Certificate number: 40893/B1 BV
File number: ACI4000/032/009
Product code: 5300H
This certificate is not valid when presented without the full attached schedule
composed of 7 sections
TYPE APPROVAL CERTIFICATE
This certificate is issued to
ROXTEC International AB
KARLSKRONA - SWEDEN
for the type of product
PIPE, CABLE, DUCT PENETRATIONS IN FIRE DIVISIONS
ROXTEC cable sealing system with multidiameter technology
Jet Fire Application for S-Series Frames and RS-Series Seals
(certified products, frame position and achieved performances - see §1)
Requirements:
Bureau Veritas Rules for the Classification of Offshore units Part C Chapter 4
ISO 22899-1
This certificate is issued to attest that Bureau Veritas Marine & Offshore did undertake the relevant approval procedures for the product identified
above which was found to comply with the relevant requirements mentioned above.
This certificate will expire on: 12 Apr 2026
For Bureau Veritas Marine & Offshore,
At BV GOTHENBURG, on 24 Nov 2023,
Hans-erik ERICSSON
This certificate was created electronically and is valid without
signature
This certificate remains valid until the date stated above, unless cancelled or revoked, provided the conditions indicated in the subsequent page(s) are complied
with and the product remains satisfactory in service. This certificate will not be valid if the applicant makes any changes or modifications to the approved product,
which have not been notified to, and agreed in writing with Bureau Veritas Marine & Offshore. Should the specified regulations or standards be amended during
the validity of this certificate, the product(s) is/are to be re-approved prior to it/they being placed on board vessels to which the amended regulations or standards
apply. This certificate is issued within the scope of the General Conditions of Bureau Veritas Marine & Offshore available on the internet site www.veristar.com.
Any Person not a party to the contract pursuant to which this document is delivered may not assert a claim against Bureau Veritas Marine & Offshore for any
liability arising out of errors or omissions which may be contained in said document, or for errors of judgement, fault or negligence committed by personnel of the
Society or of its Agents in establishment or issuance of this document, and in connection with any activities for which it may provide.
The electronic version is available at: VeriSTAR Project Management - Bureau Veritas Marine & Offshore
| BV Mod. Ad.E 530 June 2017 | This certificate consists of 4 page(s) |
|---|
Certificate number: 40893/B1 BV
THE SCHEDULE OF APPROVAL
1. PRODUCT DESCRIPTION:
ROXTEC cable sealing system with multidiameter technology
1.1 - Roxtec S series frames
Consisting of Roxtec S series frame (S, SO, SF, SFO, SR, SK, SRC r20&r40 and SBTB), welded or bolted on to the Jet Fire
steel division, and filled with Roxtec (standard, Ex or EMC, PE, ES, BG, BGB) halogen free insert modules. Assembled with
Roxtec Wedge kit or Roxtec EMC, EX Wedge kit.
Additional insulation on penetrations and/or cables:
- should be approved as having the same level of performance as the penetrated division and expected classification of
penetration,
- is to be fitted as shown in the referred Manufacturer’s drawings (see §2.1) and also according to Manufacturer’s insulation
guidelines.
| Penetration | Max. | Min. frame | Classification | Frame position Max. cable diameter / | Max. |
|---|---|---|---|---|---|
| designation | external | depth | Pipe outer diameter | filling | |
| dimensions | (mm) | range | ratio | ||
| (mm) | |||||
| S-series SK 596x271 | 200 | When installed/insulated according drawing N° S1501671 rev. B dated | Unexposed | Cables, incl. Metal | 39.3% |
| — | — | — | — | — | — |
| 1x1 up to | 24/08/2015 (detail J-30), the penetration can withstand the jet fire | Clad (MC) and Steel | |||
| 8+8x2 | (250 kW/m²) for 30 min. | Wire Armored (SWA) | |||
| cables | |||||
| When installed/insulated according drawing N° S1501671 rev. B dated | Unexposed | ≤ 103 mm | |||
| — | — | — | |||
| 24/08/2015 (detail J-60), the penetration can withstand the jet fire |
(250 kW/m²) for 60 min.
