Certificate No:
TAF00000D8
| TYPE APPROVAL CERTIFICATE | Revision No: |
|---|---|
| 3 |
This is to certify:
That the Class H Penetration
with type designation(s)
ROXTEC SEALING SYSTEM WITH MULTIDIAMETER TECHNOLOGY: RS-SERIES (CABLE)
Issued to
Roxtec International AB
Karlskrona, Sweden
is found to comply with
DNV offshore standards
Application :
Approved as cable penetration in class H-120, H-60 and H-0 steel decks and bulkheads.
Issued at Høvik on 2022-11-09
for DNV
| This Certificate is valid until 2027-02-01. | Digitally Signed By: Permoda, Jowita |
|---|---|
| Location: DNV Gdynia, Poland | |
| DNV local unit: Sweden CMC | Signing Date: 09.11.2022 |
| — | — |
Approval Engineer: Timo Linn
Jowita Permoda
Head of Section
This Certificate is subject to terms and conditions overleaf. Any significant change in design or construction may render this Certificate invalid.
The validity date relates to the Type Approval Certificate and not to the approval of equipment/systems installed.
LEGAL DISCLAIMER: Unless otherwise stated in the applicable contract with the holder of this document, or following from mandatory law, the liability of DNV AS, its
parent companies and their subsidiaries as well as their officers, directors and employees (“DNV”) arising from or in connection with the services rendered for the
purpose of the issuance of this document or reliance thereon, whether in contract or in tort (including negligence), shall be limited to direct losses and under any
circumstance be limited to 300,000 USD.
| Form code: TA 251 | Revision: 2022-09 | www.dnv.com | Page 1 of 3 |
|---|---|---|---|
| Job Id: | 262.1-001101-22 | ||
| Certificate No: | TAF00000D8 | ||
| Revision No: | 3 |
Product description
“Roxtec sealing system with multidiameter technology: RS-series”
consisting of steel sleeve, welded or bolted (openable versions included) to steel decks and steel bulkheads. The sleeve
is filled with Roxtec RS (standard or EMC) halogen free rubber sealing.
Additional Place of Production:
Roxtec Sealing System (Shanghai) Co,.Ltd Lingang Branch
Ground Floor A, No.875 QiuXin Road Zhongqilian (Lingang) Global Auto Parts Innovation Center, Shanghai, China.
Application/Limitation
Approved as cable penetration in class H-120, H-60 and H-0400 in steel decks and bulkheads for approved ship cables
as specified in the tables below.
General application: Fire against either side*
- In areas with requirements to maximum steel temperature in load bearing constructions, the bulkhead is approved for
restricted application: Fire against insulated side
Table 1: Approved cable penetration in H-120 steel bulkhead.
| Max. cable | Sleeve | Sleeve |
|---|---|---|
| Type | Size | diameter |
| [mm] | [mm] | [mm] |
| RS | 23 – 125 | 90 |
| RS | 23 – 150 | 96 |
- Bolted sleeves are approved for restricted application only.
Table 2: Approved cable penetration in H-60 steel bulkhead.
| Max. cable | Sleeve | Sleeve |
|---|---|---|
| Type | Size | diameter |
| [mm] | [mm] | [mm] |
| RS | 23 – 125 | 90 |
| RS | 23 – 150 | 96 |
- Bolted sleeves are approved for restricted application only.
Table 3: Approved cable penetration in H-0400 steel bulkhead.
| Max. cable | Sleeve | Sleeve |
|---|---|---|
| Type | Size | diameter |
| [mm] | [mm] | [mm] |
| RS | 23 – 125 | 88 |
- Bolted sleeves are approved for restricted application only.
- The protective coating is not defined as non-combustible and should not be used in accommodation or in enclosed areas.
Table 4: Approved cable penetration in H-120 steel deck.
| Max. cable | Sleeve | Sleeve |
|---|---|---|
| Type | Size | diameter |
| [mm] | [mm] | [mm] |
| RS | 23 – 125 | 88 |
Table 5: Approved cable penetration in H-60 steel deck.
| Max. cable | Sleeve | Sleeve |
|---|---|---|
| Type | Size | diameter |
| [mm] | [mm] | [mm] |
| RS | 23 – 125 | 88 |
Approved for penetration in deck and bulkheads limited to a pressure of 4.00 bar water tightness and 2.67 bar gas
tightness.
For bolted versions with gasket and self-tapping screws, the pressure is limited to 3.33 bar water tightness and 1.67 bar
gas tightness.
| Form code: TA 251 | Revision: 2022-09 | www.dnv.com | Page 2 of 3 |
|---|---|---|---|
| Job Id: | 262.1-001101-22 | ||
| Certificate No: | TAF00000D8 | ||
| Revision No: | 3 |
Each product is to be supplied with its manual for installation/application and maintenance.
Type Approval documentation
Certification in accordance with Class Programme DNV-CP-0338, September 2021.
Test report No. 22N007.12C dated 16 September 1999 from SINTEF, Trondheim, Norway.
Test report No. PG11087 dated 12 February 2003 from DIFT, Hvidovre, Denmark.
Test report No. PG11088 dated 18 February 2003 from DIFT, Hvidovre, Denmark.
Test report No. P703775 dated 7 December 2007 from SP, Borås, Sweden.
Test report No. RS-19/B-036/E dated 21 March 2019 from CTO, Gdansk, Poland.
Test report No. PBG10120A dated 17 December 2021 from DBI, Hvidovre, Denmark.
Water tightness/gas tightness:
Inspection report MLM 010235 dated 21 August 2001 from DNV, Malmö, Sweden.
Inspection report MLM 020133 dated 26 February 2002 from DNV, Malmö, Sweden.
Drawing No. S1573509 Rev. B dated 18 January 2022 from manufacturer.
Drawing No. S1573516 Rev. A dated 12 November 2021 from manufacturer.
Tests carried out
Tested according to IMO FTP Code Part 3 (IMO Res. A.754(18)) and with the hydrocarbon time-temperature curve
specified in ISO 834-3.
Pressure tests with water and Helium according to DNV Type Approval Programme 8.471.19-1.
Marking of product
The product or packing is to be marked with name of manufacturer, type designation and fire-technical rating.
Periodical assessment
DNV’s surveyor is to be given permission to perform Periodical Assessments at any time during the validity of this
certificate and at least every second year. The arrangement is to be in accordance with procedure described in DNV-
CP-0338 Section 4.
| Form code: TA 251 | Revision: 2022-09 | www.dnv.com | Page 3 of 3 |
|---|