Certificate number: 15027/D2 BV
File number: ACI4000/032/007
Product code: 5302H
CABLE PENETRATIONS IN FIRE DIVISIONS
H-0 / H-30 / H-60 / H-120 Class Cable Penetrations
Cable sealing system with multidiameter technology,
S-series, R-series and RS-seals
(For details of approved configurations, see §1)
Bureau Veritas Rules for the Classification of Offshore Units - Part C, Chapter 4
IMO Res. MSC.307(88) (2010 FTP Code)
IMO Res. MSC.61(67)-(FTP Code) with IMO Res MSC.307(88) (2010 FTP Code) article 8
IMO MSC/Circ.1120
IMO MSC.1/Circ.1488
This certificate will expire on: 04 May 2026
At BV GOTHENBURG, on 15 Mar 2022,
Torbjorn Ygesjo
| BV Mod. Ad.E 530 June 2017 | This certificate consists of 9 page(s) |
1. PRODUCT DESCRIPTION:
H Class ROXTEC cable sealing systems with multidiameter technology
Roxtec S-series frames
Consisting of Roxtec S-series frame (S, SO, SF, SFO, SR, SK, SRC r20&r40, SBTB, SRBTB) in sizes 1 - 8 and combinations
thereof, welded or bolted to the steel divisions; filled with Roxtec RM modules (standard, Ex or EMC, PE, ES, BG, BGB).
Assembled with Roxtec Wedge kit or Roxtec EMC, Ex Wedge kit.
For bolted configurations, 3 mm thick EPDM rubber sealing strips are installed in between the Roxtec frames and the division.
Overview (See below view “details of the cable transits” for approved configurations):
Single frames in size 1-8
Filling ratio
| Classification | Orientation |
| (cable area relative to total opening area) | |
| H-0 | DECK |
| H-60 | DECK |
| BULKHEAD | 0 ~ 33 % |
| H-120 | DECK |
| BULKHEAD | 0 ~ 18 % |
Combination frames of size 1-8
Filling ratio
| H-0 | DECK |
| H-60 | DECK |
| H-120 | DECK |
| BULKHEAD | 0 ~ 13% |
** Following on next page**
Details of the cable transits:
Classification: H0 (deck)
| Type | Size | Depth | Installation / | Design of the | Maximum | Filling ratio |
| insulation | insulation | cable diameter | ||||
| arrangement | system (see | |||||
| table below) | ||||||
| SBTB / SRBTB | 2x1 | Min 200 mm | N°1 drawing | (1) | ∅ 21 mm | 0~15 % |
| S1554321 | Insulation | |||||
| located with a | ||||||
| length of | ||||||
| 200 mm | ||||||
| around the | ||||||
| transit | ||||||
| SBTB / SRBTB | 2x1 | Min 320 mm | N°2 drawing | / | ∅ 20 mm | 0~15 % |
| S1554321 | ||||||
| SK | 2x1~8x1 | Min 600 mm | N°3 drawing | / | ∅ 89 mm | 0 ~28 % |
| S1554321 | ||||||
| S / SO / SF / SFO / | 1x1~8x1 | 60 mm | N°4 drawing | (2) | ∅ 62 mm | 0 ~13 % |
| SR /SRC r20&r40 | S1554321 | Insulation | ||||
| length of | ||||||
| 450 mm | ||||||
| around the | ||||||
| transit | ||||||
| SBTB / SRBTB | Single frame | Min 320 mm | N°2 drawing | / | ∅ 68 mm | 0 ~4 % |
| or | S1554321 | |||||
| combination |
frame with a
maximum
number of 6
openings not
exceeding
size 8
| S / SO / SR /SRC | Single frame | 60 mm | N°4 drawing | (3) | ∅ 82 mm | 0 ~ 12% |
| r20&r40 | or | S1554321 | Insulation | |||
| combination | located with a | |||||
| frame with a | length of | |||||
| maximum | 450 mm | |||||
| number of 4 | around the | |||||
| openings not | transit | |||||
