Certificate number: 12509/E0 BV
File number: ACI4000/032/005 and 008
Product code: 5300H
This certificate is not valid when presented without the full attached schedule
composed of 7 sections
TYPE APPROVAL CERTIFICATE
This certificate is issued to
ROXTEC International AB
KARLSKRONA - SWEDEN
for the type of product
PIPE, CABLE, DUCT PENETRATIONS IN FIRE DIVISIONS
A-0/A-60 Class Roxtec Sealing System with Multidiameter™ Technology:
RS-Series, RS PPS and RS PPS/S seals for steel divisions
(certified products, sleeve position and achieved performance - see §1)
Requirements:
Bureau Veritas Rules for the Classification of Steel Ships Part C Chapter 4
SOLAS 74, as amended, Regulations II-2/9
IMO Res. MSC.61(67)-(FTP Code) with IMO Res MSC.307(88) (2010 FTP Code) article 8
IMO Res. MSC.307(88) (2010 FTP Code)
IMO MSC.1/Circ. 1488
IMO MSC.1/Circ. 1276
This certificate is issued to attest that Bureau Veritas Marine & Offshore did undertake the relevant approval procedures for the product identified
above which was found to comply with the relevant requirements mentioned above.
This certificate will expire on: 30 Nov 2028
For Bureau Veritas Marine & Offshore,
At BV GOTHENBURG, on 30 Nov 2023,
Hans-erik ERICSSON
This certificate was created electronically and is valid without
signature
This certificate remains valid until the date stated above, unless cancelled or revoked, provided the conditions indicated in the subsequent page(s) are complied
with and the product remains satisfactory in service. This certificate will not be valid if the applicant makes any changes or modifications to the approved product,
which have not been notified to, and agreed in writing with Bureau Veritas Marine & Offshore. Should the specified regulations or standards be amended during
the validity of this certificate, the product(s) is/are to be re-approved prior to it/they being placed on board vessels to which the amended regulations or standards
apply. This certificate is issued within the scope of the General Conditions of Bureau Veritas Marine & Offshore available on the internet site www.veristar.com.
Any Person not a party to the contract pursuant to which this document is delivered may not assert a claim against Bureau Veritas Marine & Offshore for any
liability arising out of errors or omissions which may be contained in said document, or for errors of judgement, fault or negligence committed by personnel of the
Society or of its Agents in establishment or issuance of this document, and in connection with any activities for which it may provide.
The electronic version is available at: VeriSTAR Project Management - Bureau Veritas Marine & Offshore
| BV Mod. Ad.E 530 June 2017 | This certificate consists of 12 page(s) |
|---|
Certificate number: 12509/E0 BV
THE SCHEDULE OF APPROVAL
1. PRODUCT DESCRIPTION:
Roxtec sealing system with MultidiameterTM: RS-series in steel divisions
The Roxtec RS cable and pipe penetration seal consists of two halves with removable layers, making it adaptable to a single
cable or pipe of different sizes. It is available in different versions, RS, RS OMD, RS PE, RS ES, RS BG, or RS EX,
depending on application.
The RS-seal is installed into a steel sleeve that is either welded, bolted, attached through expansion (SLFRS X) or attached
with a nut (SLA) onto the steel division.
Roxtec sealing system with MultidiameterTM: RS PPS/S in steel divisions
The Roxtec RS PPS/S penetration seal consists of two halves with integrated intumescent and removable layers, making it
adaptable to a single pipe of different size.
The RS PPS/S-seal is installed into a steel sleeve that is either welded or bolted onto the steel division.
Roxtec sealing system with MultidiameterTM: RS PPS in steel divisions
The Roxtec RS PPS is a back-to-back solution, consisting of two seals and intumescent sealing strip. Each seal consists of two
halves with removable layers, making it adaptable to single pipe of different size.
The RS PPS-sealing kit is installed into a steel sleeve that is either welded or bolted onto the steel division.
Additional insulation on penetrations and/or cables/pipes:
- should be approved as having the same level of performance as the penetrated division and expected classification of
penetration,
- is to be fitted as shown in the referred Manufacturer’s drawings (see §2) and also according to Manufacturer’s insulation
guidelines.
1.1 – Metal pipes and GRE pipes
1.1.1 – A-60 bulkhead
| RS-Seals | Sleeve type | Pipe | Pipe | Sleeve | Sleeve | Sleeve | Insulation drawing |
