20-LD1956535-PDA-optimized
Address: ROMBVAGEN 2 SE 371 65 Sweden
Model(s): Roxtec RS Seals in Aluminium Divisions
Product Design Assessment (PDA) 20-LD1956535-PDA 12-MAR-2020 11-MAR-2025
Manufacturing Assessment (MA) 18-GB3595269 07-DEC-2018 08-JAN-2024
3
Single cable penetrations in Class A0, A15, A30 and A60 bulkheads and decks for Marine and Offshore
Application. Penetrations of watertight and gastight aluminium bulkheads and decks up to the specified
pressure.
“Roxtec cable sealing system with multidiameter technology” composed of aluminium sleeves (welded or
bolted, including SLA sleeve) or sleeves of SLX-RS type with RS- type (EMC versions included) halogen
free rubber sealings in size 23-125, mounted in aluminium decks or bulkheads.
Watertight Test Pressure with SLA Sleeve- 4 bar
Gastight Test Pressure with SLA Sleeve- 1.5 bar
a) Maximum cable diameter: 86 mm (without SLA Sleeve)
b) Maximum cable diameter: 10 mm for bulkheads and 50 mm for decks with SLA Sleeve.
c Minimum and Maximum frame sizes tested are 23 & 125 for RS and 25 & 100 for RS with SLA Sleeve.
03/18/2020 8:32:41 AM Copyright 2019 American Bureau of Shipping. All rights reserved. Page 1 of 4
Certificate Number: 20-LD1956535-PDA
e) Tested with Marine Power/ Instrumentation/Control Cables.
f) Insulation material is to be A-60 approved type and installed in accordance with the manufacturer’s
ABS approved installation drawings S1552203 Revision: A ( With out SLA Sleeve) and S1552210,
Revision: A ( with SLA Sleeve) to the satisfaction of the Surveyor.
g) For fire class A-0, A-15 and A-30, sleeves are to be insulated as for class A-60 and in addition the
division is to be insulated at least 200 mm around the penetration.
h) Unit Certification is not required for this product. If the manufacturer or purchaser’s request an ABS
b) Watertight or fire rated bulkheads or decks for cable penetrations are to be examined and tested as
per ABS Marine Vessels Rules 3-7-1/Table 1 and 4-8-4/29.15.
be construed as a substitute for flag Administration’s approval for the purpose of SOLAS (Consolidated
Edition 2014).
Test Reports
CTO Fire Test Report Number RS-17/B-555/E, Pipe penetrations and Cable transits and in class A-60
Aluminium Bulkhead, Dated 15-01-2018
CTO Fire Test Report Number RS-17/B-210/E, Pipe penetrations and Cable transits and in class A-60
Aluminium Deck, Dated 02-06-2017
CTO Fire Test Report Number RS-19/B-020/E, Pipe penetrations and Cable transits and in class A-60
Aluminium Bulkhead ( SLA Sleeve) , Dated 27-05-2019
CTO Fire Test Report Number RS-19/B-224/E, Pipe penetrations and Cable transits and in class A-60
Aluminium Deck ( SLA Sleeve) , Dated 01-08-2019
DBI Fire Test Report Number PGA11371A, Cable transits and pipe penetration in class A-60 Aluminium
deck ( SLA Sleeve) , Dated 20-02-2019
DNV Third Party Inspection Report number MLM010235 dated 21 Aug 2001
DNV Third Party Inspection Report number. N141EX8Z rev2, Dated 10-08-2017
Drawings
Drawing No. S1552203, Certificate drawing, Revision: A,
03/18/2020 8:32:41 AM Copyright 2019 American Bureau of Shipping. All rights reserved. Page 2 of 4
Drawing No. S1552210, Certificate drawing, Revision: A
This Product Design Assessment (PDA) Certificate remains valid until 11/Mar/2025 or until the Rules
2020 ABS Marine Vessels Rules 1-1-4/7.7, 1-1-A3, 1-1-A4, 4-8-4/21.13, 4-8-4/29.15
2020 Rules for Building and Classing Facilities on Offshore Installations 1-1-4/9.7, 1-1-A2, 1-1-A3,
3-8/9.13, 4- 8/9.13
2020 Mobile Offshore Units Rules 1-1-4/9.7, 1-1-A2, 1-1-A3, 4-3-3/5.13
SOLAS Ch. II-2, Reg. 9.3.1 (2014 Consolidated Edition)
IMO FTP Code 2010 (2012 Edition), Annex 1 Part 3
This PDA conforms to Transport of Canada requirements.as per Transport Canada Policy Letter
A8706-1 RDIMS#1961446
Print Date and Time: 18-Mar-2020 8:32
03/18/2020 8:32:41 AM Copyright 2019 American Bureau of Shipping. All rights reserved. Page 3 of 4
03/18/2020 8:32:41 AM Copyright 2019 American Bureau of Shipping. All rights reserved. Page 4 of 4