19-1787572-PDA-DUP-optimized
Model(s): Roxtec R Series Frames in Steel Divisions
Product Design Assessment (PDA) 19-1787572-PDA-DUP 05-JUL-2023 02-JUN-2024
Multi and single pipe penetrations in Class A0, A15, A30 and A60 bulkheads and decks for ship or
offshore applications. Penetrations of watertight and gastight steel bulkheads and decks up to the
specified pressure.
“Roxtec pipe sealing system with multidiameter technology” composed of a steel sleeve welded, bolted
or attached through expansion (SLX sleeve, R X kit) to a steel section. Sleeve is fitted with a Roxtec R
frame (standard, Ex/ATEX or EMC) in sizes 50-200.
The R frame is filled with Roxtec (standard, Ex/ATEX or EMC) halogen free RM modules.
A-0, A-15, A-30 and A-60 Bulkheads and Decks
a) Minimum and maximum pipe outside diameter- 6mm and 54 mm for steel and copper pipes for
bulkheads.
b) Minimum and maximum pipe outside diameter- 6mm and 95 mm for steel pipes for decks.
c) Minimum and maximum frame sizes tested are size 50 and size 200
11/17/2023 4:28:17 AM Copyright 2019 American Bureau of Shipping. All rights reserved. Page 1 of 4
Certificate Number: 19-1787572-PDA-DUP
e) For fire class A-0, A-15 and A-30, sleeves are to be insulated as for class A-60 and in addition the
division is to be insulated at least 200 mm around the penetration, except for sizes that are approved
with out insulation.
f) Unit Certification is not required for this product. If the manufacturer or purchaser request an ABS
g) The scope of Type Approval is to comply with MSC.1/Circ.1221 dated 11 December 2006
b) Insulation material is to be A-60 approved type and properly installed in accordance with ABS
approved drawings to the satisfaction of the Surveyors.
c) Watertight bulkheads or decks are to be tested as per ABS Marine Vessels Rules 3-7-1/Table 1.
penetration system has to comply with the requirements give in SOLAS Ch. 11-1 Reg. 13.2.3 (2014
Consolidated Edition), as amended.
e) This approval of penetrations passing through watertight bulkhead is not to be construed as a
substitute for flag Administration’s approval for the purpose of SOLAS (2014 Consolidated Edition), as
amended.
f) The Manufacturer has provided a declaration about the control of, or the lack of Asbestos in this
Test Reports
DBI Fire Test Reports PGA 11302 A Dated 16 January 2019, PGA 11301 A Dated 22 November 2018,
PGA10800A Dated 26 May 2016, PGA10799A Dated 24 May 2016, PGA10724A Dated 05 February
2016, PGA10723A dated 04 February 2016, PGA 10025 Dated 22 December 2011
SP Fire Test Report Numbers 8P04040 Dated 13 August 2018, 8P04039 dated 06 August 2018,
6P10022 Dated 07 March 2017, 6P07563 Dated 20 December 2016, 6P02249 17 August 2016,
4P08662 Dated 08 June 2015, P603000 Dated 23 January 2007, P602999 Dated 23 January 2007
DNV Pressure Test Report Numbers MLM 010247 Dated 28 Sept. 2001, MLM 030473-1 Dated 27
January 2003
Drawings:
Drawing No. S1534086 Revision: B- A-60 Deck with Steel Pipes
Drawing No. S1534092 Revision: B - A-60 Bulkhead with Steel Pipes
Drawing No. S1534107 Revision: B- A-0 Deck with Steel Pipes
Drawing No. S1534145 ,Revision: B- A-0 Bulkhead with Steel Pipes
Drawing No. S1534131,Revision: B- A-60 Deck/ Bulkhead with Copper Pipes
Drawing No. S1534132 Revision: A- A-0 Deck/ Bulkhead with Copper Pipes
11/17/2023 4:28:17 AM Copyright 2019 American Bureau of Shipping. All rights reserved. Page 2 of 4
Drawing No. S1534109,Revision: B- A-60 Deck/ Bulkhead with Steel Pipes, ( Expansion Type Sleeve)
Drawing No. S1534111 Revision: A- A-0 Deck/ Bulkhead with Steel Pipes, (Expansion Type Sleeve)
This Product Design Assessment (PDA) Certificate remains valid until 02/Jun/2024 or until the Rules
2019 ABS Marine Vessels Rules 1-1-4/7.7, 1-1-A3, 1-1-A4, 4-6-2/9.7
2019 ABS Mobile Offshore Units Rules 1-1-4/9.7, 1-1-A2, 1-1-A3, 4-2-1/11.15
Regulation II-2/ 9.3.1 of SOLAS (2014 Consolidated Edition)
A8706-1 RDIMS#1961446 dated 15 November 2006
Print Date and Time: 17-Nov-2023 4:28
11/17/2023 4:28:17 AM Copyright 2019 American Bureau of Shipping. All rights reserved. Page 3 of 4
11/17/2023 4:28:17 AM Copyright 2019 American Bureau of Shipping. All rights reserved. Page 4 of 4