|---|---|---|---|---|---|---|---|
| size | material | diameter | length | thickness | position | ||
| (mm) | (mm) | (mm) | |||||
| 23 - 400 | SLRS-Series (1) | Steel | 6 – 330 | 35 - 65 | 4-7 | Any | S1587909 Rev. B dated 20/11/23 |
| ID 1-4 | |||||||
| 23 - 644 | SLRS-Series (1) | Steel | 6 - 558 | 35 - 65 | 4–7 | Unexposed | S1587909 Rev. B dated 20/11/23 |
| — | — | — | — | — | — | — | — |
| ID 5 | |||||||
| 23 - 300 | SLRS-Series (1) | Copper | 6 - 222 | 35 - 65 | 4-7 | Any | S1587909 Rev. B dated 20/11/23 |
| — | — | — | — | — | — | — | — |
| ID 6-9 | |||||||
| 25 - 500 | SLRS-Series (1) | CuNi | 10 - 420 | 35 - 65 | 4-7 | Any | S1587909 Rev. B dated 20/11/23 |
| — | — | — | — | — | — | — | — |
| ID 10-13 | |||||||
| 50 - 125 | SLRS-Series (1) | GRE | 25 - 1040 | 35 - 65 | 4-7 | Any | S1587909 Rev. B dated 20/11/23 |
| — | — | — | — | — | — | — | — |
| ID 14-15 | |||||||
| 25 - 100 | SLRS-Series (1) | Bundle | 8 - 50 | 35 - 65 | 4-7 | Any | S1587909 Rev. B dated 20/11/23 |
| — | — | — | — | — | — | — | — |
| pipe | ID 16 | ||||||
| (steel) | |||||||
| 23 - 150 | SLRS-Series (2) | Steel | 6 - 114 | Up to | 4-7 | Any | S1587906 Rev. B dated 20/11/23 |
| — | — | — | — | — | — | — | — |
| 400 | ID 1-3 | ||||||
| 23 - 150 | SLRS-Series (2) | Copper | 6 - 108 | Up to | 4-7 | Any | S1587906 Rev. B dated 20/11/23 |
| 400 | ID 4-6 | ||||||
| 25 - 150 | SLRS-Series (2) | CuNi | 10 - 108 | Up to | 4-7 | Any | S1587906 Rev. B dated 20/11/23 |
| 400 | ID 7-8 | ||||||
| 50 - 125 | SLRS-Series (2) | GRE | 25 -90 | Up to | 4-7 | Any | S1587906 Rev. B dated 20/11/23 |
| 400 | ID 9 | ||||||
| 25 - 100 | SLRS-Series (2) | Bundle | 8 - 50 | Up to | 4-7 | Any | S1587906 Rev. B dated 20/11/23 |
| pipe | 400 | ID 10 | |||||
| (steel) | |||||||
| 25 - 75 | SLA | Steel | 6 - 30 | 47 - 86 | 4-6 | Any | S1587910 Rev. A dated 29/05/23 |
| — | — | — | — | — | — | — | — |
| ID 1 | |||||||
| 25 - 75 | SLA | Copper | 6 - 34 | 47 - 86 | 4-6 | Any | S1587910 Rev. A dated 29/05/23 |
| — | — | — | — | — | — | — | — |
| ID 2-4 | |||||||
| 25 - 75 | SLA | CuNi | 6 - 34 | 47 - 86 | 4-6 | Any | S1587910 Rev. A dated 29/05/23 |
| — | — | — | — | — | — | — | — |
| ID 5-7 | |||||||
| 25 - 200 | SLFRS X | Steel | 6 - 168 | 65 | 4-7 | Unexposed | S1587913 Rev. A dated 26/05/23 |
| — | — | — | — | — | — | — | — |
| ID 1-2 |
The electronic version is available at: VeriSTAR Project Management - Bureau Veritas Marine & Offshore
| BV Mod. Ad.E 530 June 2017 | This certificate consists of 12 page(s) |
|---|
Certificate number: 12509/E0 BV
| RS-Seals | Sleeve type | Pipe | Pipe | Sleeve | Sleeve | Sleeve | Insulation drawing |
|---|---|---|---|---|---|---|---|
| size | material | diameter | length | thickness | position | ||
| (mm) | (mm) | (mm) | |||||
| 25 - 150 | SLFRS X | Copper | 6 - 108 | 65 | 4-7 | Unexposed | S1587913 Rev. A dated 26/05/23 |
| ID 3-4 | |||||||
| 25 - 150 | SLFRS X | CuNi | 6 - 108 | 65 | 4-7 | Unexposed | S1587913 Rev. A dated 26/05/23 |
| — | — | — | — | — | — | — | — |
| ID 5-6 | |||||||
| (1) SLRS-series includes the following sleeve types: SLRS, SLRS Ex or sleeves equal to dimensions specified in drawing S1586454 Rev A | |||||||
| (2) SL-series are longer versions of the sleeves in SLRS-series |
1.1.2 – A-60 deck
| RS-Seals | Sleeve type | Pipe | Pipe | Sleeve | Sleeve | Sleeve | Insulation drawing |
|---|---|---|---|---|---|---|---|
| size | material | diameter | length | thickness | position | ||
| (mm) | (mm) | (mm) | |||||
| 23 - 400 | SLRS-Series (1) | Steel | 6 - 323 | 35 - 65 | 4-7 | Any | S1587914 Rev. A dated 26/05/23 |
| ID 1-3 | |||||||
| 23 - 644 | SLRS-Series (1) | Steel | 6 - 558 | 35 - 65 | 4-7 | Unexposed | S1587914 Rev. A dated 26/05/23 |
| — | — | — | — | — | — | — | — |
| ID 4 | |||||||
| 23 - 150 | SLRS-Series (1) | Copper | 6 - 108 | 35 - 65 | 4-7 | Any | S1587914 Rev. A dated 26/05/23 |
| — | — | — | — | — | — | — | — |
| ID 5-7 | |||||||
| 25 - 300 | SLRS-Series (1) | Copper | 6 - 225 | 35 - 65 | 4-7 | Any | S1587914 Rev. A dated 26/05/23 |
| — | — | — | — | — | — | — | — |
| ID 8 | |||||||
| 25 - 500 | SLRS-Series (1) | CuNi | 10 - 420 | 35 - 65 | 4-7 | Any | S1587914 Rev. A dated 26/05/23 |
| — | — | — | — | — | — | — | — |
| ID 9-13 | |||||||
| 50 - 1125 | SLRS-Series (1) | GRE | 25 - 1040 | 35 - 65 | 4-7 | Any | S1587914 Rev. A dated 26/05/23 |
| — | — | — | — | — | — | — | — |
| ID 14-16 | |||||||
| 25 - 100 | SLRS-Series (1) | Bundle | 8 - 50 | 35 - 65 | 4-7 | Any | S1587914 Rev. A dated 26/05/23 |
