Product: Fire Stop System
Model(s): Roxtec RS Seals, for Jet fire steel divisions (Bulkhead/Deck)
| Product Design Assessment (PDA) | 21-2132106-PDA-DUP | 05-JUL-2023 | 11-AUG-2026 |
| Manufacturing Assessment (MA) | 23-6047656 | 28-SEP-2023 | 27-SEP-2028 |
Structural steel jet fire protection system: pipe penetration sealing system in Jet fire resisting bulkhead
and deck divisions for offshore applications only.
“Roxtec pipe sealing system with multidiameter technology” composed of steel sleeves (welded or
bolted) with RS- type (EMC versions included) halogen free rubber sealings. Frame size 23-400 for steel
pipe services, and filled with Roxtec halogen free insert modules, mounted in steel bulkheads and decks.
Jet Fire rating J30: RS-, Roxtec modules installed back to back; between the ends the space between
the pipe and the flange filled with 100mm ceramic fibre;
Pipes - Maximum pipe outside diameter up to 323 mm.
Watertight test pressure 6 bar g. (except bolted versions test pressure at 5 bar g.);
Gastight test pressures 4 bar g. (except bolted versions test pressure at 2.5 bar g.).
1) Not for use in tank boundaries.
Applications in each case to be approved by ABS at the design stage.
Unit Certification is not required for this product. If the manufacturer or purchaser’s request an ABS
| 11/17/2023 4:28:00 AM | Copyright 2019 American Bureau of Shipping. All rights reserved. | Page 1 of 3 |
| Certificate Number: 21-2132106-PDA-DUP |
- All seal types should be installed in accordance with manufacturer’s ABS approved installation
drawing number S1023312 rev A.
- Insulation material is to be H class approved type and properly installed to the satisfaction of the
Surveyors.
- Although the jet fire resistance test has been designed to reproduce conditions similar to those found
in large-scale jet fires resulting from realistic releases of hydrocarbons, it cannot guarantee a specific
degree of protection from the myriad of possible jet fires. The Jet Fire Resistance Test, or indeed
large-scale demonstrations, cannot therefore be used to confer a universal fire resistance rating for a
specified time in the way that a standard furnace test confers a hydrocarbon rating. Hence this test does
not give a rating analogous to the “H” rating derived from the hydrocarbon fire resistance test as detailed
in ISO 834. This test is not intended to replace the hydrocarbon fire resistance test but is seen as a
complementary test.
- Although the method specified for jet-fire resistance test has been designed to simulate some of the
conditions which occur in an actual jet fire, it cannot reproduce them all exactly. The results of this test
do not guarantee safety but may be used as elements of a fire risk assessment for structures or plant.
This should also take into account all the other factors which are pertinent to an assessment of the fire
hazard for a particular end use.
- The Manufacturer has provided a declaration about the control of, or the lack of Asbestos in this
Sintef test report no. NBL F10106 dated 13 October 2010.
SINTEF/SP assessment report no. F15 20119-1 dated 29 January 2015.
3) Drawing number S1023312 rev A.
- Drawing No. Roxtec letter 2021-05-20. Declaration of Conformity.
This Product Design Assessment (PDA) Certificate remains valid until 11/Aug/2026 or until the Rules
2021 Rules for Offshore Units and Structures: 1-1-4/9.7, 1-1-A2, 1-1-A3, which covers the following:
2021 Rules for Building and Classing Mobile Offshore Drilling Units: 4-2-1/11.15, 5-1-1/3.5, 5-1-1/ 5.17 &
5-1-1/5.21
2021 Rules for Building and Classing Facilities on Offshore Installations: 3-8/9.13, 4-8/9.13
ISO 22899-1: 2021 “Determination of the resistance to jet fires of passive fire protection materials”
| 11/17/2023 4:28:00 AM | Copyright 2019 American Bureau of Shipping. All rights reserved. | Page 2 of 3 |
Print Date and Time: 17-Nov-2023 4:28
| 11/17/2023 4:28:00 AM | Copyright 2019 American Bureau of Shipping. All rights reserved. | Page 3 of 3 |
