W-N-8002-optimized
| 6/22/2021 | XHEZ7.W-N-8002 - Through-penetration Firestop Systems Certified for Canada | UL Product iQ |
Design/System/Construction/Assembly Usage Disclaimer
Authorities Having Jurisdiction should be consulted in all cases as to the particular requirements covering the installation and
use of UL Certified products, equipment, system, devices, and materials.
Authorities Having Jurisdiction should be consulted before construction.
Fire resistance assemblies and products are developed by the design submitter and have been investigated by UL for
compliance with applicable requirements. The published information cannot always address every construction nuance
encountered in the field.
When field issues arise, it is recommended the first contact for assistance be the technical service staff provided by the product
manufacturer noted for the design. Users of fire resistance assemblies are advised to consult the general Guide Information for
each product category and each group of assemblies. The Guide Information includes specifics concerning alternate materials
and alternate methods of construction.
Only products which bear UL’s Mark are considered Certified.
XHEZ - Through-penetration Firestop Systems
XHEZ7 - Through-penetration Firestop Systems Certified for
Canada
See General Information for Through-penetration Firestop Systems
See General Information for Through-penetration Firestop Systems Certified for Canada
System No. W-N-8002
June 16, 2021
ANSI/UL1479 (ASTM E814) CAN/ULC S115
| F Rating — 2 Hr | F Rating — 2 Hr |
| T Ratings — 3/4, 1 and 1-1/4 Hr (See Item 2) | FT Ratings — 3/4, 1 and 1-1/4 Hr (See Item 2) |
| L Rating At Ambient — Less Than 1 CFM per Device | FH Rating — 2 Hr |
| L Rating At 400°F — Less Than 1 CFM per Device | FTH Ratings — 3/4, 1 and 1-1/4 Hr (See Item 2) |
L Rating At Ambient — Less Than 0.5 L/s Per Device
L Rating At 204°C — Less Than 0.5 L/s Per Device
https://iq.ulprospector.com/en/profile?e=3896889 1/3
6/22/2021 XHEZ7.W-N-8002 - Through-penetration Firestop Systems Certified for Canada
  1. Partition Panel Units* — The 2 hr fire rated composite wall assembly shall be constructed of nom 6 in. (152 mm) thick coated steel faced
    Partition Panel Units* (CJMR) installed in the manner specified in Wall and Partition Design No. U059 in the Fire Resistance Directory. Panel
    cutout sized to fit the rectangular outer dimensions and depth of recessed device sleeve. Max size of panel cutout is 6 by 12-13/64 in. (152.5 by
    310 mm). Panel cutout of steel skin is required at both sides of opening. As an option, the steel skin cutout on side of wall opposite firestop
    device can be smaller and of sufficient size to accommodate the passing of the through penetrants. Panel cutout shall extend into the insulation
    core of the panel at one side of wall to accommodate the depth of the recessed firestop device sleeve. Opening can be located on or off panel
    unit joints. After installation of firestop device and through penetrants, retained cutout pieces of the insulation core are used to tightly fill any
    visible voids between and around the penetrant to be flush with face of wall.
DURASYSTEMS BARRIERS INC — DuraWall Panels
  1. Through-Penetrants — Within the loading area for the firestop device, the penetrants may represent a 0 to 100 percent visual fill. Penetrants to
    be installed through the firestop device and the insulation core of the partition panel to pass through the opening. Penetrants to be rigidly
supported on both sides of wall assembly.
A. Cables — The following cable types may be used:
A1. Max 750 kcmil (or smaller) copper conductor shielded or unshielded power cable with polyvinyl chloride (PVC) jacket and
ethylene-propylene rubber (EPR) insulation. When this cable is used, the T, FT and FTH Ratings are 1 hr.
A2. Max 24 pair No. 16 AWG (or smaller) copper conductor shielded or unshielded instrumentation cable with polyvinyl chloride
insulation and jacket materials. When this cable is used, the T, FT and FTH Ratings are 1-1/4 hr.
A3. Max 8 pair No. 16 AWG (or smaller) copper conductor shielded or unshielded instrumentation cable with polyvinyl chloride
insulation and jacket materials. When this cable is used, the T, FT and FTH Ratings are 1 hr.