| S-series | 298x141 | 300 | When installed/insulated according drawing N° S1577491 rev. A dated | Any | Cables ∅ ≤ 90 mm | 20.6% |
|---|---|---|---|---|---|---|
| SBTB 1x1 | 14/03/2022 (N°1), the penetration can withstand with regards to integrity | Steel pipes ∅ 6-30 mm | ||||
| up to 8x1 | only the jet fire (250 kW/m²) for 180 min. | |||||
| Restricted application: exposed side of frame and division is the side | ||||||
| coated with passive fire protection. | ||||||
| S-series | 298x141 | 300 | When installed/insulated according drawing N° S1577491 rev. A dated | Any | Cables ∅ ≤ 77 mm | 16.2% |
| — | — | — | — | — | — | — |
| SBTB 1x1 | 14/03/2022 (N°2), the penetration can withstand with regards to integrity | Steel pipes ∅ 6-30 mm | ||||
| up to 8x1 | only the jet fire (250 kW/m²) for 180 min. | |||||
| S-series | 596x141 | 300 | When installed/insulated according drawing N° S1501671 rev. B dated | Unexposed | Cables ∅ ≤ 43 mm | 7.5% |
| SBTB 1x1 | 24/08/2015 (detail J-60 SBTB), the penetration can withstand the jet fire | Steel pipes ∅ 20 mm | ||||
| up to 8+8x1 | (250 kW/m²) for 60 min. | |||||
| S-series | 296x532 | 400 | When installed/insulated according drawing N° S1501671 rev. B dated | Unexposed | Cables ∅ ≤ 79 mm | 13.2% |
| SBTB 1x1 | 24/08/2015 (detail J-120 SBTB), the penetration can withstand the jet fire | Steel pipes ∅ 10-30 | ||||
| up to 8x4 | (250 kW/m²) for 120 min. | mm | ||||
| S-series | 298x271 | 400 | When installed/insulated according drawing N° S1558321 rev.C dated | Any | Cables ∅ ≤ 83 mm | 12.7% |
| SBTB 1x1 | 15/03/2022 (N°1), the penetration can withstand with regards to integrity | |||||
| up to 8x2 | only: | Steel pipes ∅ 6-30 mm |
- the HHF jet fire (350 kW/m²) for 20 min,
- the extended pool fire (250 kW/m²) for 35 min.
| S-series | 298x271 | 400 | When installed/insulated according drawing N° S1558321 rev.C dated | 300 mm | Cables ∅ ≤ 83 mm | 12.7% |
|—|—|—|—|—|—|—|
| SBTB 1x1 | 15/03/2022 (N°2), the penetration can withstand with regards to integrity exposed side / Steel pipes ∅ 6-30 mm |
| up to 8x2 | only: | 100 mm |
| - the HHF jet fire (350 kW/m²) for 20 min, | unexposed side | - the extended pool fire (250 kW/m²) for 10 min.
| S-series | 238x532 | 300 | When installed/insulated according drawings N° S1558321 rev.C dated | Unexposed | Cables ∅ ≤ 83 mm | 10.0% |
|—|—|—|—|—|—|—|
| SBTB 1x1 | 15/03/2022 (N°3), the penetration can withstand with regards to integrity | Steel pipes ∅ 6-30 mm |
| up to 6x4 | only: | - the HHF jet fire (350 kW/m²) for 15 min,
- the jet fire (250 kW/m²) for 30 min,
- the extended pool fire (150 kW/m²) for 75 min.
| S-series | 238x532 | 300 | When installed/insulated according drawings N° S1558321 rev.C dated | Unexposed | Cables ∅ ≤ 90 mm | 10.7% |
|—|—|—|—|—|—|—|
| SBTB 1x1 | 15/03/2022 (N°4), the penetration can withstand with regards to integrity | Steel pipes ∅ 6-30 mm |
| up to 6x4 | only: | - the HHF jet fire (350 kW/m²) for 15 min,
- the jet fire (250 kW/m²) for 20 min.