| — | — | — | — | — | — | — | — |
| pipe | ID 17 | ||||||
| (steel) | |||||||
| 23 - 150 | SLRS-Series (2) | Steel | 6 - 114 | Up to | 4-7 | Any | S1587915 Rev. A dated 25/01/23 |
| — | — | — | — | — | — | — | — |
| 400 | ID 1-2 | ||||||
| 23 - 150 | SLRS-Series (2) | Copper | 6 - 108 | Up to | 4-7 | Any | S1587915 Rev. A dated 25/01/23 |
| 400 | ID 3-5 | ||||||
| 25 - 150 | SLRS-Series (2) | CuNi | 10 - 108 | Up to | 4-7 | Any | S1587915 Rev. A dated 25/01/23 |
| 400 | ID 6-8 | ||||||
| 25 - 100 | SLRS-Series (2) | Bundle | 8 - 50 | Up to | 4-7 | Any | S1587915 Rev. A dated 25/01/23 |
| pipe | 400 | ID 9 | |||||
| (steel) | |||||||
| 25 - 75 | SLA | Steel | 6 - 30 | 47 - 86 | 4-6 | Unexposed | S1587929 Rev. A dated 14/06/23 |
| — | — | — | — | — | — | — | — |
| ID 1 | |||||||
| 25 - 75 | SLA | Copper | 6 - 34 | 47 - 86 | 4-6 | Unexposed | S1587929 Rev. A dated 14/06/23 |
| — | — | — | — | — | — | — | — |
| ID 2-3 | |||||||
| 25 - 75 | SLA | CuNi | 6 - 34 | 47 - 86 | 4-6 | Unexposed | S1587929 Rev. A dated 14/06/23 |
| — | — | — | — | — | — | — | — |
| ID 4-5 | |||||||
| 25 - 200 | SLFRS X | Steel | 6 - 168 | 65 | 4-7 | Any | S1587931 Rev. A dated 29/05/23 |
| — | — | — | — | — | — | — | — |
| ID 1-2 | |||||||
| 25 - 150 | SLFRS X | Copper | 6 - 108 | 65 | 4-7 | Any | S1587931 Rev. A dated 29/05/23 |
| — | — | — | — | — | — | — | — |
| ID 3-4 | |||||||
| 25 - 150 | SLFRS X | CuNi | 6 - 108 | 65 | 4-7 | Any | S1587931 Rev. A dated 29/05/23 |
| — | — | — | — | — | — | — | — |
| ID 5-6 | |||||||
| (1) SLRS-series includes the following sleeve types: SLRS, SLRS Ex or sleeves equal to dimensions specified in drawing S1586454 Rev A | |||||||
| (2) SL-series are longer versions of the sleeves in SLRS-series |
** Following on next page**
The electronic version is available at: VeriSTAR Project Management - Bureau Veritas Marine & Offshore
| BV Mod. Ad.E 530 June 2017 | This certificate consists of 12 page(s) |
|---|
Certificate number: 12509/E0 BV
1.1.3 – A-0 bulkhead
| RS-Seals | Sleeve type | Pipe | Pipe | Sleeve | Sleeve | Sleeve | Insulation drawing |
|---|---|---|---|---|---|---|---|
| size | material | diameter | length | thickness | position | ||
| (mm) | (mm) | (mm) | |||||
| 23 - 400 | SLRS-Series (1) | Steel | 6 - 323 | 35 - 65 | 4-7 | Any | S1587933 Rev. B dated 16/11/23 |
| ID 1-3 | |||||||
| 23 - 644 | SLRS-Series (1) | Steel | 6 - 558 | 35 – 65 | 4–7 | Unexposed | S1587933 Rev. B dated 16/11/23 |
| — | — | — | — | — | — | — | — |
| ID 4 | |||||||
| 23 - 300 | SLRS-Series (1) | Copper | 6 - 222 | 35 - 65 | 4-7 | Any | S1587933 Rev. B dated 16/11/23 |
| — | — | — | — | — | — | — | — |
| ID 5-7 | |||||||
| 25 - 500 | SLRS-Series (1) | CuNi | 10 - 420 | 35 - 65 | 4-7 | Any | S1587933 Rev. B dated 16/11/23 |
| — | — | — | — | — | — | — | — |
| ID 8-11 | |||||||
| 50 - 1125 | SLRS-Series (1) | GRE | 25 - 1040 | 35 - 65 | 4-7 | Any | S1587933 Rev. B dated 16/11/23 |
| — | — | — | — | — | — | — | — |
| ID 12-13 | |||||||
| 25 - 100 | SLRS-Series (1) | Bundle | 8 - 50 | 35 - 65 | 4-7 | Any | S1587933 Rev. B dated 16/11/23 |
| — | — | — | — | — | — | — | — |
| pipe | ID 14 | ||||||
| (steel) | |||||||
| 23 - 150 | SLRS-Series (2) | Steel | 6 - 114 | Up to | 4-7 | Any | S1587935 Rev. B dated 16/11/23 |
| — | — | — | — | — | — | — | — |
| 400 | ID 1-3 | ||||||
| 23 - 150 | SLRS-Series (2) | Copper | 6 - 108 | Up to | 4-7 | Any | S1587935 Rev. B dated 16/11/23 |
| 400 | ID 4-6 | ||||||
| 25 - 150 | SLRS-Series (2) | CuNi | 10 - 108 | Up to | 4-7 | Any | S1587935 Rev. B dated 16/11/23 |
| 400 | ID 7-8 | ||||||
| 50 - 125 | SLRS-Series (2) | GRE | 25 -90 | Up to | 4-7 | Any | S1587935 Rev. B dated 16/11/23 |
| 400 | ID 9 | ||||||
| 25 - 100 | SLRS-Series (2) | Bundle | 8 - 50 | Up to | 4-7 | Any | S1587935 Rev. B dated 16/11/23 |
| pipe | 400 | ID 10 | |||||
| (steel) | |||||||
| 25 - 75 | SLA | Steel | 6 - 30 | 47 - 86 | 4-6 | Any | S1587938 Rev. A dated 29/05/23 |
| — | — | — | — | — | — | — | — |
| ID 1 | |||||||
| 25 - 75 | SLA | Copper | 6 - 34 | 47 - 86 | 4-6 | Any | S1587938 Rev. A dated 29/05/23 |
| — | — | — | — | — | — | — | — |
| ID 2-4 | |||||||
| 25 - 75 | SLA | CuNi | 6 - 34 | 47 - 86 | 4-6 | Any | S1587938 Rev. A dated 29/05/23 |
| — | — | — | — | — | — | — | — |
| ID 5-7 | |||||||
| 25 - 200 | SLFRS X | Steel | 6 - 168 | 65 | 4-7 | Unexposed | S1587940 Rev. A dated 29/05/23 |
| — | — | — | — | — | — | — | — |
| ID 1-2 | |||||||
