| Page | 1 of 11 |
|---|---|
| Certificate No: | LR2006428SF |
| Issue Date: | 08/07/2020 |
| Expiry Date: | 07/07/2025 |
Certificate Of Fire Approval
This is to certify that the product detailed below will be accepted for compliance with the applicable Lloyd’s Register
Rules and Regulations and with the International Convention for the Safety of Life at Sea, (SOLAS), 1974, as
amended, for use on ships and offshore installations classed with Lloyd’s Register, and for use on ships and offshore
installations when authorised by contracting governments to issue the relevant certificates, licences, permits etc.
| Manufacturer | Roxtec International AB |
|---|---|
| Address | Rombvägen 2, Box 540, S-371 23 Karlskrona, Sweden |
| Type | Pipe Penetration (Standard Fire Test) |
| Description | Fire Resisting Single Metallic Pipe Circular Penetrations– Type: “Roxtec SPM |
Seal” for applications in A Class steel and aluminium bulkheads and decks
| Trade Name | Roxtec SPM Seal |
|---|
| Specified Standard | IMO Res. MSC.307 (88) - (2010 FTP Code) Annex 1, Part 3 |
IMO MSC.1/Circ.1488
This certificate is not valid for equipment, the design or manufacture of which has been varied or modified from the
specimen tested. The manufacturer should notify Lloyd’s Register EMEA of any modification or changes to the
equipment in order to obtain a valid Certificate.
The Design Appraisal Document and its supplementary Type Approval Terms and Conditions form part of this
Certificate.
This certificate remains valid unless cancelled or revoked, provided the conditions in the attached Design Appraisal
Document are complied with and the equipment remains satisfactory in service.
Saji Abraham
Surveyor to Lloyd’s Register EMEA
| 71 Fenchurch Street, London, EC3M 4BS, United | A member of the Lloyd’s Register Group |
|---|---|
| Kingdom |
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and
conditions set out in that contract.
TA02 1.0.0
| Page | 2 of 11 |
|---|---|
| Certificate No: | LR2006428SF |
| Issue Date: | 08/07/2020 |
| Expiry Date: | 07/07/2025 |
| Reference: | UKITSO/FIRE/TA/SA/WP35151560 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2006428SF
The undernoted documents have been appraised for compliance with the relevant requirements of International
Conventions.
This Design Appraisal Document forms part of the Certificate.
This certificate is a renewal and amendment of SAS F160195/M1
EXAMINED DOCUMENTATION
SP Technical Research Institute of Swedaen, Boras, Sweden; Fire Test Reports No: 5P03451 dated 3 November 2015,
5P03457 dated 12 November 2015, 5P08346 dated 21 December 2015, 5P08343 dated 21 December 2015 and 5P08395
dated 17 March 2016, 6P05989 and 6P05989 both dated 24 October 2016 and 6P07565 dated 20 December 2016.
Danish Institute of Fire and Security Technology, Hvidovre, Denmark; Fire test report No: PGA10870A dated 13 December
2016.