Following on next page
The electronic version is available at: VeriSTAR Project Management - Bureau Veritas Marine & Offshore
| BV Mod. Ad.E 530 June 2017 | This certificate consists of 4 page(s) |
|---|
Certificate number: 40893/B1 BV
| Penetration | Max. | Min. frame | Classification | Frame position Max. cable diameter / Max. |
|---|---|---|---|---|
| designation external | depth | Pipe outer diameter filling | ||
| dimensions | (mm) | range | ratio | |
| (mm) | ||||
| S-series | 296x532 | 400 | When installed/insulated according drawing N° S1558323 rev. B dated | Any |
| — | — | — | — | — |
| SBTB 1x1 | 14/03/2022 (N°1), the penetration can withstand: | Steel pipes | ||
| up to 8x4 | - the HHF jet fire (350 kW/m²) for 30 minutes, | ∅ 6-30 mm |
- the extended pool (250 kW/m²) for 30 minutes.
Restricted application: exposed side of frame and division is the side
coated with passive fire protection.
| S-series | 238x532 | 370 | When installed/insulated according drawing N° S1558323 rev. B dated | Any | Cables ∅ ≤ 49 mm | 16.0% |
|—|—|—|—|—|—|—|
| SKFOH 1x1 | 14/03/2022 (N°2), the penetration can withstand HHF jet fire (350 kW/m²) | Steel pipes |
| up to 6x4 | for 60 min. | ∅ 16 mm |
Restricted application: exposed side of frame and division is the side
coated with passive fire protection.
| S-series | 238x532 | 370 | When installed/insulated according drawing N° S1558323 rev. B dated | Any | Cables ∅ ≤ 49 mm | 16.0% |
|—|—|—|—|—|—|—|
| SKFOH 1x1 | 14/03/2022 (N°3), the penetration can withstand: | Steel pipes |
| up to 6x4 | - the HHF jet fire (350 kW/m²) for 20 minutes, | ∅ 16 mm | - the pool fire (200 kW/m²) for 40 minutes.
Restricted application: exposed side of frame and division is the side
coated with passive fire protection.
1.2 - Roxtec RS seals
Composed of steel sleeves (welded or bolted) with RS-type (Ex and EMC versions included) halogen free rubber seals mounted
in steel deck and bulkheads.
Additional insulation on penetrations and/or cables:
- should be approved as having the same level of performance as the penetrated division and expected classification of
penetration,
- is to be fitted as shown in the referred Manufacturer’s drawings (see §2.1) and also according to Manufacturer’s insulation
guidelines.
| Penetration designation | External | Sleeve | Classification | Sleev | Pipe outer |
|---|---|---|---|---|---|
| dimensions | depth | position | diameter | ||
| (mm) | (mm) | range | |||
| RS-series | ∅32 to 414 | 480 | When installed/insulated according drawing N° S1501673 rev. B | Unexposed | Steel pipes |
| 23 up to 400 | dated 24/08/2015, the penetration can withstand the jet fire (250 | ∅ ≤ 324 mm | |||
| (back-to-back installation) | kW/m²) for 60 minutes. |
2. DOCUMENTS AND DRAWINGS:
As per the Manufacturer’s insulation drawings quoted in tables in §1.
3. TEST REPORTS:
3.1 - Test report N° 846031.02 dated 04/11/1997, as per Health and Safety Executiv, Offshore Technology Report - OTI 95 634
“Jet Fire Resistance Test of Passive Fire Protection Materials”, from SINTEF, Norway.
3.2 - Test report N° NBL-107332 dated 03/06/2005, as per Health and Safety Executiv, Offshore Technology Report - OTI 95
634 “Jet Fire Resistance Test of Passive Fire Protection Materials”, from SINTEF, Norway.
3.3 - Test report N° NBL-F10106 dated 13/10/2010, as per ISO 22899-1:2007, from SINTEF, Norway.
3.4 - Test report N° NBL-F10107 dated 15/11/2010, as per ISO 22899-1:2007, from SINTEF, Norway.
3.5 - Study report N° F15 20119-1 Version 1, “Evaluation of jet fire attack direction on response of products”, dated 29/01/2015,
from SP Fire Research AS, Norway (technical justification for worst case scenario being horizontal jet fire test).