| 25 - 150 | SLFRS X | Copper | 6 - 108 | 65 | 4-7 | Unexposed | S1587940 Rev. A dated 29/05/23 |
| — | — | — | — | — | — | — | — |
| ID 3-4 | |||||||
| 25 - 150 | SLFRS X | CuNi | 6 - 108 | 65 | 4-7 | Unexposed | S1587940 Rev. A dated 29/05/23 |
| — | — | — | — | — | — | — | — |
| ID 5-6 | |||||||
| (1) SLRS-series includes the following sleeve types: SLRS, SLRS Ex or sleeves equal to dimensions specified in drawing S1586454 Rev A | |||||||
| (2) SL-series are longer versions of the sleeves in SLRS-series |
** Following on next page**
The electronic version is available at: VeriSTAR Project Management - Bureau Veritas Marine & Offshore
| BV Mod. Ad.E 530 June 2017 | This certificate consists of 12 page(s) |
|---|
Certificate number: 12509/E0 BV
1.1.4 – A-0 deck
| RS-Seals | Sleeve type | Pipe | Pipe | Sleeve | Sleeve | Sleeve | Insulation drawing |
|---|---|---|---|---|---|---|---|
| size | material | diameter | length | thickness | position | ||
| (mm) | (mm) | (mm) | |||||
| 23 - 400 | SLRS-Series (1) | Steel | 6 - 323 | 35 - 67 | 4-7 | Any | S1587941 Rev. B dated 16/11/23 |
| ID 1-4 | |||||||
| 23 - 644 | SLRS-Series (1) | Steel | 6 - 558 | 35 – 65 | 4–7 | Unexposed | S1587941 Rev. B dated 16/11/23 |
| — | — | — | — | — | — | — | — |
| ID 5 | |||||||
| 23 - 300 | SLRS-Series (1) | Copper | 6 - 225 | 35 - 65 | 4-7 | Any | S1587941 Rev. B dated 16/11/23 |
| — | — | — | — | — | — | — | — |
| ID 6-9 | |||||||
| 25 - 500 | SLRS-Series (1) | CuNi | 10 - 420 | 35 - 65 | 4-7 | Any | S1587941 Rev. B dated 16/11/23 |
| — | — | — | — | — | — | — | — |
| ID 10-14 | |||||||
| 50 - 1125 | SLRS-Series (1) | GRE | 35 - 1040 | 35 - 65 | 4-7 | Any | S1587941 Rev. B dated 16/11/23 |
| — | — | — | — | — | — | — | — |
| ID 15-17 | |||||||
| 25 - 100 | SLRS-Series (1) | Bundle | 8 - 50 | 35 - 65 | 4-7 | Any | S1587941 Rev. B dated 16/11/23 |
| — | — | — | — | — | — | — | — |
| pipe | ID 18 | ||||||
| (steel) | |||||||
| 23 - 150 | SLRS-Series (2) | Steel | 6 - 114 | Up to | 4-7 | Any | S1588591 Rev. A dated 29/05/23 |
| — | — | — | — | — | — | — | — |
| 400 | ID 1-2 | ||||||
| 23 - 150 | SLRS-Series (2) | Copper | 6 - 108 | Up to | 4-7 | Any | S1588591 Rev. A dated 29/05/23 |
| 400 | ID 3-5 | ||||||
| 25 - 150 | SLRS-Series (2) | CuNi | 10 - 108 | Up to | 4-7 | Any | S1588591 Rev. A dated 29/05/23 |
| 400 | ID 6-8 | ||||||
| 25 - 100 | SLRS-Series (2) | Bundle | 8 - 50 | Up to | 4-7 | Any | S1588591 Rev. A dated 29/05/23 |
| pipe | 400 | ID 9 | |||||
| (steel) | |||||||
| 25 - 75 | SLA | Steel | 6 - 30 | 47 - 86 | 4-6 | Unexposed | S1588541 Rev. A dated 14/06/23 |
| — | — | — | — | — | — | — | — |
| ID 1 | |||||||
| 25 – 75 | SLA | Copper | 6 – 34 | 47 – 86 | 4–6 | Unexposed | S1588541 Rev. A dated 14/06/23 |
| — | — | — | — | — | — | — | — |
| ID 2-3 | |||||||
| 25 – 75 | SLA | CuNi | 6 – 34 | 47 – 86 | 4–6 | Unexposed | S1588541 Rev. A dated 14/06/23 |
| — | — | — | — | — | — | — | — |
| ID 4-5 | |||||||
| 25 – 200 | SLFRS X | Steel | 6 – 168 | 65 | 4–7 | Any | S1588592 Rev. A dated 29/05/23 |
| — | — | — | — | — | — | — | — |
| ID 1-2 | |||||||
| 25 - 150 | SLFRS X | Copper | 6 - 108 | 65 | 4-7 | Any | S1588592 Rev. A dated 29/05/23 |
| — | — | — | — | — | — | — | — |
| ID 3-4 | |||||||
| 25 - 150 | SLFRS X | CuNi | 6 - 108 | 65 | 4-7 | Any | S1588592 Rev. A dated 29/05/23 |
| — | — | — | — | — | — | — | — |
| ID 5-6 | |||||||
| (1) SLRS-series includes the following sleeve types: SLRS, SLRS Ex or sleeves equal to dimensions specified in drawing S1586454 Rev A | |||||||
| (2) SL-series are longer versions of the sleeves in SLRS-series |
1.2 – Plastic pipes
1.2.1 – A-60 bulkhead
| RS-Seals | Sleeve Type | Pipe material | Pipe diameter | Sleeve | Insulation drawing |
|---|---|---|---|---|---|
| size | (mm) | position | |||
| 31 - 450 | RS PPS | Thermoplastic* | 16 – 355 | Any | S1587873 Rev. A dated 05/06/23 |
| ID 1-2 | |||||
| 31 - 150 | RS PPS | PE/ALU/PE | 16 – 110 | Any | S1587873 Rev. A dated 05/06/23 |
| — | — | — | — | — | — |
| ID 3-4 | |||||
| 125 - 400 | RS PPS | Pre-insulated | 90 - 315 | Any | S1587873 Rev. A dated 05/06/23 |
| — | — | — | — | — | — |
| thermoplastic pipe | ID 5 | ||||
| 31 – 150 | RS PPS/S | Thermoplastic* | 16 – 110 | Any | S1587875 Rev. A dated 05/06/23 |
| ID 1 | |||||
| 31 – 100 | RS PPS/S | PE/ALU/PE | 16 - 63 | Any | S1587875 Rev. A dated 05/06/23 |
| — | — | — | — | — | — |
| ID 2 | |||||
| 125 – 150 | RS PPS/S | Pre-insulated | 75 - 110 | Any | S1587875 Rev. A dated 05/06/23 |
| — | — | — | — | — | — |
| thermoplastic pipe | ID 3-4 | ||||
