92 up to 143 mm mineral wool cyl., 100 mm thick and length of unexposed side.
1200 mm
Transits from SPM 196 up to SPM 279 - pipe Mineral wool cylinder having length of 700 mm Seal fitted on the
diameter greater than 143 mm up to 222 mm and thickness of 100 mm fitted on both sides unexposed side.
p STYLE=" page-break-after: always" >
Fire resistant A-0 Class metallic pipe penetrations through steel decks as per following table:
STEEL - deck uninsulated
TYPE OF TRANSITS - PIPE TRANSIT INSULATION TRANSIT
DIAMETER FIXING AND
NOTES
Transits from SPM 39 up to SPM 138 - Two layers of mineral wool, around the pipe (50 mm Seal fitted on the
pipe diameter from 12 mm up to 92 mm thick – density 120 kg/m3 and 30 mm thick – density exposed side.
125 kg/m3), having width of 100 mm from the
penetration edge
Transits from SPM 138 up to SPM 279 - Two layers of mineral wool, around the pipe (50 mm Seal fitted on the
pipe diameter greater than 92 up to 222 thick – density 120 kg/m3 and 30 mm thick – density exposed side.
mm 125 kg/m3), having width of 200 mm from the
penetration edge
Enclosure - Page 5 of 5
Roxtec drawings included in:
• SP Reports No. 5P03457 dated 12 November 2015, No. 5P08343 dated 21 December 2015, No. 5P08395 dated 17
March 2016, No. 6P05989 dated 24 October 2016 and No. 6P07563 dated 20 December 2016.
• CTO Report No. RS-17/B-177/E dated 26 May 2017
Tests as per SP Reports No. 5P03457 dated 12 November 2015, No. 5P08343 dated 21 December 2015, No. 5P08395
dated 17 March 2016, No. 6P05989 dated 24 October 2016 and No. 6P07563 dated 20 December 2016 and CTO
Report No. RS-17/B-177/E dated 26 May 2017 issued according to IMO 2010 FTP Code - Annex 1 - Part 3.
Genoa July 30, 2021