Ship Design and Research Centre S.A. (CTO), Gdansk, Poland; Fire test reports No: RS-17/B-209/E and RS-17/B-210/E both
dated 2 June 2017, RS-18/B-179/E and RS-18/B-180/E both dated 25 June 2018
Manufacturer’s guidance drawings No: S1513650A, S1513651A, S1513652C and S1513653A (for steel divisions) and
S1536362A dated 4 October 2018, S1536464A dated 7 April 2020, S1536485A and S1536486A both dated 17 April 2020 (for
aluminium divisions). Note: Manufacturer drawings are for reference purposes only; product applications to be in
accordance with Conditions of Certification below
CONDITIONS OF CERTIFICATION
| 1. | For applications in A-60 Class steel bulkheads and decks, with approved insulation arrangements as described in |
|---|---|
| Tables 1 and 2 below and also generally in accordance with manufacturer’s guidance drawings No: S1513650A, | |
| S1513651A, S1513652C and S1513653A. Final insulation arrangements onboard are to be approved by the relevant |
project authority on a case-by-case basis
| 2. | All “SPM Series” pipe seals were tested only in A-60 Class steel divisions, but not separately in A-0 Class steel divisions |
|---|---|
| in accordance with IMO Res. MSC.307(88)-(2010 FTP Code) Annex 1, Part 3 Appendix 2. A.III.2.2.1.1 Therefore for | |
| applications in A-0, A-15 and A-30 Class steel bulkheads and decks, they shall be fitted with the same or equivalent A- | |
| 60 Class insulation arrangements as those used in the fire tests (including any insulation fitted on the penetration itself | |
| in the tests) for a minimum distance of 200mm around the penetration, on all fire risk sides of bulkheads and decks (as | |
| identified by the Design Plan Approval Authority for each project) and insulation should be extended to cover the full | |
| side(s) and the end face(s) of the steel frame, with an overlap of at least 20mm from the steel end plate edges. The | |
| above mentioned A-60 Class insulation arrangements should be additional to any thermal or acoustic insulation, but | |
| may include any fire rated insulation (e.g. A-15, or A-30) already fitted on the bulkhead or deck and/or on the | |
| penetration itself, such that the total fire rating is A-60 | |
| 3. | For applications in A-60 equivalent aluminium bulkheads and decks, with approved insulation arrangements as |
| — | — |
| described in Tables 3 and 4 below and also generally in accordance with manufacturer’s guidance drawings No: | |
| S1536362A dated 4 October 2018, S1536464A dated 7 April 2020, S1536485A and S1536486A both dated 17 April 2020. | |
| Final insulation arrangements onboard are to be approved by the relevant project authority on a case-by-case basis |
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and
conditions set out in that contract.
| Page | 3 of 11 |
|---|---|
| Certificate No: | LR2006428SF |
| Issue Date: | 08/07/2020 |
| Expiry Date: | 07/07/2025 |
| Reference: | UKITSO/FIRE/TA/SA/WP35151560 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2006428SF
| 4. | Aluminium bulkheads and decks in all cases must be insulated with an approved system to prevent the core |
|---|---|
| temperature exceeding 2000c and all pipe penetrations fitted to such divisions shall also be insulated with either the |
same system or an approved A-60 system
| 5. | Roxtec “SPM Series” pipe seals consist of: stainless steel circular plates fitted to the front and rear ends of the “Roxylon” |
|---|---|
| rubber seal unit and secured using 5 stainless steel bolts and nuts fitted through the front and rear end plates and the | |
| “Roxylon” rubber seal unit. The “SPM” pipe seal unit is fitted around the pipes and secured to the steel bulkhead or | |
| deck by expansion of the rubber seal fitted through the aperture in bulkhead or deck plate, when the bolts are | |
| tightened. Constructional details of the Roxtec “SPM Series” pipe seals are to be as described in Roxtec drawing: |
S1502970 Rev. D
| 6. | Approved arrangements for Roxtec “SPM Series” pipe seals in A-60 Class steel and aluminium bulkheads and decks are |
|---|---|
| as described in Tables 1 & 2 and 3&4 below respectively | |
| 7. | Type Approval is limited to the as-tested SPM pipe penetration seals only, for use with the specific size or size range of |
| — | — |
| each type of pipe tested as described in the Tables. Intermediate size SPM seals within the tested range may only be | |
| accepted subject to final approval from the design project authority, provided they are fitted with at least the same | |
| insulation arrangements as the next greater size seal approved in the Tables (for example, seals larger than SPM 81 in | |
| Table 1 must be fitted with at least the same insulation arrangements approved for SPM 138) and the size of the | |
| penetrating pipe being proportional to the size of the specific intermediate penetration, which may be determined by |
linear interpolation
| 8. | Production items are to be manufactured in accordance with a quality control system which shall be maintained to |
|---|---|
| ensure that items are of the same standard as the approved prototype | |
| 9. | The certificate holder is solely responsible for the products supplied under this Certificate and to ensure that their |
| — | — |
| products, whether manufactured by themselves or their licensee manufacturers, if agreed by Lloyd’s Register, are fully | |
| compliant with the relevant statutory regulations and Lloyd’s Register Class rules as applicable and designed and | |
| manufactured to the same quality and specifications as the prototype tested, including components that are designed |
and manufactured by third parties
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and
conditions set out in that contract.