3.6 - Test report N° 120000-56 Version 1, “Sequential HHF jet fire test and “extended pool fire” test”, dated 09/12/2019, from
RISE, Norway.
3.7 - Test report N° F17 120000-15:2 Version 1, “Jet fire test based on ISO 22899-1”, dated 06/07/2017, from RISE, Norway.
3.8 - Test report N° F19 120000-48:1 Version 1, “Jet fire test based on ISO 22899-1”, dated 11/04/2019, from RISE, Norway.
3.9 - Test report N° F19 120000-48:2 Version 1, “Jet fire test based on ISO 22899-1”, dated 11/04/2019, from RISE, Norway.
3.10 - Test report N° 120000-59 Version 2, “Sequential HHF jet fire test, “standard” jet fire test and “pool fire” test”, dated
17/08/2020, from RISE, Norway.
3.11 - Statement N° 120000-81 on results in test reports N° F17 120000-15:2 Version 1 and N° F19 120000-48:1 Version 1,
dated 04/03/2022, from RISE, Norway.
The electronic version is available at: VeriSTAR Project Management - Bureau Veritas Marine & Offshore
| BV Mod. Ad.E 530 June 2017 | This certificate consists of 4 page(s) |
|---|
Certificate number: 40893/B1 BV
3.12 - Test report N° 120000-70 Version 1, “Jet fire test based on ISO 22899-1”, dated 18/05/2021, from RISE, Norway.
3.13 - Test report N° 120000-67 Version 1, “Sequential HHF jet fire test and “extended pool fire” test”, dated 05/10/2020, from
RISE, Norway.
4. APPLICATION / LIMITATION:
4.1 - Approved for use as cable transits in jet-fire resistant steel divisions with limitations contained in §1.
4.2 – Restricted application (refer to §1 for concerned cable penetration systems): the use of cable penetration systems in
bulkhead or deck is restricted to application where on board fire hazard has been identified as being from the bulkhead’s or
deck’s insulated side.
4.3 - For S-Series including cables, filling ratio not to exceed the one tested (see § 1).
5. PRODUCTION SURVEY REQUIREMENTS:
5.1 - The ROXTEC cable sealing system with multidiameter technology, S-series and RS-series are to be supplied by
ROXTEC International AB in compliance with the type described in this certificate.
5.2 - This type of product is within the category HBV of Bureau Veritas Rule Note NR320 and as such does not require a BV
product certificate.
5.3 - ROXTEC International AB has to make the necessary arrangements to have its works recognised by Bureau Veritas in
compliance with the requirements of NR320 for HBV products.
5.4 - For information, Roxtec International AB has declared to Bureau Veritas the following production site(s):
ROXTEC International AB
Rombvägen 2
371 23 KARLSKRONA
SWEDEN
6. MARKING OF PRODUCT:
The product or packing is to be marked with Manufacturer name, type, designation and fire-technical rating.
7. OTHERS:
7.1 - It is ROXTEC International AB’s responsibility to inform shipbuilders or their sub-contractors of the proper methods of
fitting, use and general maintenance of the approved equipment and the conditions of this approval.
7.2 - This Certificate supersedes the Type Approval Certificate N° 40893/B0 BV issued on 12/04/2021 by the Society.
7.3 - Testing for water and gas tightness witnessed by third party (DNV):
| Product | Report N° | Date |
|---|---|---|
| SLFO/RI | MLM090673 | 08/10/2009 |
| Bolted sleeve | MLM020401 | 25/03/2002 |
| S-frame | MLM020400 | 25/03/2002 |
| S-frame | SKM-04-4088 | 16/06/2004 |
| RS-seal | MLM090652 | 15/06/2009 |
| Product | Test pressure water tightness | Test pressure gas tightness |
| S Series frame | 6 bar | 3 bar |
| RS Series seal | 6 bar | 3 bar |
| Welded SL, SLF sleeve and frame | 6 bar | 3 bar |
| Bolted SLF sleeve and frame | 5 bar | 2.5 bar |
| SLFO/RI sleeve | 2 bar | 1 bar |
*** END OF CERTIFICATE ***