Certificate of Compliance
| Certificate: | 70100154 | Master Contract: 215242 |
| Project: | 80030567 | Date Issued: | June 15, 2020 |
| Issued to: | Roxtec International AB |
Rombvägen 2
Karlskrona, 371 23
Attention: Jorgen Akesson
The products listed below are eligible to bear the CSA Mark shown
with adjacent indicators ‘C’ and ‘US’ for Canada and US or with adjacent
indicator ‘US’ for US only or without either indicator for Canada only
Issued by:
Matthew Brooks
PRODUCTS
CLASS 4418-05 - CABLE-Hardware - For Hazardous Locations
CLASS 4418-85 - CABLE-Hardware - For Hazardous Locations – Certified to U.S. Standards
Canada: Ex eb IIC Gb; Ex tb IIIC Db;
USA: Class I, Zone 1, AEx eb IIC Gb; Class II, Zone 21, AEx tb IIIC Db:
CABLE TRANSIT DEVICE, FRAME
Models HD 24 Ex, HD 32 Ex and HD 16 Ex, for use with CX or CX BG Modules.
Ambient Rating: -60°C to +80°C; Environmental Ratings: Types 1, 2, 3, 3R, 3S, 4, 4X, 5, 12, 13, IP66.
Model HDLC Ex for use with RMX- or RX BG B modules.
FRAME MODULES
Adaptable Multi-diameter CX Modules, 40 mm length:
CX 15w40, CX 20, CX 30w40, CX 40, CX 40 10-31.
FF0 002
| DQD 507 Rev. 2019-04-30 | © 2018 CSA Group. All rights reserved. | Page 1 |
| Project: | 80030567 | Date Issued: June 15, 2020 |
Solid Compensation CX Modules, 40 mm length:
CX 5w40/0, CX 10w40/0, CX 40/0.
Single Diameter CX Modules, 40 mm length:
CX 20/14, CX 20/15, CX20/16.
Adaptable Multi-diameter Bonding and Grounding CX BG Modules, 40 mm length:
CX 20w40 BG, CX 30w40 BG, CX 40 10-31 BG, CX 40 BG.
Solid Compensation CX BG Modules, 40 mm length:
CX 10w40/0 BG, CX 20/0 BG, CX 40/0 BG.
Adaptable Multi-diameter RMX Modules, 60 mm length:
RMX 15w40, RMX 20w40, RMX 30w40, RMX 40, RMX 40 10-31, RMX 30, RMX 60.
Solid Compensation RMX Modules, 60 mm length:
RMX 5w40/0, RMX 10w40/0.
Single Diameter RMX Modules, 60 mm length:
RMX 20w40/16.5, RMX 60/54
Adaptable Multi-diameter RX BG B Modules, 60 mm length:
RX 20w40 BG B, RX 30w40 BG B, RX 40 BG B, RX 40 10-31 BG B, RX 30 BG B, RX 40 BG B.
Solid Compensation RX BG B Modules, 60 mm length:
RX 10w40/ BG B.
Conditions of Acceptability:
A The above listed cable transit devices shall be installed in accordance with the applicable local electrical
code and final acceptance is subject to inspection by the local authority having jurisdiction.
B Cable Transit Devices to be approved as apparatuses concerning the following special conditions for safe
use:
- For maintaining the explosion protection, the Assembly Instruction that accompanies the products,
shall be considered.
- Only cable for fixed installation is permitted for the Cable Entry.
- For optimum reliability wait 24 hours or longer after installation before exposing the cables/pipes to
strain or pressure.
- The cables shall have sufficient clamping to ensure that no pulling or twisting will be transmitted to
the terminals
| DQD 507 Rev. 2019-04-30 | © 2018 CSA Group. All rights reserved. | Page 2 |
APPLICABLE REQUIREMENTS
| CSA Std. C22.2 No. 18.3-12 | Conduit, Tubing and Cable Fittings. |
| CSA Std. C22.2 No. 94.2-15 | Enclosures for Electrical Equipment, Environmental Considerations |
| CAN-CSA C22.2 No. 60079-0: 15 | Explosive Atmospheres - Part 0: Equipment - General requirements |
| CAN-CSA C22.2 No. 60079-7: 16 | Explosive Atmospheres - Part 7: Equipment protection by Increased |
| Safety “e” | |
| CAN/CSA C22.2 No. 60079-31: 15 | Explosive atmospheres - Part 31: Equipment dust ignition protection by |
| enclosure “t” |
| UL Standard 514B, 6th Ed. | Conduit, Tubing and Cable Fittings. |
| UL Standard 50E, 2nd Ed | Enclosures for Electrical Equipment, Environmental Considerations. |
| UL 60079-0 - 6th Ed. | Explosive Atmospheres - Part 0: Equipment - General requirements |
| UL 60079-7 - 5th Ed | Explosive Atmospheres - Part 7: Equipment protection by Increased |
| Safety “e”. | |
| UL 60079-31 - 2nd Ed | Explosive Atmospheres - Part 31: Equipment Dust Ignition Protection |
| by Enclosure “t” |
MARKINGS
See Certification Report for Complete details.
| DQD 507 Rev. 2019-04-30 | © 2018 CSA Group. All rights reserved. | Page 3 |