LAB498522CS-004-optimized
No. LAB498522CS/004
divisions
Type Roxtec S Series
ROMBVAGEN 2, P.O. BOX 540
SE-37123 KARLSKRONA
Place of manufacture ROMBVAGEN 2,
37165 LYCKEBY
Issued in Genoa on June 5, 2023. This Certificate is valid until February 7, 2028
No. LAB498522CS/004
Enclosure - Page 1 of 2
Roxtec S S eries
Devices, composed of halogen free material packing system, for the passage of metallic pipes having diameter ranging
from 8 up to 57 mm through A Class aluminium bulkheads and decks. The aluminium bulkheads and decks are
insulated by means of two layers of mineral wool with aluminium foil (certified non-combustible according to the IMO
FTP Code), having, each, minimum thickness of 30 mm thick and minimum density of 130 kg/m3 fitted on the exposed
side (decks) and on both sides (bulkhead). The division insulation covers also the transits and is applied all around the
same for a minimum width of 250 mm; the transits are fitted with additional insulation (certified non-combustible
according to the IMO FTP Code) as described in the following tables; the thicknesses and density values are to be
considered as the minimum.
BULKHEADS - METALLIC PIPES
TYPE OF TRANSITS TYPE OF PIPES ADDITIONAL TRANSIT FIXING AND
INSULATION NOTES
S 1x1 Copper pipe diameter of 10 Mineral wool cylinder, one The penetration is fixed to
mm layer 50 mm thick having the bulkhead plate in the
density of 100 kg/m3 and middle; the additional
length of 300 mm insulation is fitted on the
unexposed side.
S 1x1 Steel pipe diameter of 10 Mineral wool cylinder, one The penetration is fixed to
and 12 mm layer 50 mm thick having the bulkhead plate in the
length of 200 mm insulation is fitted on the
unexposed side.
S 8x2 Copper pipe diameter from 8 Mineral wool cylinder, one The penetration is fixed to
up to 57 mm layer 50 mm thick having the bulkhead plate in the
Steel pipe diameter from 8 density of 100 kg/m3 and middle; the additional
up to 54 mm length of 200 mm (steel insulation is fitted on the
pipe) and 300 mm (copper unexposed side.
pipe)
LAB498522CS /004
Enclosure - Page 2 of 2
DECKS - METALLIC PIPES
INSULATION NOTES
mm layer 50 mm thick having the deck plate in the middle,
density of 100 kg/m3 and exposed or unexposed side;
length of 400 mm the additional insulation is
fitted on the exp. side.
S 8x2 Steel pipe diameter from 8 Mineral wool cylinder, one The penetration is fixed to
up to 54 mm layer 50 mm thick having the deck plate in the middle,
S 1x1 Copper pipe diameter of Mineral wool cylinder, two The penetration is fixed to
10mm layers 50 mm thick each, the deck plate in the middle,
having density of 100 kg/m3 exposed or unexposed side;
and length of 500 mm the additional insulation is
S 8x2 Copper pipe diameter from Mineral wool cylinder, one The penetration is fixed to
10 up to 57 mm layer 50 mm thick having the deck plate in the middle,
Fire resistant A-60 Class pipe penetrations through load-bearing aluminium bulkheads and decks.
Roxtec drawings enclosed in DANAK Test Reports No. PG11898 and No. PG11955 dated 17 April 2009 and CTO Test
Report No. RS-17/B-210/E dated 2 June 2016 .
Tests as per DANAK Test Reports No. PG11898 and No. PG11955 dated 17 April 2009 issued according to IMO Res.
A.754 (18) and CTO Test Report No. RS-17/B-210/E dated 2 June 2016 issued according to IMO 2010 FTP Code.
Genoa 5/06/2023