MEDB00000NV
3
Application of: Directive 2014/90/EU of 23 July 2014 on marine equipment (MED), issued as “Forskrift
om Skipsutstyr” by the Norwegian Maritime Authority. This Certificate is issued by DNV GL AS under the
authority of the Government of Norway.
Roxtec sealing system: Roxtec SPM seal series / Roxtec SPM Blind seal series (steel divisions)
Regulation (EU) 2020/1170,
item No. MED/3.26b. SOLAS 74 as amended, Regulation II-2/9, IMO MSC.1/Circ.1276, IMO
2010 FTP Code and IMO MSC.1/1488
This Certificate is valid until 2025-10-01.
Issued at Høvik on 2020-10-02
for DNV GL AS
| DNV GL local station: | Digitally Signed By: Hoff, Øyvind |
| Sweden CMC | Location: DNV GL Høvik, Norway |
| on behalf of |
Roald Vårheim
| Helge Bjørnarå | Notified Body |
A U.S. Coast Guard approval number will be assigned to the equipment when the production module has been completed and will appear on the
production module certificate (module D, E or F), as allowed by the “Agreement between the United States of America and the EEA EFTA states
on the mutual recognition of Certificates of Conformity for Marine Equipment” signed 17 October 2005, and amended by Decision No 1/2019
dated February 22nd, 2019.
The mark of conformity may only be affixed to the above type approved equipment and a Manufacturer’s Declaration of Conformity
issued when the production-surveillance module (D, E or F) of Annex B of the MED is fully complied with and controlled by a written
inspection agreement with a Notified Body. The product liability rests with the manufacturer or his representative in accordance with
Directive 2014/90/EU.
This certificate is valid for equipment, which is conform to the approved type. The manufacturer shall inform DNV GL AS of any
changes to the approved equipment. This certificate remains valid unless suspended, withdrawn, recalled or cancelled.
Should the specified regulations or standards be amended during the validity of this certificate, the product is to be re-approved
before being placed on board a vessel to which the amended regulations or standards apply.
LEGAL DISCLAIMER: Unless otherwise stated in the applicable contract with the holder of this document, or following from mandatory law, the
liability of DNV GL AS, its parent companies and subsidiaries as well as their officers, directors and employees (“DNV GL”) arising from or in
connection with the services rendered for the purpose of the issuance of this document or reliance thereon, whether in contract or in tort
(including negligence), shall be limited to direct losses and under any circumstance be limited to 300,000 USD.
| Form code: MED 201.NOR | Revision: 2020-01 | www.dnvgl.com | Page 1 of 4 |
© DNV GL 2014. DNV GL and the Horizon Graphic are trademarks of DNV GL AS.
| Job Id: | 344.1-005182-4 |
| Certificate No: MEDB00000NV | |
| Revision No: | 3 |
“Roxtec sealing system: Roxtec SPM seal series / Roxtec SPM Blind seal series (steel divisions)”,
Consisting of Roxtec SPM rubber seal in size 39 to 279 attached through expansion to steel sections and
Roxtec SPM Blind rubber seal in sizes 39/0 to 92/0 attached through expansion to steel section.
Approved for use as a single pipe penetration system in A-class steel divisions according to below tables.
Other applications are subject to case-by case approval.
For A-15 and A-30 applications, the penetration shall be insulated as for A-60 and the division is to be
fitted with A-60 insulation for a minimum distance of 200 mm around the penetration.
| Pipe | Sleeve | Sleeve |
| Pipe | Seal | Sleeve |
| Type | Size | diameter |
| material | position | insulation |
| (OD) [mm] | [mm] | [mm] |
| SPM | 39 – 279 | Steel |
| SPM | 39 – 279 | Copper |
| SPM Blind | 39/0 – 92/0 | NA |
| Pipe | Seal | Seal |
| material | position | Insulation |
Table 3: Approved pipe penetration in A-0 steel bulkhead
Table 4: Approved pipe penetration in A-0 steel deck
All seals shall be installed in accordance with Roxtec’s SPM seal Installation Instructions, including
aperture dimensions and tolerances, tightening torque, etc.
Penetrations through structural divisions should not impair the structural strength of the division.
Special consideration should be given to bulkheads and decks with high stress locations
(IMO MSC.1/Circ.1488).
| Form code: MED 201.NOR | Revision: 2020-01 | www.dnvgl.com | Page 2 of 4 |
| Job Id: | 344.1-005182-4 | ||
| Certificate No: MEDB00000NV | |||
| Revision No: | 3 | ||
The insulation material used has to be approved according to the Marine Equipment Directive and bear
the Mark of Conformity.
Test Report No. 5P03451 dated 3 November 2015 from SP, Borås, Sweden.
Test Report No. 5P03457 dated 12 November 2015 from SP, Borås, Sweden.
Test Report No. 5P08343 dated 21 December 2015 from SP, Borås, Sweden.
Test Report No. 5P08346 dated 21 December 2015 from SP, Borås, Sweden.
Test Report No. 5P08395 dated 17 March 2016 from SP, Borås, Sweden.
Test Report No. 6P05989 dated 24 October 2016 from SP, Borås, Sweden.
Test Report No. 6P05990 dated 16 November 2016 from SP, Borås, Sweden.
Test Report No. PGA1087A dated 13 December 2016 from DBI, Hvidovre, Denmark.
Test Report No. RS-17/B-177/E dated 6 May 2017 from CTO, Gdansk, Poland.
Test Report No. RS-18/B-022/E dated 29 January 2018 from CTO, Gdansk, Poland.
Test Report No. RS-18/B-023/E dated 29 January 2018 from CTO, Gdansk, Poland.
Test Report No. RS-18/B-181/E dated 7 May 2018 from CTO, Gdansk, Poland.
Test Report No. PGA11302A dated 16 January 2019 from DBI, Hvidovre, Denmark.
Drawing No. S1518359 Rev. A dated 22 December 2016 from maker.
Drawing No. S1518384 Rev. A dated 22 December 2016 from maker.
Drawing No. S1518385 Rev. B dated 28 September 2020 from maker.
Drawing No. S1518386 Rev. A dated 22 December 2016 from maker.
Drawing No. S1518398 Rev. B dated 28 September 2020 from maker.
Drawing No. S1518399 Rev. A dated 22 December 2016 from maker.
Drawing No. S1518400 Rev. A dated 22 December 2016 from maker.
Drawing No. S1553706 Rev. A dated 28 September 2020 from maker.
Drawing No. S1553712 Rev. A dated 28 September 2020 from maker.
Drawing No. S1553744 Rev. A dated 28 September 2020 from maker.
The product or packing is to be marked with name of manufacturer, type designation, fire-technical
rating, MED Mark of Conformity and USCG approval number if applicable.
| Form code: MED 201.NOR | Revision: 2020-01 | www.dnvgl.com | Page 3 of 4 |
SPM 39 – 279:
Approved for penetration in steel bulkheads or decks limited to a pressure of 1.00 bar watertightness
and 0.67 bar gastightness.
SPM Blind 39/0 – 92/0:
Test Report No. N1417RRN dated 29 January 2016 from DNV GL Malmö.
Test Report No. N1419WS4 dated 22 June 2016 from DNV GL Malmö.
Test Report No. N14805C dated 22 November 2017 from DNV GL Malmö.
Tested according to Class Programme DNVGL-CP-0165 Chapter 4, February 2016.
| Form code: MED 201.NOR | Revision: 2020-01 | www.dnvgl.com | Page 4 of 4 |