| 100 – 125 | RS PPS/S | Pre-insulated | 67 - 96 | Any | S1587875 Rev. A dated 05/06/23 |
| plastic bundle | ID 5 | ||||
| pipe |
*PP, PVC, PB, ABS, PE, PVDF
The electronic version is available at: VeriSTAR Project Management - Bureau Veritas Marine & Offshore
| BV Mod. Ad.E 530 June 2017 | This certificate consists of 12 page(s) |
|---|
Certificate number: 12509/E0 BV
1.2.2 – A-60 deck
| RS-Seals | Sleeve Type | Pipe material | Pipe diameter | Sleeve | Insulation drawing |
|---|---|---|---|---|---|
| size | (mm) | position | |||
| 31 – 450 | RS PPS | Thermoplastic* | 16 - 355 | Any | S1587874 Rev. A dated 07/06/23 |
| ID 1-2 | |||||
| 31 -150 | RS PPS | PE/ALU/PE | 16 – 110 | Unexposed | S1587874 Rev. A dated 07/06/23 |
| — | — | — | — | — | — |
| ID 3 | |||||
| 125 - 400 | RS PPS | Pre-insulated | 90 - 315 | Any | S1587874 Rev. A dated 07/06/23 |
| — | — | — | — | — | — |
| thermoplastic | ID 4 | ||||
| pipe | |||||
| 100 – 125 | RS PPS | Pre-insulated | 67 - 96 | Unexposed | S1587874 Rev. A dated 07/06/23 |
| — | — | — | — | — | — |
| plastic bundle | ID 5 | ||||
| pipe | |||||
| 31 – 150 | RS PPS/S | Thermoplastic* | 16 – 110 | Any | S1587876 Rev. B dated 16/11/23 |
| — | — | — | — | — | — |
| ID 1 | |||||
| 31 – 125 | RS PPS/S | PE/ALU/PE | 16 - 75 | Any | S1587876 Rev. B dated 16/11/23 |
| — | — | — | — | — | — |
| ID 2-3 | |||||
| 31 – 75 | RS PPS/S | PE/ALU/PE with | 16 - 50 | Any | S1587876 Rev. B dated 16/11/23 |
| — | — | — | — | — | — |
| armaflex | ID 4 | ||||
| 68 – 100 | RS PPS/S | Plastic bundle | 36 – 60 | Any | S1587876 Rev. B dated 16/11/23 |
| pipe | ID 5 | ||||
| 100 – 125 | RS PPS/S | Pre-insulated | 67 – 96 | Any | S1587876 Rev. B dated 16/11/23 |
| plastic bundle | ID 6 | ||||
| pipe | |||||
| 125 – 150 | RS PPS/S | Pre-insulated | 75 – 110 | Any | S1587876 Rev. B dated 16/11/23 |
| — | — | — | — | — | — |
| thermoplastic | ID 7 | ||||
| pipe |
*PP, PVC, PB, ABS, PE, PVDF
1.2.3 – A-0 bulkhead
| RS-Seals | Sleeve Type | Pipe material | Pipe diameter | Sleeve | Insulation drawing |
|---|---|---|---|---|---|
| size | (mm) | position | |||
| 31 - 450 | RS PPS | Thermoplastic* | 16 - 355 | Any | S1587877 Rev. A dated 07/06/23 |
| ID 1-2 | |||||
| 31 - 150 | RS PPS | PE/ALU/PE | 16 – 110 | Any | S1587877 Rev. A dated 07/06/23 |
| — | — | — | — | — | — |
| ID 3-4 | |||||
| 125 - 400 | RS PPS | Pre-insulated | 90 - 315 | Any | S1587877 Rev. A dated 07/06/23 |
| — | — | — | — | — | — |
| thermoplastic | ID 5 | ||||
| pipe | |||||
| 31 – 150 | RS PPS/S | Thermoplastic* | 16 – 110 | Any | S1587879 Rev. A dated 15/06/23 |
| — | — | — | — | — | — |
| ID 1-2 | |||||
| 31 – 100 | RS PPS/S | PE/ALU/PE | 16 - 63 | Any | S1587879 Rev. A dated 15/06/23 |
| — | — | — | — | — | — |
| ID 3 | |||||
| 125 –150 | RS PPS/S | Pre-insulated | 75 – 110 | Any | S1587879 Rev. A dated 15/06/23 |
| — | — | — | — | — | — |
| thermoplastic | ID 4-5 | ||||
| pipe | |||||
| 100 – 125 | RS PPS/S | Pre-insulated | 67 - 96 | Any | S1587879 Rev. A dated 15/06/23 |
| — | — | — | — | — | — |
| plastic bundle | ID 6 | ||||
| pipe |
*PP, PVC, PB, ABS, PE, PVDF
** Following on next page**
The electronic version is available at: VeriSTAR Project Management - Bureau Veritas Marine & Offshore
| BV Mod. Ad.E 530 June 2017 | This certificate consists of 12 page(s) |
|---|
Certificate number: 12509/E0 BV
1.2.4 – A-0 deck
| RS-Seals | Sleeve Type | Pipe material | Pipe diameter | Sleeve | Insulation drawing |
|---|---|---|---|---|---|
| size | (mm) | position | |||
| 31 – 450 | RS PPS | Thermoplastic* | 16 - 355 | Any | S1587878 Rev. A dated 07/06/23 |
| ID 1-2 | |||||
| 31 – 150 | RS PPS | PE/ALU/PE | 16 - 32 | Any | S1587878 Rev. A dated 07/06/23 |
| — | — | — | — | — | — |
| ID 3-4 | |||||
| 125 – 400 | RS PPS | Pre-insulated | 90 - 315 | Any | S1587878 Rev. A dated 07/06/23 |
| — | — | — | — | — | — |
| thermoplastic | ID 5 | ||||
| pipes | |||||
| 100 - 125 | RS PPS | Pre-insulated | 67 - 96 | Unexposed | S1587878 I Rev. A dated 07/06/23 |
| — | — | — | — | — | — |
| plastic bundle | ID 6 | ||||
| pipe | |||||
| 31 - 150 | RS PPS/S | Thermoplastic* | 16 - 110 | Any | S1587080 Rev. A dated 07/06/23 |
| — | — | — | — | — | — |
| ID 1 | |||||
| 31 - 125 | RS PPS/S | PE/ALU/PE | 16 - 75 | Any | S1587080 Rev. A dated 07/06/23 |
| — | — | — | — | — | — |
| ID 2-3 | |||||
| 31 – 125 | RS PPS/S | PE/ALU/PE with | 16 - 75 | Any | S1587080 Rev. A dated 07/06/23 |
| — | — | — | — | — | — |
| armaflex | ID 4 | ||||