| Page | 4 of 11 |
|---|---|
| Certificate No: | LR2006428SF |
| Issue Date: | 08/07/2020 |
| Expiry Date: | 07/07/2025 |
| Reference: | UKITSO/FIRE/TA/SA/WP35151560 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2006428SF
Table 1: Approved arrangements in A-60 Class Steel Bulkheads
Minimum
Minimum
thickness/length of as-
diameter of as-
tested or equivalent A-
tested or
60 insulation to be
| Position of | equivalent A-60 |
|---|---|
| Tested Pipe | fitted along the pipe on |
| Maxi- | SPM seal in |
| Nominal | single side or both |
| Pipe | mum |
| Seal | Outside |
| Material | Fire |
| Diameter | applicable, when |
| rating | Restricted(b) |
| (in mm) | measured from the |
| Applications | both sides of |
| Penetration insulation | |
| bulkhead as | |
| collar (if applicable) or | |
| applicable (in | |
| bulkhead insulation (in | |
| mm). | |
| mm). | |
| Fire exposed | |
| side or Fire | |
| SPM 39 | 12 |
| — | — |
| side (General | |
| Applications) | |
| Fire exposed | |
| side or Fire | |
| SPM 41 | 12 |
| — | — |
| side (General | |
| Applications) | |
| Fire exposed | |
| side or Fire | |
| SPM 81 | 45.4 |
| — | — |
| side (General | |
| Applications) | |
| Fire | |
| unexposed | |
| side | |
| SPM 138 | 92 |
| — | — |
| (insulated | |
| side)/Restricte | |
| d applications | |
| Fire exposed | |
| side or Fire | |
| SPM 279 | 220 |
| — | — |
| side (General | |
| Applications) |
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and
conditions set out in that contract.
| Page | 5 of 11 |
|---|---|
| Certificate No: | LR2006428SF |
| Issue Date: | 08/07/2020 |
| Expiry Date: | 07/07/2025 |
| Reference: | UKITSO/FIRE/TA/SA/WP35151560 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2006428SF
Table 1: Approved arrangements in A-60 Class Steel Bulkheads (Continued)
Fire exposed side
| SPM | Coppe | or Fire unexposed |
|---|---|---|
| 12 | A-60 | Not required |
| 39 | r | side (General |
| Applications) | ||
| Fire exposed side | ||
| SPM | Coppe | or Fire unexposed |
| — | — | — |
| 12 | A-60 | 50/400 (Single side) |
| 41 | r | side (General |
| Applications) | ||
| Fire exposed side | ||
| SPM | Coppe | or Fire unexposed |
| — | — | — |
| 45 | A-60 | 50/400 (Single side) |
| 81 | r | side (General |
| Applications) | ||
| Fire exposed side | ||
| SPM | Coppe | or Fire unexposed |
| — | — | — |
| 90 | A-60 | 50/600 (Single side) |
| 138 | r | side (General |
| Applications) | ||
| Fire exposed side | ||
| SPM | Coppe | or Fire unexposed |
| — | — | — |
| 220 | A-60 | 100/700 (Both sides) |
| 279 | r | side (General |
| Applications) |
| (a) | General applications refer to installation arrangements where the penetrations are accepted for use on any one side |
|---|---|
| (fire exposed side or fire unexposed side) of the bulkhead. | |
| (b) | Restricted applications refer to installation arrangements where the penetrations are accepted for use on the fire |
| — | — |
| unexposed, insulated side of the bulkhead in all cases. |
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and
conditions set out in that contract.