| exceeding |
size 8
| SBTB / SRBTB | Single frame | Min 200 mm | N°1 drawing | (4) | ∅ 89 mm | 0 ~5 % |
| or | S1554321 | Insulation | ||||
| maximum | 200 mm | |||||
| number of | around the | |||||
| 2 rows, | transit | |||||
| 5 columns and |
10 openings
not exceeding
size 6
Classification: H60 (deck)
| S / SO / SR /SRC | 1x1 ~ 8x1 | 60 mm | N°1 drawing | (2) | ∅ 62 mm | 0 ~14 % |
| r20&r40 | S1554279 | |||||
| S / SO / SR /SRC | Single frame or | 60 mm | N°2 drawing | (3) | ∅ 82 mm | 0 ~12 % |
| r20&r40 | combination | S1554279 | ||||
| frame with a |
maximum
number of 4
openings not
exceeding size 8
Classification: H60 (bulkhead)
| S / SO / SR /SRC | Single frame or | 60 mm | N°3 drawing | (5) | ∅ 96 mm | 0 ~ 33 % |
| frame with a | (see §4.2) | |||||
| maximum number |
of 6 openings not
exceeding size 8
| SK | 1x1 ~ 8x2 | 200 mm | N°1 drawing | (6) | ∅ 103 mm | 0 ~ 33% |
| S1554304 | ||||||
| SK / SBTB / SRBTB | Combination | 200 mm | N°2 drawing | (7) | ∅ 103 mm | 0 ~ 32% |
| frame with a | S1554304 | |||||
| maximum number |
of 4 openings not
exceeding size 8
| S / SO / SR /SRC | 1x1 ~ 8x1 | 60 mm | N°3 drawing | (8) | ∅ 49 mm | 12% ~ 18 % |
| r20&r40 | S1554304 | |||||
| (see §4.2) | ||||||
| S / SO / SR /SRC | Single frame or | 60 mm | N°3 drawing | (8) | ∅ 49 mm | 18% with |
| r20&r40 | combination | S1554304 | cables | |||
| frame with a | (see §4.2) | evenly | ||||
| maximum number | spread | |||||
| of 6 openings not |
exceeding size 8
| SBTB / SRBTB | Single frame or | 200 mm | N°4 drawing | (9) | ∅ 21 mm | 0 ~ 11.7% |
| combination | S1554304 | |||||
| maximum number |
of 6 openings not
exceeding size 8
Classification: H120 (deck)
| Type | Size | Depth | Installation / | Design of | Maximum | Filling ratio |
| insulation | the | cable diameter | ||||
| arrangement | insulation | |||||
| system (see | ||||||
| S / SO / SF / SFO / | Single frame or | 60 mm | N°1 or N°2 | (10) | ∅ 98 mm | 0 ~15 % |
| SR /SRC r20&r40 | combination | drawing | ||||
| frame with a | S1554312 | |||||
| maximum |
number of 4
openings not
exceeding size 8
| S / SO / SF / SFO / | Single frame or | 60 mm | N°1 drawing | (10) | ∅ 98 mm | 0 ~29 % |
| SR /SRC r20&r40 | combination | S1554312 | ||||
| frame with a |
maximum
number of 2
openings not
exceeding size 8
| S / SO / SF / SFO / | 1x1 ~ 8x1 | 60 mm | N°3 drawing | (11) | ∅ 47 mm | 0 ~14 % |
| SR /SRC r20&r40 | S1554309 | |||||
| S / SO / SF / SFO / | Single frame or | 60 mm | N°4 drawing | (10) | ∅ 98 mm | 0 ~15 % |
| SR /SRC r20&r40 | combination | S1554309 | ||||
| frame with a |
maximum
number of 4
openings not
exceeding size 8
Classification: H120 (bulkhead)
| S / SO / SF / SFO / | 1x1 ~ 6x1 | 60 mm | N°1 drawing | (12) | ∅ 54 mm | 0 ~ 18 % |
| (see §4.2) | ||||||
| S / SO / SF / SFO / | Single frame or | 60 mm | N°2 drawing | (13) | ∅ 80 mm | 0 ~ 13 % |
| maximum |
number of 4
openings not
exceeding size 6
Design of the insulation system:
| N° of insulation | Division | Insulation system |
| system | ||