| 68-100 | RS PPS/S | Plastic bundle | 36 - 60 | Any | S1587080 Rev. A dated 07/06/23 |
| pipes | ID 5 | ||||
| 100-125 | RS PPS/S | Pre-insulated | 67 - 96 | Any | S1587080 Rev. A dated 07/06/23 |
| plastic bundle | ID 6 | ||||
| pipe | |||||
| 125-150 | RS PPS/S | Pre-insulated | 75 - 110 | Any | S1587080 Rev. A dated 07/06/23 |
| — | — | — | — | — | — |
| thermoplastic pipe | ID 7 | ||||
| *PP, PVC, PB, ABS, PE, PVDF |
1.3 – Cables
1.3.1 – A-60 bulkhead
| RS-Seals | Sleeve type | Cable | Cable | Sleeve | Sleeve | Sleeve | Insulation drawing |
|---|---|---|---|---|---|---|---|
| size | diameter | length | thickness | position | |||
| (mm) | (mm) | (mm) | |||||
| 23 - 150 | SLRS-Series (1) | Marine | Up to 100 | 47 - 86 | 4-7 | Any | S1587074 Rev. A dated 30/05/23 |
| Cable | ID 1-2 | ||||||
| 25 - 75 | SLA | Marine | Up to 32 | 47 - 86 | 4-6 | Any | S1587072 Rev. A dated 30/05/23 |
| Cable | ID 1-3 | ||||||
| 23 – 125 | SLFRS-X | Marine | Up to 86 | 65 | 4-7 | Unexposed | S1587076 Rev. A dated 30/05/23 |
| Cable | ID 1 | ||||||
| 25 - 125 | SLRS-Series (2) | Marine | Up to 90 | Up to 400 | 4-7 | Any | S1587078 Rev. A dated 30/05/23 |
| Cable | ID 1 | ||||||
| (1) SLRS-series includes the following sleeve types: SLRS, SLRS Ex or sleeves equal to dimensions specified in drawing S1586454 Rev A | |||||||
| (2) SL-series are longer versions of the sleeves in SLRS-series |
1.3.2 – A-60 deck
| RS-Seals | Sleeve type | Cable | Cable | Sleeve | Sleeve | Sleeve | Insulation drawing |
|---|---|---|---|---|---|---|---|
| size | diameter | length | thickness | position | |||
| (mm) | (mm) | (mm) | |||||
| 23 – 150 | SLRS-Series (1) | Marine | Up to 100 | 47 - 86 | 4-7 | Any | S1587074 Rev. A dated 30/05/23 |
| Cable | ID 3 | ||||||
| 25 – 75 | SLA | Marine | Up to 32 | 47 - 86 | 4-6 | Any | S1587072 Rev. A dated 30/05/23 |
| Cable | ID 4-6 | ||||||
| 25 – 125 | SLFRS-X | Marine | Up to 90 | 65 | 4-7 | Exposed | S1587076 Rev. A dated 30/05/23 |
| Cable | ID 2 | ||||||
| 25 - 125 | SLRS-Series (2) | Marine | Up to 90 | Up to 400 | 4-7 | Any | S1587078 Rev. A dated 30/05/23 |
| Cable | ID 2 | ||||||
| (1) SLRS-series includes the following sleeve types: SLRS, SLRS Ex or sleeves equal to dimensions specified in drawing S1586454 Rev A | |||||||
| (2) SL-series are longer versions of the sleeves in SLRS-series |
The electronic version is available at: VeriSTAR Project Management - Bureau Veritas Marine & Offshore
| BV Mod. Ad.E 530 June 2017 | This certificate consists of 12 page(s) |
|---|
Certificate number: 12509/E0 BV
1.3.3 – A-0 bulkhead
| RS-Seals | Sleeve type | Cable | Cable | Sleeve | Sleeve | Sleeve | Insulation drawing |
|---|---|---|---|---|---|---|---|
| size | diameter | length | thickness | position | |||
| (mm) | (mm) | (mm) | |||||
| 23 – 150 | SLRS-Series (1) | Marine | Up to | 47 - 86 | 4-7 | Any | S1587063 Rev. B dated 16/11/23 |
| Cable | 100 | ID 1 | |||||
| 25 - 75 | SLA | Marine | Up to 33 | 47 - 86 | 4-6 | Any | S1587065 Rev. A dated 09/06/23 |
| Cable | ID 1-3 | ||||||
| 23 – 125 | SLFRS-X | Marine | Up to 86 | 65 | 4-7 | Unexposed | S1587079 Rev. A dated 30/05/23 |
| Cable | ID 1 | ||||||
| 25 - 125 | SLRS-Series (2) | Marine | Up to 90 | Up to 400 | 4-7 | Any | S1588275 Rev. A dated 30/05/23 |
| Cable | ID 1 | ||||||
| (1) SLRS-series includes the following sleeve types: SLRS, SLRS Ex or sleeves equal to dimensions specified in drawing S1586454 Rev A | |||||||
| (2) SL-series are longer versions of the sleeves in SLRS-series |
1.3.4 – A-0 deck
| RS-Seals | Sleeve type | Cable | Cable | Sleeve | Sleeve | Sleeve | Insulation drawing |
|---|---|---|---|---|---|---|---|
| size | diameter | length | thickness | position | |||
| (mm) | (mm) | (mm) | |||||
| 23 - 125 | SLRS-Series (1) | Marine | Up to 86 | 47 - 86 | 4-7 | Any | S1587063 Rev. B dated 16/11/23 |
| Cable | ID 2 | ||||||
| 25 - 75 | SLA | Marine | Up to 32 | 47 - 86 | 4-6 | Any | S1587065 Rev. A dated 09/06/23 |
| Cable | ID 4-6 | ||||||
| 25 – 125 | SLFRS-X | Marine | Up to 90 | 65 | 4-7 | Exposed | S1587079 Rev. A dated 30/05/23 |
| Cable | ID 2 | ||||||
| 25 - 125 | SLRS-Series (2) | Marine | Up to 90 | Up to 400 | 4-7 | Any | S1588275 Rev. A dated 30/05/23 |
| Cable | ID 2 | ||||||
| (1) SLRS-series includes the following sleeve types: SLRS, SLRS Ex or sleeves equal to dimensions specified in drawing S1586454 Rev A | |||||||
| (2) SL-series are longer versions of the sleeves in SLRS-series |
2. DOCUMENTS AND DRAWINGS:
As per the Manufacturer’s insulation drawings quoted in tables in §1.