| Page | 6 of 11 |
|---|---|
| Certificate No: | LR2006428SF |
| Issue Date: | 08/07/2020 |
| Expiry Date: | 07/07/2025 |
| Reference: | UKITSO/FIRE/TA/SA/WP35151560 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2006428SF
Table 2: Approved arrangements in A-60 Class Steel Decks
| Seal | Tested Pipe | Pipe | Maxi- | Position of SPM | Minimum diameter | Minimum |
|---|---|---|---|---|---|---|
| Nominal | Material | mum Fire | seal in | of as-tested or | thickness/length of | |
| Outside | Rating | Decks/General(a) | equivalent A-60 | as-tested or | ||
| Diameter | or Restricted(b) | Class Insulation | equivalent A-60 Class | |||
| (in mm) | Applications | Collar required | insulation to be fitted | |||
| around the | along the pipe on the | |||||
| penetration on the | underside, topside or | |||||
| underside, topside | both sides of deck as | |||||
| or both sides of | applicable, when | |||||
| deck as applicable | measured from the | |||||
| of decks as | penetration | |||||
| applicable (in mm). | insulation collar or | |||||
| deck insulation as | ||||||
| applicable (in mm). | ||||||
| Fire exposed | ||||||
| SPM | underside | |||||
| — | — | |||||
| 8 to 12 | Steel | A-60 | Not required | Not required | ||
| 39 | (Restricted | |||||
| Applications) | ||||||
| SPM | 12 | Steel | A-60 | Fire exposed | Not required | Not required |
| — | — | — | — | — | — | — |
| 41 | underside or | |||||
| Fire unexposed | ||||||
| side (General | ||||||
| Applications) | ||||||
| SPM | 30 | Steel | A-60 | Fire exposed | Not required | Not required |
| — | — | — | — | — | — | — |
| 62 | underside or | |||||
| Fire unexposed | ||||||
| side (General | ||||||
| Applications) | ||||||
| SPM | 36 | Steel | A-60 | Fire exposed | Not required | Not required |
| — | — | — | — | — | — | — |
| 69 | underside or | |||||
| Fire unexposed | ||||||
| side (General | ||||||
| Applications) | ||||||
| SPM | 45.4 | Steel | A-60 | Fire exposed | Not required | 50/300 (Underside) |
| — | — | — | — | — | — | — |
| 81 | underside or | |||||
| Fire unexposed | ||||||
| side (General | ||||||
| Applications) |
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and
conditions set out in that contract.
| Page | 7 of 11 |
|---|---|
| Certificate No: | LR2006428SF |
| Issue Date: | 08/07/2020 |
| Expiry Date: | 07/07/2025 |
| Reference: | UKITSO/FIRE/TA/SA/WP35151560 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2006428SF
| SPM | 92 | Steel | A-60 | Fire exposed | Not required | 50/400 (Underside) |
|---|---|---|---|---|---|---|
| 138 | underside or | |||||
| Fire unexposed | ||||||
| side (General | ||||||
| Applications) | ||||||
| SPM | 220 | Steel | A-60 | Fire exposed | Not required | 100/600 (Underside) |
| — | — | — | — | — | — | — |
| 279 | underside or | |||||
| Fire unexposed | ||||||
| side (General | ||||||
| Applications) | ||||||
| Fire exposed | ||||||
| SPM | underside | |||||
| — | — | |||||
| 8 to 12 | Copper | A-60 | Not required | 50/400 (Underside) | ||
| 39 | (Restricted | |||||
| Applications) | ||||||
| SPM | 12 | Copper | A-60 | Fire exposed | Not required | 50/400 (Underside) |
| — | — | — | — | — | — | — |
| 41 | underside or | |||||
| Fire unexposed | ||||||
| side (General | ||||||
| Applications) | ||||||
| SPM | 16 | Copper | A-60 | Fire exposed | Not required | 50/400 (Underside) |
| — | — | — | — | — | — | — |
| 41 | underside | |||||
| (Restricted | ||||||
| Applications) | ||||||
| SPM | 45.4 | Copper | A-60 | Fire exposed | Not required | 100/800 (Underside) |
| — | — | — | — | — | — | — |
| 81 | underside or | |||||
| Fire unexposed | ||||||
| side (General | ||||||
| Applications) | ||||||
| SPM | 92 | Copper | A-60 | Fire exposed | 100 (underside) | 100/800 (Underside) |
| — | — | — | — | — | — | — |
| 138 | underside or | |||||
| Fire unexposed | ||||||
| side (General | ||||||
| Applications) | ||||||
| SPM | 143 | Copper | A-60 | Fire exposed | 100 (underside) | 100/800 (Underside) |
| — | — | — | — | — | — | — |
| 196 | underside | |||||
| (Restricted | ||||||
| Applications) | ||||||
| SPM | 171 | Copper | A-60 | Fire exposed | Not Required | 100/1200 (Underside) |
| — | — | — | — | — | — | — |
| 226 | underside | |||||
| (Restricted | ||||||
| Applications) |
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and
conditions set out in that contract.
