No. LAB498522CS/003
| Description | Devices for the passage of pipes through A or B Class |
| divisions | |
| Type | Roxtec SLEEV-IT WT MAR ALU on aluminium decks |
| ROMBVAGEN 2, P.O. BOX 540 | |
| SE-37123 KARLSKRONA |
| Place of manufacture | ROMBVAGEN 2, |
| 37165 LYCKEBY |
| Reference standards | IMO Res. MSC.307(88)-(2010 FTP Code) |
Issued in Genoa on June 5, 2023. This Certificate is valid until May 9, 2028
No. LAB498522CS/003
Enclosure - Page 1 of 1
Roxtec S LEEV-IT WT MAR ALU on aluminium decks
Device for the passage of plastic pipes (not reinforced and multilayer) through A Class aluminium decks composed of a
stainless steel tubular casing fitted with aluminium flange welded to the deck plate. Decks insulated on the side exposed
to the fire by means of two layers of mineral wool (certified non combustible according to the IMO FTP CODE),
having minimum thickness of 30 mm and minimum density of 130 kg/m3. The deck insulation covers also the transits
and is applied all around the same for a minimum width of 250 mm.
Fire resistant A-60 Class plastic pipe penetrations through aluminium decks as per following tables:
| TYPE OF TRANSITS - PIPE DIAMETER | ADDITIONAL | TRANSIT FIXING AND |
| INSULATION | NOTES | |
| Transits from SLEEV-IT WT-MAR16M ALU up to SLEEV-IT | No additional insulation Seal fitted on the exposed | |
| WT-MAR225M ALU | side. | |
| pipe diameter from 16 mm up to 225 mm |
Roxtec drawings included in DBI Report No. PGA10802A dated 29 August 2016 and in CTO Report No. RS-17/B-
210/E dated 2 June 2017.
Tests as per DBI Report No. PGA10802A dated 29 August 2016 and CTO Report No. RS-17/B-210/E dated 2 June
2017 issued according to IMO 2010 FTP Code - Annex 1 - Part 3.
Note: Transits SLEEV-IT WT-MAR16M and SLEEV-IT WT-MAR225M were subjected to hydrostatic test (water - 1.5
bar) for 60 minutes and gas-tightness test (helium - 1 bar) for 30 minutes without any leakage - Tests as per DNV-GL
Survey Report No. N141EX90 dated 30 June 2017.