Certificate number: 41353/B0 BV
File number: ACI4000/032/010
Product code: 5302H
CABLE PENETRATIONS IN FIRE DIVISIONS
A-Class Aluminium Divisions “Cable sealing system with multidiameter technology, Roxtec S-Series”
SOLAS 74, as amended, Regulations II-2/9.3.1
IMO Resolution MSC.307(88) (2010 FTP Code)
IMO Resolution MSC.61(67)-(FTP Code) with IMO Resolution MSC.307(88) (2010 FTP Code) article 8
IMO MSC/Circ.1120
This certificate will expire on: 12 Apr 2026
At BV GOTHENBURG, on 12 Apr 2021,
Torbjorn Ygesjo
| BV Mod. Ad.E 530 June 2017 | This certificate consists of 3 page(s) |
1. PRODUCT DESCRIPTION:
A-Class Aluminium Divisions “Cable sealing system with multidiameter technology, S-series”
Consisting of Roxtec S-series frames (S, SO, SF, SFO, SR, SK, SRC r20&r40 and BTB) in sizes 1-8 and combinations thereof,
welded or bolted on to the steel divisions; filled with Roxtec (Standard, Ex, EMC, PE, ES, BG, BGB) halogen free insert
modules. Assembled with Roxtec Wedge kit (Standard, Ex or EMC). Frames are welded or bolted symmetrically in aluminium
division.
| Penetration designation | S-series frames 1x1 to 8+8x10 |
| Type of division tested | Aluminium Deck and Bulkhead |
| Depth of the penetration (mm) | 60 |
| External dimensions (mm) | 141x121 to 596x402 |
| Classification | A-0 Class to A-60 Class |
| Maximum cable diameter: 88 mm | |
| Tested fill based on transit opening area and the Roxtec Cable Sealing System. Maximum fill of a Roxtec transit is to install | |
| cable in every module installed in transit opening and minimum is to not install cable in any module in transit opening. | |
| The thickness of A-Class aluminium division insulation is to be at least the length of protruding frame. |
2. DOCUMENTS AND DRAWINGS:
As per Manufacturer’s drawing N° S1502938 rev.B dated 13/10/2020.
3. TEST REPORTS:
Test reports as per (1)IMO FTP Code Annex 1 Part 3 [test standard: IMO Resolution A.754(18)] or (2)IMO 2010 FTP Code
Annex 1 Part 3:
| Laboratory | Test report | Date | Cable transits | Division | Fire rating |
| SP, Sweden | N° P603001(1) | 23/07/2007 | S 8+8x3 (combination) | ||
| CTO, Poland | N° RS-18/B-180/E | 25/06/2018 | S 2x1 (single) and S 8x1 (single) | Aluminium bulkhead | A-60 |
| CTO, Poland | N° RS-19/B-020/E | 27/05/2019 | S 8x4 (combination) | ||
| CTO, Poland | N° RS-18/B-179/E | 25/06/2018 | S 2x1 (single) and S 8x1 (single) | Aluminium deck | A-60 |
| CTO, Poland | N° RS-19/B-224/E | 01/08/2019 | S 8+8x3 (combination) |
4. APPLICATION / LIMITATION:
4.1 - Approved for use as cable transits in A-15, A-30, A-60 class steel divisions, with fire insulation as described in §1.
For A-0 class divisions, local insulation arrangement shall be installed (on the penetration itself and 200 mm around).
4.2 - Any other arrangement of cable transit is subject to a case-by-case approval.
4.3 - Filling ratio not to exceed the one tested (see § 1).
4.4 - The fitting aboard to be the same as used for the test.
5.1 - The A-Class Aluminium Divisions “Cable sealing system with multidiameter technology, S-series” are to be supplied
by ROXTEC International AB in compliance with the type described in this certificate.
7. OTHERS:
7.2 - This Certificate supersedes the Type Approval Certificate N° 41353/A0 BV issued on 02/11/2015 by the Society.
7.3 - Testing of the penetrations for gastightness and watertightness as per following inspection reports, witnessed by Third
Party surveyor:
- report N° 020400 dated 25/03/2002, from DNV, Norway.
- report N° SKM-04-4088 dated 16/06/2004 from DNV, Norway.
| Watertightness test | Gastightness test |
| (before fire exposure) | (before fire exposure) |
| 6 bar during 60 min | 4 bar during 30 min |