| (1) | Deck | On side exposed to fire: 2 layers 38 + 38 mm thick of ceramic fibre FireMaster 607 |
| manufactured by Thermal Ceramic (density 96 kg/m3). | ||
| (2) | Deck | On side exposed to fire: 3 layers 25 + 25 + 25 mm thick of ceramic fibre FireMaster 607 |
| manufactured by Thermal Ceramic (density 128 kg/m3) | ||
| (3) | Deck | On side exposed to fire: 2 layers 38 + 50 mm thick of ceramic fibre FireMaster 607 |
| manufactured by Thermal Ceramic (density 96 kg/m3) | ||
| (4) | Deck | On side exposed to fire: 2 layers 50 + 50 mm thick of ceramic fibre FireMaster 607 |
| (5) | Bulkhead | On the stiffened side: 2 layers 50 + 50 mm thick of ceramic fibre FireMaster 607 |
| (6) | Bulkhead | On the stiffened side: 2 layers 50 + 50 mm thick of ceramic fibre FireMaster 607 |
| manufactured by Thermal Ceramic (density 96 kg/m3). 5 additional compressed layers 30 |
- 30 + 30 +30 + 30 mm thick of ceramic fibre FireMaster 607 manufactured by Thermal
Ceramic (density 96 kg/m3) are laid on the 2 layers of FireMaster607
| (7) | Bulkhead | On the stiffened side: 2 layers 50 + 50 mm thick of ceramic fibre FireMaster 607 |
manufactured by Thermal Ceramic (density 96 kg/m3). 4 compressed layers 30 + 30 + 30
+30 mm thick of ceramic fibre FireMaster 607 manufactured by Thermal Ceramic (density
96 kg/m3) are laid on the 2 layers of FireMaster 607 and located around the frame on 100
mm. The transit system is in addition insulated with 1 layer 50 mm thick of ceramic fibre
FireMaster 607 manufactured by Thermal Ceramic (density 96 kg/m3) overlapping the
compressed layer on 100 mm around the frame.
| (8) | Bulkhead | On side exposed to fire: 12 mm thick of coating Chartek 7 manufactured by International |
Paint located on the transit frame and the cables with a length of 250 mm.
| (9) | Bulkhead | On side exposed to fire: 12 mm thick of coating Chartek 7 manufactured by International |
Paint.
| (10) | Deck | On side exposed to fire: 2 layers 38 + 50 mm thick of ceramic fibre FireMaster 607 |
manufactured by Thermal Ceramic (density 96 kg/m3). 4 additional layers 50 + 50 + 50 +
50 mm thick are laid on the bottom of the 2 layers of insulation under the transit system and
150 mm around.
| (11) | Deck | On side exposed to fire: 2 layers 50 + 50 mm thick of mineral wool Rockwool Firebatt |
| 110 manufactured by ROCKWOOL (density 120 kg/m3) and 1 layer 25 mm thick of | ||
| ceramic fibre FireMaster 607 manufactured by Thermal Ceramic (density 128 kg/m3) | ||
| (12) | Bulkhead | On side exposed to fire: 1 layer 100 mm thick of mineral wool Rockwool Firebatt 110 |
| manufactured by ROCKWOOL (density 100 kg/m3) and 1 layer 25 mm thick of ceramic | ||
| (13) | Bulkhead | On side exposed to fire: 3 layers 25+25+25 mm thick of ceramic fibre FireMaster 607 |
Roxtec R-series frames
Composed of steel sleeves with R type frames (standard, Ex or EMC, PE, ES, BG, BGB) made of steel and rubber, in sizes 70 –
200 and filled with Roxtec halogen free RM modules made of rubber (standard, Ex or EMC, PE, ES, BG, BGB), welded or
bolted to steel divisions.