| Page | 8 of 11 |
|---|---|
| Certificate No: | LR2006428SF |
| Issue Date: | 08/07/2020 |
| Expiry Date: | 07/07/2025 |
| Reference: | UKITSO/FIRE/TA/SA/WP35151560 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2006428SF
| SPM | 222 | Copper | A-60 | Fire unexposed | Not required | 100/700 (Both sides) |
|---|---|---|---|---|---|---|
| 279 | side(topside)/R | |||||
| estricted | ||||||
| Applications | ||||||
| SPM | 222 | Copper | A-60 | Fire exposed | Not Required | 100/1200 (Underside) |
| — | — | — | — | — | — | — |
| 279 | underside | |||||
| (Restricted | ||||||
| Applications) |
| (a) | General applications refer to installation arrangements where the penetrations are accepted for use on any one side |
|---|---|
| (fire exposed side or fire unexposed side) of a steel deck, which is insulated on the fire exposed underside in all cases. | |
| (b) | Restricted applications refer to installation arrangements where the penetrations are accepted for use only on one |
| — | — |
| specific side (fire exposed side or fire unexposed side) of a steel deck, depending on the tested configuration as | |
| described in the Table , with the steel deck insulated on the fire exposed underside in all cases. |
Table 3: Approved arrangements in A-60 Class equivalent aluminium bulkheads
Minimum thickness/length
| Tested | of as-tested or equivalent A- |
|---|---|
| Pipe | Maxi- |
| Position of SPM seal in | |
| Nominal | Pipe |
| — | — |
| Seal | bulkheads/ |
| Outside | Material |
| General Applications (a) | |
| Diameter | rating |
| — | — |
| (in mm) | from the bulkhead insulation |
| (in mm). | |
| Fire exposed side or Fire | |
| SPM 39 | 8 |
| — | — |
| (General Applications) | |
| Fire exposed side or Fire | |
| SPM 81 | 45.4 |
| — | — |
| (General Applications) | |
| Fire exposed side or Fire | |
| SPM 87 | 51 |
| — | — |
| (General Applications) | |
| Fire exposed side or Fire | |
| SPM 138 | 92 |
| — | — |
| (General Applications) | |
| Fire exposed side or Fire | |
| SPM 149 | 103 |
| — | — |
| (General Applications) |
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and
conditions set out in that contract.
| Page | 9 of 11 |
|---|---|
| Certificate No: | LR2006428SF |
| Issue Date: | 08/07/2020 |
| Expiry Date: | 07/07/2025 |
| Reference: | UKITSO/FIRE/TA/SA/WP35151560 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2006428SF
Fire exposed side or Fire
| SPM 279 | 222 | Steel | A-60 | unexposed side | 100/500 (both sides) |
|---|---|---|---|---|---|
| (General Applications) | |||||
| Fire exposed side or Fire | |||||
| SPM 39 | 8 | Copper | A-60 | unexposed side | 50/400 (single side) |
| — | — | — | — | — | — |
| (General Applications) | |||||
| Fire exposed side or Fire | |||||
| SPM 81 | 45.4 | Copper | A-60 | unexposed side | 50/400 (single side) |
| — | — | — | — | — | — |
| (General Applications) | |||||
| Fire exposed side or Fire | |||||
| SPM 87 | 51 | Copper | A-60 | unexposed side | 50/500 (single side) |
| — | — | — | — | — | — |
| (General Applications) | |||||
| Fire exposed side or Fire | |||||
| SPM 138 | 92 | Copper | A-60 | unexposed side | 50/500 (single side) |
| — | — | — | — | — | — |
| (General Applications) | |||||
| Fire exposed side or Fire | |||||
| SPM 149 | 103 | Copper | A-60 | unexposed side | 100/600 (single side) |
| — | — | — | — | — | — |
| (General Applications) | |||||
| Fire exposed side or Fire | |||||
| SPM 157 | 110 | Copper | A-60 | unexposed side | 100/600 (single side) |
| — | — | — | — | — | — |
| (General Applications) |
| (a) | General applications refer to installation arrangements where the penetrations are accepted for use on any one side |
|---|---|
| (fire exposed side or fire unexposed side) of the bulkhead. |
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and
conditions set out in that contract.