3. TEST REPORTS:
3.1 – Metal pipes
3.1.1.1 – A-60 bulkhead
| Test report N° | Dated | Laboratory |
|---|
| PX05454 | 8th September 2011 | SP, Sweden |
| PGA10650 | 18th May 2015 | DBI, Denmark |
| 4P08662 | 8th June 2015 | SP, Sweden |
| 4P06068 | 17th January 2015 | SP, Sweden |
| 6P04351 | 22nd June 2016 | SP, Sweden |
| RS-18/B-022/E | 29th January 2018 | CTO, Poland |
| RS-18/B-485/E | 10th December 2018 | CTO, Poland |
| RS-19/B-035/E | 25th February 2019 | CTO, Poland |
| RS-19/B-355/E | 16th October 2019 | CTO, Poland |
| RS-20/B-017/E | 23rd January 2020 | CTO, Poland |
| PGB10020A | 5th May 2020 | DBI, Denmark |
| RS-20/B-191/E | 5th June 2020 | CTO, Poland |
| RS-21/B-241/E | 30th June 2021 | CTO, Poland |
| RS-21/B-445/E | 7th October 2021 | CTO, Poland |
| RS-21/B-519/E | 15th December 2021 | CTO, Poland |
| RS-22/B-336/E | 28th October 2022 | CTO, Poland |
The electronic version is available at: VeriSTAR Project Management - Bureau Veritas Marine & Offshore
| BV Mod. Ad.E 530 June 2017 | This certificate consists of 12 page(s) |
|---|
Certificate number: 12509/E0 BV
| Test report N° | Dated | Laboratory |
|---|
| RS-22/B-395/E | 15th November 2022 | CTO, Poland |
| PGB10233A | 12th December 2022 | DBI, Denmark |
All tests as per IMO 2010 FTP Code, Annex 1, part 3
3.1.2 – A-60 deck
| Test report N° | Dated | Laboratory |
|---|---|---|
| 09-346E | 11th December 2009 * | RIME, Japan |
| 4P07023 | 4th February 2015 | SP, Sweden |
| PGA10649 | 18th May 2015 | DBI, Denmark |
| PGA10800A | 26th May 2016 | DBI, Denmark |
| 6P02249 | 17th August 2016 | SP, Sweden |
| 7P02167 | 7th August 2017 | SP, Sweden |
| PGA10871A | 17th November 2017 | DBI, Denmark |
| RS-18/B-023/E | 29th January 2018 | CTO, Poland |
| RS-18/B-484/E | 10th December 2018 | CTO, Poland |
| RS-19/B-356/E | 18 October 2019 | CTO, Poland |
| PGA11611A | 11th January 2020 | DBI, Denmark |
| PGB10032A | 1st July 2020 | DBI, Denmark |
| PGB10047A | 30th November 2020 | DBI, Denmark |
| PGB10111A rev.1 | 20th September 2021 | DBI, Denmark |
| PGB10118A | 15th November 2021 | DBI, Denmark |
| PGB10172A | 3rd May 2022 | DBI, Denmark |
| RS-22/B-337/E | 28th October 2022 | CTO, Poland |
| All tests as per IMO 2010 FTP Code, Annex 1, part 3, except * as per per IMO FTP Code, Annex 1, part 3 [test standard:IMO |
Resolution A.754(18)].
3.1.3 – A-0 bulkhead
| Test report N° | Dated | Laboratory |
|---|---|---|
| RS-20/B-081/E | 31st March 2020 | CTO, Poland |
| RS-21/B-517/E | 10th November 2021 | CTO, Poland |
| PGB10178A | 4th November 2022 | DBI, Denmark |
| All tests as per IMO 2010 FTP Code, Annex 1, part 3. |
3.1.4 – A-0 deck
| Test report N° | Dated | Laboratory |
|---|---|---|
| RS-18/B-292/E | 13th September 2018 | CTO, Poland |
| PGA11302A | 16th January 2019 | CTO, Poland |
| PGA11610A | 10th January 2020 | DBI, Denmark |
| PGB10110A | 27th April 2021 | DBI, Denmark |
| PGB10119A | 15th November 2021 | DBI, Denmark |
| All tests as per IMO 2010 FTP Code, Annex 1, part 3. |
** Following on next page**
The electronic version is available at: VeriSTAR Project Management - Bureau Veritas Marine & Offshore
| BV Mod. Ad.E 530 June 2017 | This certificate consists of 12 page(s) |
|---|
Certificate number: 12509/E0 BV
3.2 – Plastic pipes
3.2.1 – A-60 bulkhead
| Test report N° | Dated | Laboratory |
|---|---|---|
| P902394 | 25th May 2009 * | SP, Sweden |
| 6P10024 | 7th Mars 2017 | SP, Sweden |
| RS_19_B_355_E | 16th October 2019 | CTO, Poland |
| RS_19_B_424_E | 27th November 2019 | CTO, Poland |
| 8P07094 | 16th January 2020 | SP, Sweden |
| RS-20_B-083E | 20th April 2020 | CTO, Poland |
| PGB10030A | 16th July 2020 | DBI, Denmark |
| All tests as per IMO 2010 FTP Code, Annex 1, part 3, except * as per per IMO FTP Code, Annex 1, part 3 [test standard:IMO |
Resolution A.754(18)].
3.2.2 – A-60 deck
| Test report N° | Dated | Laboratory |
|---|---|---|
| 09-346E | 27th February 2009 * | RIME, Japan |
| PGA10025 | 22nd December 2011 * | DBI, Denmark |
| PGA10141 | 10th July 2012 | DBI, Denmark |
| 7P02167 | 7th August 2017 | SP, Sweden |
| RS-18_B-023_E | 29th January 2018 | CTO, Poland |
| 8P04040 | 16th August 2018 | SP, Sweden |
| RS-18_B-484_E | 10th December 2018 | CTO, Poland |
| RS_19_B_256_E | 20th August 2019 | CTO, Poland |
| RS_19_B_356_E | 18th October 2019 | CTO, Poland |
| PGB10113A | 23rd July 2021 | DBI, Denmark |
| PGB10116A | 2nd August 2021 | DBI, Denmark |
| PGB10118A | 15th November 2021 | DBI, Denmark |
| PGB10177A | 4th November 2022 | DBI, Denmark |
| All tests as per IMO 2010 FTP Code, Annex 1, part 3, except * as per per IMO FTP Code, Annex 1, part 3 [test standard:IMO |
Resolution A.754(18)].
3.2.3 – A-0 bulkhead
| Test report N° | Dated | Laboratory |
|---|---|---|
| RS-18_B-291_E | 20th August 2018 | CTO, Poland |
| RS-18_B-293_E | 13th September 2018 | CTO, Poland |
| PGA11301A | 22nd November 2018 | DBI, Denmark |
| 8P07094 | 23rd September 2019 | DBI, Denmark |
| RS-21_B-240E | 30th June 2021 | CTO, Poland |
| All tests as per IMO 2010 FTP Code, Annex 1, part 3. |
3.2.4 – A-0 deck
| Test report N° | Dated | Laboratory |
|---|---|---|
| RS-18_B-292_E | 13th September 2018 | CTO, Poland |
| PGA11302A | 16th January 2019 | DBI, Denmark |
| All tests as per IMO 2010 FTP Code, Annex 1, part 3. |
The electronic version is available at: VeriSTAR Project Management - Bureau Veritas Marine & Offshore
| BV Mod. Ad.E 530 June 2017 | This certificate consists of 12 page(s) |
|---|
Certificate number: 12509/E0 BV
4. APPLICATION / LIMITATION:
4.1 - Approved for use:
- in A-15, A-30, A-60 class steel divisions, with fire insulation as described in §1,
- in A-0 class steel divisions, with local fire insulation arrangement (on the penetration itself as described in §1 and
200 mm around) or without fire insulation.