Classification: H60/H120 (deck and bulkhead)
| insulation | the | cable diameter | (cable area | |||
| arrangement | insulation | relative to | ||||
| system (see | packing | |||||
| table below) | space area) | |||||
| R | 70 ~ 200 | Steel sleeve: | N°1 S1554319 | (14) | ∅ 63 mm | 10 ~ 28 % |
| 55 mm | (see §4.2) | |||||
| Frame: 71 ~ 75 |
mm
| R | 70 ~ 200 | Steel sleeve: | N°2 S1554319 | (14) | ∅ 63 mm | 10 ~ 28 % |
| 55 mm |
Frame: 71 ~ 75
mm
| system | ||
| (14) | Bulkhead / | On side exposed to fire: 3 layers 25+25+25 mm thick of ceramic fibre FireMaster 607 |
| Deck | manufactured by Thermal Ceramic (density 128 kg/m3) |
Roxtec RS-series seals
Composed of steel sleeves with RS- type frames (Ex and EMC versions included) made of steel and rubber, in sizes 23 - 150,
welded or bolted to steel decks or bulkheads.
| RS | 23 ~ 125 | Steel sleeve: | N°1 S1554320 | (14) or (15) | ∅ 96 mm | |
| 35-65 mm | (bulkhead) | |||||
| Frame: | (see §4.2) | |||||
| 39-79 mm | ||||||
| RS | 150 | Steel sleeve: | N°2 S1554320 | (15) | ∅ 96 mm | Not applicable |
| 35-65 mm | (bulkhead) | (1 cable max. | ||||
| Frame: | (see §4.2) | in each rubber | ||||
| 39-79 mm | frame) | |||||
| RS | 23 ~ 125 | Steel sleeve: | N°3 S1554320 | (14) | ∅ 78 mm | |
| 35-65 mm | (deck) | |||||
| Frame: |
39-79 mm
| system | ||
| (14) | Bulkhead / | On side exposed to fire: 3 layers 25 + 25 + 25 mm thick of ceramic fibre FireMaster 607 |
| Deck | manufactured by Thermal Ceramic (density 128 kg/m3) | |
| (15) | Bulkhead | On side exposed to fire: 2 layers 50 + 50 mm thick of ceramic fibre FireMaster 607 |
| blankets (96 kg/m3) |
2. DOCUMENTS AND DRAWINGS :
As per the Manufacturer’s drawings:
2.1 – Design of the transit systems:
S1004649 Rev.E dated 28/09/2010: S2-S4-S6-S8 Ex Frame - Single Frame
S1005518 Rev.B dated 07/05/2019: S Frame - Single Frame
S1005519 Re.E dated 07/05/2019: S Frame - Combination Frame
S1513135 Rev.A dated 03/06/2016: R Frames- R70 Ex and Standard
S1513136 Rev.A dated 03/06/2016: R Frames - R200 Ex and Standard
S1005507 Rev.D dated 29/04/2016: RS Seals - RS 25-31
S1005510 Rev.E dated 29/04/2016: RS Seals - RS 100-150
S1023958 Rev.A dated 27/05/2011: RS 23 – Assembly
S1007491 Rev.B dated 27/06/2010: RS 25 Ex Assembly
S1007536 Rev.B dated 27/06/2010: RS 150 Ex Assembly
S1000392 Rev.B dated 18/02/1999: SR Frame (S) - Single frame
S1000391 Rev.D dated 07/05/2019: SR Frame (S) - Combination frame
S1000686 Rev. C dated 18/02/1999: SO Frame - Single frame
S1002302 Rev. A dated 06/06/2001: SO Frame + Single frame
S1005261 Rev.E dated 10/09/2003: SFO Frame - SFO Single Spot Welded
S1005675 Rev.D dated 18/10/2019: SFO Frame - SFO Comb. Spot Welded
S1007987 Rev.B dated 13/05/2005: SFO Frame / bolted assembly
S1008448 Rev.B dated 05/10/2005: SO Frame - Combination frame
S1010396 Rev.A dated 03/01/2007: SR Frame (T) - Single Frame
S1010399 Rev.A dated 07/05/2019: SR Frame (T) - Combination Frame
S1026459 Rev.F dated 09/03/2021: gasket – SFOH combination frame
S1032396 Rev.A dated 11/04/2013: SFHM Gasket 50x3 – Single Frame 60
S1032393 Rev.A dated 11/04/2013: SFHM Gasket 50x3 + Combination Frame
S1035764 Rev.B dated 03/10/2014: SRBTB/S Frame + Combination Frame (part of test report 6P02536)
S1006967 Rev.L dated 14/06/2018: SLR and SLRS Sleeve
2.2 – Installation / insulation arrangement:
S1554279 Rev.B dated 17/12/2021: S-Series Frames W Cables - H-60 Steel Deck/Bulkhead
S1554304 Rev.C dated 03/01/2022: S-Series W Cables Incl. MC/SWA Cables - H-60 Steel Bulkhead
S1554309 Rev.B dated 17/12/2021: S-Series Frames Cables - H-120 Steel Deck/Bulkhead
S1554312 Rev.B dated 17/12/2021: S-Series Frames W Cables Incl. MC/SWA Cables - H60-H120 Steel Deck
S1554321 Rev.B dated 17/12/2021: S-Series Frames W Cables - H0 Steel Deck
S1554319 Rev.B dated 03/01/2022: R-Frames W Cables - H60- 120 Steel Deck/Bulkhead,
S1554320 Rev.B dated 10/01/2022: RS Seals W Cables - H60-H120 Steel Deck/Bulkhead,
2.3 –Technical statement n°PHD10048A dated 12/01/2022, from DBI, Denmark.