| Page | 10 of 11 |
|---|---|
| Certificate No: | LR2006428SF |
| Issue Date: | 08/07/2020 |
| Expiry Date: | 07/07/2025 |
| Reference: | UKITSO/FIRE/TA/SA/WP35151560 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2006428SF
Table 4: Approved arrangements in A-60 Class equivalent aluminium decks
Minimum thickness/length of as-
| Tested | tested or equivalent A-60 Class |
|---|---|
| Pipe | Maxi- |
| Nominal | Pipe |
| Seal | |
| Outside | Material |
| — | — |
| Diameter | Rating |
| (in mm) | insulation collar or deck insulation |
| as applicable (in mm). | |
| Fire exposed | |
| underside | |
| SPM 39 | 8 |
| — | — |
| (Restricted | |
| Applications) | |
| Fire exposed | |
| underside | |
| SPM 81 | 45.4 |
| — | — |
| (Restricted | |
| Applications) | |
| Fire exposed | |
| underside | |
| SPM 87 | 47 |
| — | — |
| (Restricted | |
| Applications) | |
| Fire exposed | |
| underside | |
| SPM 138 | 92 |
| — | — |
| (Restricted | |
| Applications) | |
| Fire exposed | |
| underside | |
| SPM 149 | 103 |
| — | — |
| (Restricted | |
| Applications) | |
| Fire exposed | |
| underside | |
| SPM 279 | 222 |
| — | — |
| (Restricted | |
| Applications) | |
| Fire exposed | |
| underside | |
| SPM 39 | 8 |
| — | — |
| (Restricted | |
| Applications) | |
| Fire exposed | |
| underside | |
| SPM 157 | 110 |
| — | — |
| (Restricted | |
| Applications) |
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and
conditions set out in that contract.
| Page | 11 of 11 |
|---|---|
| Certificate No: | LR2006428SF |
| Issue Date: | 08/07/2020 |
| Expiry Date: | 07/07/2025 |
| Reference: | UKITSO/FIRE/TA/SA/WP35151560 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2006428SF
(a) Restricted applications refer to installation arrangements where the penetrations are accepted for use only on one
specific side (fire exposed side or fire unexposed side) of a steel deck, depending on the tested configuration as
described in the Table, with the steel deck insulated on the fire exposed underside in all cases.
NOTES (For Information only; outside the scope of Fire Type Approval Certification)
| 1. | Single “SPM Series” Pipe penetration seals, types: “SPM 41”, “SPM 81”, “SPM 138” and “SPM 279” were subjected to a |
|---|---|
| hydrostatic pressure of 1.5 bar for a period of 60 minutes with no leakage, followed by a helium gas pressure test at 1 | |
| bar for a period of 30 minutes with no leakage, as detailed in DNV-GL Reports No. N1417RRN dated 29 January 2016 |
and N1419WS4 dated 22 June 2016.
| 2. | Roxtec SPM 39 seal with a single steel pipe of outer diameter 8mm, mounted in 4mm and 15mm thick steel plates, was |
|---|---|
| subjected to a 60minutes watertightness test at 1.5bar followed by a 30minutes helium gas tightness test at 1bar, with | |
| the pressure applied from different sides of the seal, and no leakage was reported for the full test duration, as described | |
| in DNV-GL Survey Report No: N141805A dated 20 December 2016 and associated Test Report TST-000505. | |
| 3. | The above-mentioned Pipe penetration seals may be considered to prevent flooding or maintain gastight |
| — | — |
| requirements on a ship approval basis. These types of penetrations are not suitable for tank boundaries and where the | |
| penetrations are subject to frequent immersion in fluids and are not suitable for applications identified in SOLAS, | |
| Chapter II-1, Regulation 13.2.3 for “Openings in watertight bulkheads below the bulkhead deck in passenger ships.” |
PLACE OF PRODUCTION
Roxtec International AB
Box 540
S-371 23 Karlskrona
Sweden
Saji Abraham
Senior Specialist
Fire & Safety, Statutory Discipline Team
UK&I Technical Support Office, Marine & Offshore
Lloyd’s Register EMEA
Supplementary Type Approval Terms and Conditions
This certificate and Design Appraisal Document relates to type approval, it certifies that the prototype(s) of the product(s)
referred to herein has/have been found to meet the applicable design criteria for the use specified herein, it does not mean
or imply approval for any other use, nor approval of any products designed or manufactured otherwise than in strict
conformity with the said prototype(s).
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and