4.2 - The pipe penetration system has only been evaluated with regard to its fire resistance only. For installation in watertight
bulkhead below the bulkhead deck, specific rules may require to subject the pipe penetrations to a prototype test of
watertightness after having undergone the standard fire test for A-class divisions described in IMO 2010 FTP Code Annex 1
Part 3.
5. PRODUCTION SURVEY REQUIREMENTS:
5.1 - The “A-Class Single-Cable or Single-Pipe Sealing System with Multidiameter Technology, RS-series seals” are to be
supplied by ROXTEC International AB in compliance with the type described in this certificate.
5.2 - This type of product is within the category HBV of Bureau Veritas Rule Note NR320 and as such does not require a BV
product certificate.
5.3 - ROXTEC International AB has to make the necessary arrangements to have its works recognized by Bureau Veritas in
compliance with the requirements of NR320 for HBV products.
6. MARKING OF PRODUCT:
The product or packing is to be marked with Manufacturer name, type, designation and fire-technical rating.
7. OTHERS:
7.1 - It is ROXTEC International AB’s responsibility to inform shipbuilders or their sub-contractors of the proper methods of
fitting, use and general maintenance of the approved equipment and the conditions of this approval.
7.2 - This certificate supersedes the Type Approval Certificate N° 12509/D1 BV issued on 29/01/2020 by the Society.
7.3 - Testing of the penetrations for gastightness and watertightness as per following inspection reports, witnessed by Third
Party surveyor (DNV):
7.3.1 – Metal pipes
| Statement N14254FG | dated 30/04/2021 issued by DNV Welded sleeves - GRE pipe, RS 1125 |
|---|---|
| Statement N1421782 | dated 01/09/2021 issued by DNV Welded sleeves – Steel pipes, RS 23-64 |
| Inspection report MLM060561 | dated 01/12/2006 issued by DNV Welded sleeves - GRE pipe, RS 68-500 / |
| Bundle pipes, RS 43-100 | |
| Inspection report MLM 030473-1 dated 27/01/2003 issued by DNV SLFRS X – RS 223-200, test of expansion sleeve function | |
| Inspection report MLM090673 | dated 08/10/2009 issued by DNV SLFO/RI sleeve, RS 23-644, test for bolted openable |
| — | — |
| sleeves | |
| Statement N142G50V | dated 11/11/2022 issued by DNV Welded long sleeves - Steel pipes, RS 23-150 |
| — | — |
| Statement N141EX8Z rev.2 | dated 10/08/2017 issued by DNV SLA sleeve, RS 25-100 |
| Statement N142JK51 | dated 27/02/2023 issued by DNV Bolted sleeves – RS 23-150/SLFRS |
7.3.2 – Plastic pipes
| Inspection report MLM060511 | dated 28/02/2006 issued by DNV Plastic pipes, RS-400 |
|---|---|
| Inspection report MLM070656 | dated 18/04/2007 issued by DNV Plastic pipes, RS PPS 31-175 |
| Statement N141ZEM0 | dated 15/05/2020 issued by DNV Thermoplastic pipes, RS PPS/S 31–150 |
| Statement N141ZEM1 | dated 15/05/2020 issued by DNV Pre-insulated thermoplastic pipes, RS PPS 125–400 |
| Statement N141ZEM2 | dated 15/05/2020 issued by DNV Pre-insulated thermoplastic pipes, RS PPS/S 125–150 |
| Statement N142299W rev.1 | dated 09/11/2020 issued by DNV Thermoplastic pipes, RS PPS 31–450 |
| Survey report SKM-04-4088 | dated 16/06/2004 issued by DNV Plastic pipes, RS PPS 31–150 |
7.3.3 – Cables
| Inspection report MLM010235 | dated 21/08/2001 issued by DNV Cables, RS 23–50 and RS 125 |
|---|---|
| Inspection report MLM020133 | dated 26/02/2002 issued by DNV Cables,RS 23-150 OMD |
| Inspection report MLM020406 | dated 07/05/2002 issued by DNV Cables, RS 23-125 |
| Inspection report MLM030473 | dated 27/01/2003 issued by DNV Cables, SLFRS X, RS 23-200 |
| Statement N141EX8Z rev.2 | dated 10/08/2017 issued by DNV SLA sleeve, RS 25-100 |
The electronic version is available at: VeriSTAR Project Management - Bureau Veritas Marine & Offshore
| BV Mod. Ad.E 530 June 2017 | This certificate consists of 12 page(s) |
|---|
Certificate number: 12509/E0 BV
| Statement N142G50V | dated 11/11/2022 issued by DNV Long sleeves - Cables, RS 23 -150 |
|---|---|
| Statement N1428HVZ | dated 24/11/2021 issued by DNV Cables, RS BG 25–150 |
Tightness performances:
| Sleeve type | Mounting option | Watertightness | Gastightness |
|---|---|---|---|
| SLRS-Series (1) | Welded | 6 bar | 3 bar |
| SLFRS-Series (2) | Bolted | 3,75 bar | 1.5 bar |
| SLFO-Series (2) | Bolted openable | 2 bar | 1 bar |
| SLFRS X | Expansion | 6 bar | 3 bar |
| SLA | Bolted | 4.5 bar | 1.5 bar |
| SL-Series (3) | Welded | 3 bar | 1.5 bar |
| Sleeve type | Pipe material | Watertightness | Gas tightness |
| SL PPS | Thermoplastic | 6 bar | 3 bar |
| SL PPS/S | Thermoplastic | 6 bar | 3 bar |
| SL PPS | Pre-insulated thermoplastic | 3 bar | 1,5 bar |
| SL PPS/S | Pre-insulated thermoplastic | 3 bar | 1,5 bar |
(1) SLRS-series includes the following sleeve types: SLRS, SLRS Ex or sleeves equal to Roxtec dimensions
specified in drawing S1586454 Rev A
(2) Installed with pre-punched gasket
(3) SL-series are longer versions of the sleeves in SLRS-series
*** END OF CERTIFICATE ***
The electronic version is available at: VeriSTAR Project Management - Bureau Veritas Marine & Offshore
| BV Mod. Ad.E 530 June 2017 | This certificate consists of 12 page(s) |
|---|