A4. Max 24 fiber, fiber optic cable with polyvinyl chloride jacket and insulation. When this cable is used, the T, FT and FTH
A5. Max 4 pair No. 24 AWG (or smaller) Cat 5E cables with PVC jacket and insulation. When this cable is used, the F, FT and FTH
A6. Max 4 pair No. 23 AWG (or smaller) Cat 6 cables with PVC jacket and insulation. When this cable is used, the F, FT and FTH
https://iq.ulprospector.com/en/profile?e=3896889 2/3
A7. Max 24 fiber interlocking armored Fiber Optic Cable with polyvinyl chloride jacket and insulation. When this cable is used,
B. Metallic Penetrants —The following types and sizes of metallic penetrants may be used:
B1. Nom 2 in. (51 mm) diam (or smaller) Sch 40 steel conduit. When this conduit is used, the T, FT and FTH Ratings are 3/4 hr.
  1. Firestop System — The firestop system shall consist of the following:
A. Firestop Devices* — Firestop devices each consist of a rectangular steel frame with integral flange, multi diameter elastomeric sealing
modules, steel stay plates and a compression unit consisting of a Roxtec Wedge. Firestop device frame shall be installed into the panel
cutout at one side of wall with the flange of device installed flush against steel skin of partition panel. The rectangular packing area of
each frame shall be filled with multiple rows of multi diameter elastomeric sealing modules with a max of one cable in each sealing
module. The layers of the multi diameter sealing module halves are removed one by one until a max gap of 0.04 in. (1 mm) is formed
between the two module halves. When the number of sealing modules exceeds the number of cables, the solid cylindrical cores of the
unpenetrated sealing modules shall be left in place or “blank” (solid) sealing modules shall be used. During installation of the elastomeric
sealing modules, thin steel stay plates shall be used to separate the rows of sealing modules and to retain the sealing modules within the
steel frame. After installation of the modules, the bolts of the compression unit are tightened to form an effective seal around the
through penetrants and insert modules. Firestop device secured in place with min 1/4 in. (6 mm) diam by min 6-1/2 in. (165 mm) long
washer head lag screws within each preformed hole in device flange around periphery of opening and extending through full thickness of
partition panel. The firestop devices shall be installed in accordance with the accompanying installation instructions.
ROXTEC INTERNATIONAL AB — B-2x1, B-4x1, B-6x1, B-8x1, G-2x1, G-4x1, G-6x1, G-8x1, GH-2x1, GH-4x1, GH-6x1, GH-8x1, GH BG-2X1,
GH BG-4X1, GH BG-6X1, GH BG-8X1, GHM-2x1, GHM-4x1, GHM-6x1, GHM-8x1, GHM BG-2X1, GHM BG-4X1, GHM BG-6X1, GHM BG-8X1,
GOH-2x1, GOH-4x1, GOH-6x1, GOH-8x1, GKOH-2x1, GKOH-4x1, GKOH-6x1, GKOH-8x1, SF-2x1, SF-4x1, SF-6x1, SF-8x1
ROXTEC INC — B-2x1, B-4x1, B-6x1, B-8x1, G-2x1, G-4x1, G-6x1, G-8x1, GH-2x1, GH-4x1, GH-6x1, GH-8x1, GH BG-2X1, GH BG-4X1, GH
BG-6X1, GH BG-8X1, GHM-2x1, GHM-4x1, GHM-6x1, GHM-8x1, GHM BG-2X1, GHM BG-4X1, GHM BG-6X1, GHM BG-8X1, GOH-2x1, GOH-
B. Fill, Void or Cavity Material* — Sealant — Nom 3/8 in. (10 mm) bead of fill material applied around the periphery of the firestop
device frame flange at the interface with the steel skin of the partition panel. In addition, for L Rating, sealant shall be applied on the
device frame flange to seal each screw head location and at the panel seam.
See Fill, Void or Cavity Material (XHHW) category in the Fire Resistance Directory for the names of manufacturers. Any sealant or caulk
material meeting the above specification and bearing the UL Classification Marking may be used.
  • Indicates such products shall bear the UL or cUL Certification Mark for jurisdictions employing the UL or cUL Certification (such as
    Canada), respectively.
Last Updated on 2021-06-16
The appearance of a company’s name or product in this database does not in itself assure that products so identified have been manufactured
under UL’s Follow-Up Service. Only those products bearing the UL Mark should be considered to be Certified and covered under UL’s Follow-Up
Service. Always look for the Mark on the product.
UL permits the reproduction of the material contained in the Online Certification Directory subject to the following conditions: 1. The Guide
Information, Assemblies, Constructions, Designs, Systems, and/or Certifications (files) must be presented in their entirety and in a non-misleading
manner, without any manipulation of the data (or drawings). 2. The statement “Reprinted from the Online Certifications Directory with permission
from UL” must appear adjacent to the extracted material. In addition, the reprinted material must include a copyright notice in the following
format: “© 2021 UL LLC”