3. TEST REPORTS :
3.1 – Test report N° 250000.20/90.313 dated 09/11/1990, as per IMO Resolution A.517(13), from SINTEF, Norway.
3.2 – Test reports as per IMO FTP Code Annex 1 Part 3 [test standard: IMO Resolution A.754(18)]:
- N° 846007.06 dated 19/09/1997, from SINTEF, Norway.
- N° PG11087 dated 12/02/2003, from DBI, Denmark.
- N° PG11088 dated 18/02/2003, from DBI, Denmark.
- N° PG11199 dated 04/07/2003, from DBI, Denmark.
- N° P400834 dated 31/03/2004, from SP, Sweden.
- N° P703775 dated 07/12/2007, from SP, Sweden.
- N° PX07235 dated 15/12/2010, from SP, Sweden.
3.3 – Test reports as per IMO 2010 FTP Code Annex 1 Part 3, from SP, Sweden:
−N° 3P04210 dated 24/09/2013
−N° 4P02192 dated 30/06/2014
−N° 6P02536 dated 12/07/2016
4. APPLICATION / LIMITATION :
4.1 – Approved for use as cable transits in H-0, H-30, H-60 and H-120 class steel divisions, with limitations contained in §1.
4.2 – Restricted application: the use of bulkhead transit systems is restricted to application where on board fire hazard has
been identified as being from the bulkhead insulation side.
4.3 – Approval of deck cable transit fitted on the unexposed side is limited to this orientation.
4.4 – The arrangement of the cable transit (with fire insulation, if any) is subject to approval in each case.
4.5 – Insulated transit systems have been tested with fire insulating materials FireMaster 607 (96 kg/m3, from Thermal Ceramic)
and Rockwool Firebatt 110 (density 120 kg/m3, from Rockwool). Alternative insulation material is suject to case-by-case
approval providing that it has been approved as giving at least an equivalent insulation performance (H-class approved).
5.1 – The ROXTEC cable sealing system with multidiameter technology, S-series, R-series and RS-series are to be
supplied by ROXTEC International AB in compliance with the type described in this certificate.
5.2 – This type of product is within the category HBV of Bureau Veritas Rule Note NR320 and as such does not require a BV
5.3 – ROXTEC International AB has to make the necessary arrangements to have its works recognised by Bureau Veritas in
5.4 - For information, ROXTEC International AB has declared to Bureau Veritas the following production site(s):
Rombvägen 2
371 23 KARLSKRONA
6. MARKING OF PRODUCT :
7. OTHERS :
7.1 – It is ROXTEC International AB’s responsibility to inform shipbuilders or their sub-contractors of the proper methods of
7.2 – This Certificate supersedes the Type Approval Certificate N° 15027/D1 BV issued on 04/02/2022 by the Society.
7.3 – Watertightness and Gastightness:
Third Party Inspection reports from DNV, Norway: N° MLM 010235 dated 21/08/2001
N° MLM 010238 dated 30/08/2001
N° MLM 020106 dated 19/12/2001
N° MLM 020133 dated 26/02/2002
N° MLM 020408 dated 03/06/2002
- Tested watertightness (before fire exposure): 6 bar during 60 min.