52326_A0 BV-optimized
Certificate number: 52326/A0 BV
File number: ACI 4000/032/012
Product code: 5302H
This certificate is not valid when presented without the
full attached schedule composed of 7 sections
CABLE PENETRATIONS IN FIRE DIVISIONS
GK MC FC Single- and Multiple Cable Penetration System (steel)
SOLAS 74 Convention, as amended, Regulations II-2/9.3.1
IMO Res MSC.307(88) (2010 FTP Code)
This certificate will expire on: 20 Jul 2023
At BV GOTHENBURG, on 20 Jul 2018,
Magne MOLLER
BV Mod. Ad.E 530 June 2017 This certificate consists of 3 page(s)
1. PRODUCT DESCRIPTION :
GK Multi-Cable Fire Collars (GK MC FC) Single- and Multiple Cable Penetration System (steel)
Consisting of circular or oval sleeve(s) with or without flange, one side circumferentially welded to a steel division. Sizes GK
MC FC ROUND 89 to 244 (circular) and GK MC FC OVAL 200x150 to 550x170 (oval). The GK MC FC cable penetration
system is filled with intumescent material and a glass fiber tissue hose, folded back on each side of the sleeves. The glass fiber
tissue hose and the cable bundle are secured with a plastic covered metal strap on each side. On both sides of the cable transit,
the cable bundle is secured with a cold smoke stop.
GK MC FC ROUND:
The coaming is welded symmetrically of the deck/bulkhead.
Insulation details according drawing Roxtec No. S1529242 rev A
Approved for cable outer diameter up to 41,5 mm
Filling ratios to be up to 77% for Deck and Bulkhead
GK MC FC OVAL:
Insulation details according drawings Roxtec No. S1529241 rev A & S1529242 rev A
Filling ratios to be up to 67% for Bulkhead
Filling ratios to be up to 67% or 68%, depending on the configuration for Deck
2. DOCUMENTS AND DRAWINGS :
As per Manufacturer’s drawings No. S1529241 rev A, dated June 1, 2018 & S1519242 rev A, dated June 1, 2018.
3. TEST REPORTS :
  • Test report N° DMT-DO-53-056, dated 2016-08-01 as per IMO Resolution MSC.307(88), from DMT, Germany.
  • Test report N° DMT-DO-53-060, dated 2016-11-17 as per IMO Resolution MSC.307(88), from DMT, Germany.
  • Test report N° DMT-DO-53-064, dated 2016-11-21 as per IMO Resolution MSC.307(88), from DMT, Germany.
  • Test report N° DMT-DO-53-065, dated 2017-01-19 as per IMO Resolution MSC.307(88), from DMT, Germany.
4. APPLICATION / LIMITATION :
4.1 - The fitting aboard to be the same as used for the test.
4.2 - The cables filling ratios of the penetrations are to be up to the values indicated in insulation drawings in §2.
4.3 - Approved for use as cable transits in A-0, A-15, A-30 and A-60 class steel divisions, with limitations contained in §1.
4.4 - The insulation material shall be type approved. The fire tests were conducted with various types of insulation materials;
alternative ones (duly type approved) may be used provided their insulation performance are equivalent/appropriate.
5.1. - The GK Multi-Cable Fire Collars (GK MC FC) are to be supplied by ROXTEC International AB in compliance with the
type described in this certificate.
For information concerning the production phase modules, ROXTEC International AB has declared the following
manufacturing site(s):
BOX 540
371 23 KARLSKRONA
6. MARKING OF PRODUCT :
7. OTHERS :
It is ROXTEC International AB’s responsibility to inform shipbuilders or their sub-contractors of the proper methods of