61826_A0 BV-optimized
Certificate number: 61826/A0 BV
File number: ACI4000/032/013
Product code: 5302H
CABLE PENETRATIONS IN FIRE DIVISIONS
Roxtec GK Firestop Sealing Kit (GK FS SK) in steel divisions
SOLAS 74, as amended, SOLAS 2000 Regulations II-2/9.3.1
IMO Resolution MSC.307(88) -(FTP Code 2010)-
This certificate will expire on: 12 Apr 2026
At BV GOTHENBURG, on 12 Apr 2021,
Torbjorn Ygesjo
BV Mod. Ad.E 530 June 2017 This certificate consists of 4 page(s)
1. PRODUCT DESCRIPTION:
Roxtec “GK Firestop Sealing kit” consists of a fibreglass cloth with built-in heat activated intumescent material to be wrapped
around cable bundles and fitted into circular or oblong (noted “oval”) steel sleeves. Folded back on each side with ends sealed
off to create a cold smoketight seal and secured by metal cable ties. It is also intended to be used for bundled cables or as a blank
fire stop solution. The installation shall be made in symmetrically welded or bolted sleeves (coaming). Sleeves are 105-205 mm
long (52.5-102.5 mm from each side of steel division).
1-1 - A-60 Class in steel bulkhead:
Type Size (mm) Insulation on unexposed side Filling ratio
89 2 layers of 45 mm thick mineral wool*, 150 mm around the sleeve 0%
GK MC FC 273 0%
ROUND KIT 89 2 layers of 45 mm thick mineral wool* 150 mm around the sleeve 70%
273 and min. wrap 300 mm covering totally the GK MC FC cloth 69%
2x168 2 layers of 45 mm thick mineral wool* 150 mm around the sleeve 0%
GK MC FC 2x(250x170) 0%
OVAL KIT 2x(250x170) 2 layers of 45 mm thick mineral wool* 150 mm around the sleeve 67%
200x150 and min. wrap 300 mm covering totally the GK MC FC cloth 67%
(*) see §4.3
1-2 - A-60 Class in steel deck:
Type Size (mm) Insulation on exposed side Filling ratio
89 one layer of 45 mm thick mineral wool* 100 mm around the sleeve 0%
GK MC FC 273 0%
ROUND KIT 89 one layer of 45 mm thick mineral wool* 100 mm around the sleeve 69%
2x168 0%
2x(250x170) one layer of 45 mm thick mineral wool* 100 mm around the sleeve 0%
GK MC FC 200x150 0%
OVAL KIT 2x168 one layer of 45 mm thick mineral wool* 100 mm around the sleeve 68%
2x(250x170) and one layer covering totally the GK MC FC cloth 68%
200x150 70%
(*) see §4.3
1.3 - A-0 Class in steel bulkhead:
Type Size (mm) Filling ratio
89 0%
GK MC FC 273 0%
ROUND KIT 89 67%
273 68%
200x150 0%
OVAL KIT 200x150 70%
2x(250x170) 67%
1.4 - A-0 Class in steel deck:
89 0%
GK MC FC 273 0%
ROUND KIT 89 70%
273 68%
2x168 0%
GK MC FC 200x150 0%
OVAL KIT 2x(250x170) 0%
200x150 67%
2. DOCUMENTS AND DRAWINGS:
As per the Manufacturer’s drawings:
  • N° S1554857 rev.A dated 27/04/2020: “GK FS SK WITH CABLES - A-60 CLASS STEEL BULKHEAD”
  • N° S1554858 rev.A dated 27/04/2020: “GK FS SK WITH CABLES - A-0 CLASS STEEL BULKHEAD”
  • N° S1554853 rev.A dated 27/04/2020: “GK FS SK WITH CABLES - A-60 CLASS STEEL DECK”
  • N° S1554856 rev.A dated 27/04/2020"GK FS SK WITH CABLES - A-0 CLASS STEEL DECK"
3. TEST REPORTS:
Test reports, as per IMO 2010 FTP Code Annex 1 Part 3, from (a)CTO Poland, (b)DBI Denmark, (c)RISE Sweden or (d)DMT
Germany:
Fire Filling A-Class steel bulkhead A-Class Steel deck
Type Size (mm)
rating ratio Test report N° Test report N°
0%
89 A-60 RS-19/B-255/E dated 20/08/2019(a) RS-19/B-225/E dated 20/08/2019(a)
Max
0% RS-19/B-423/E dated 19/11/2019(a)
A-0 8P07092 dated 27/09/2019(c)
GK MC FC Max PGA11387 A dated 05/07/2019(b)
ROUND KIT 0% RS-19/B-256/E dated 20/08/2019(a)
273 A-60 RS-19/B-255/E dated 20/08/2019(a)
Max RS-19/B-225/E dated 20/08/2019(a)
0% RS-20/B-081/E dated 31/03/2020(a)
A-0 PGA11610A dated 10/01/2020(b)
0% RS-19/B-255/E dated 20/08/2019(a) RS-19/B-225/E dated 20/08/2019(a)
2x168 A-60
Max / /
0% / 8P07092 dated 27/09/2019(c)
A-0
Max / /
2x(250x170) A-60
GK MC FC Max RS-19/B-355/E dated 16/10/2019(a) /
OVAL KIT 0% RS-19/B-423/E dated 19/11/2019(a) 8P07092 dated 27/09/2019(c)
A-0
Max PGA11387 A dated 05/07/2019(b) /
0% / /
200x150 A-60
Max DMT-DO-53112 dated 22/05/2019(d) RS-19/B-225/E dated 20/08/2019(a)
0%
A-0 8P07094 dated 23/09/2019(c) 8P07092 dated 27/09/2019(c)
Max
4. APPLICATION / LIMITATION:
4.1 - Approved for use:
  • in A-15, A-30, A-60 class steel divisions with fire insulation as described in §1.
  • in A-0 class steel divisions without fire insulation.
    4.2 - Any other arrangement of cable transit is subject to a case-by-case approval.
    4.3 - The tests have been carried out with fire insulating material “SeaRox WM 620” (nominal density 90 kg/m³; manufactured
    by Rockwool International A/S); any alternative A-class insulation material, previously proven and approved, giving at least an
equivalent insulation performance, can be used.
4.4 - Filling ratio not to exceed the one tested (see § 1).
5.1 - Roxtec GK Firestop Sealing Kit (GK FS SK) in steel divisions is to be supplied by ROXTEC International AB in
compliance with the type described in this certificate.
The product or packing is to be marked with Manufacturer name, type, designation and fire-technical rating.
7. OTHERS:
7.2 - In-house type testing for cold smoke tightness as per test reports N° 22032017-01 dated 22/03/2017 (one cable bundle,
filling ratio 21%; test pressure 0.3 mbar during 15 minutes) and 14122016-01 dated 14/12/2016 (three cable bundles; test
pressure 0.3 mbar during 20 minutes).