Doc_32861_3-optimized

SP Sveriges Tekniska Member of
Forskningsinstitut

SP Certifiering

Box 553

SE-371 23 Karlskrona

SWEDEN www.eota.eu

Tel: +46 10 516 63 00

Web: www.sp.se

Mail: eta-se@sp.se

European Technical Assessment ETA 11/0313
of 30/06/2015

General Part

Technical Assessment Body issuing the ETA SP Sveriges Tekniska Forskningsinstitut

| Trade name of the construction product | Roxtec Modular Penetration Sealing System |

| Product family to which the construction | Fire stopping and fire sealing products – |
| product belongs | Penetration seals |

| Manufacturer | Roxtec International AB, |
Box 540,
SE-371 23 Karlskrona, Sweden,
Internet: www.roxtec.com

Manufacturing plant(s) Roxtec International AB, Karlskrona, Sweden

| This European Technical Assessment | 30 pages including 4 Annexes which form an |
| contains | integral part of this assessment. |
Annex 5 contains confidential information and is
not included in the European Technical
Assessment when that assessment is publicly
available.

This European Technical Assessment is ETAG 026-1, edition 9 April 2013 and ETAG
issued in accordance with regulation (EU) No 026-2, edition August 2011, used as European
305/2011, on the basis of Assessment Document (EAD)

| This version replaces | ETA-11/0313 issued on 16/12/2011 |

Translations of this European Technical Assessment in other languages shall fully correspond to the
original issued document and should be identified as such.

Communication of this European Technical Assessment, including transmission by electronic means,
shall be in full (excepted the confidential Annex(es) referred to above). However, partial reproduction may
be made with the written consent of the issuing Technical Assessment Body. Any partial reproduction has

to be identified as such.

4P02632 ETA 11/0313 of 30/06/2015 – page 1 of 30
Ver.14-2
1 Technical description of the product
This ETA refers to cable penetration seal with the designation “Roxtec Modular Penetration

Sealing System”.

The Roxtec Modular Penetration Sealing System consists of rectangular frames: G Frame and
B frame and round frames: R frame (multiple cables), RS series (single cables) and H3-seals
(three cables). The frames are used together with elastometric blocks and a compression unit.

The frames can either be cast, bolted, welded or fitted into sleeves. The frames and other steel
components are made of stainless steel or galvanised steel. Steel sleeves and frames are also

available in coated mild steel.

Details of the systems are shown in Annexes 2-3.

Detailed design specifications for components are shown in the supporting document Annex 5.
Annex 5 is a formal part of the ETA, and the valid version of the document is the latest version
filed by SP Sveriges Tekniska Forskningsinstitut.

2 Specification of the intended use(s) in accordance with the
applicable European Assessment Document (hereinafter EAD)
The intended use of Roxtec Modular Penetration Sealing System is to reinstate the fire
resistance performance of flexible and rigid wall constructions and rigid floor constructions,

where they are penetrated by various cables.

Details of the supporting constructions, cables etc are shown in Annexes 2-4. For the

installation procedure, see Annex 1.

The provisions made in this ETA are based on an assumed working life of the Roxtec Modular
Penetration Sealing System of 25 years. The indications given on the working life cannot be
interpreted as a guarantee given by the producer, but are to be regarded only as a means for
choosing the right products in relation to the expected economically reasonable working life of

the works.

Use category

The use category of Roxtec Modular Penetration Sealing System is

Type X, for the system with components made of stainless steel or galvanised steel.

and

Type Z2, for the system with components made of coated mild steel

Type X: intended for use in conditions exposed to weathering
Type Y1: intended for use at temperatures below 0°C with exposure to UV but no
exposure to rain
Type Y2: intended for use at temperatures below 0°C, but with no exposure to rain nor UV

| 4P02632 | ETA 11/0313 of 30/06/2015 – page 2 of 30 |
Ver.14-2

Type Z1: intended for use in internal conditions with humidity equal to or higher than 85 %
RH, excluding temperatures below 0°C. These uses apply for internal humidity
class 5 in accordance with EN ISO 13788
Type Z2: intended for uses in internal conditions with humidity lower than 85 % RH,
excluding temperatures below 0°C

Note: Products that meet requirements for type X, meet the requirements for all other types.
Products that meet requirements for type Y1 also meet the requirements for type Y2, Z1 and Z2.
Products that meet the requirements for type Y2 also meet the requirements for type Z1 and Z2.
Products that meet the requirements for type Z1, also meet the requirements for type Z2.

3 Performance of the product and references to the methods
used for its assessment
The characteristics given in this chapter are applicable to all combinations of materials,
components and dimensions described in this ETA if no other provisions are specified.

Provisions shall be taken such that floor penetration seals cannot be stepped on, e.g. by

covering with a wire mesh.

The service support construction shall be fixed to the building element on both sides of the
penetration in such a manner that in the case of fire no additional load is imposed on the seal.
Furthermore it is assumed that this support is maintained for the required period of fire

resistance.

3.1 Essential characteristics and their performance
Basic requirement for construction Characteristic
work
BWR 1 Mechanical
resistance and

stability

BWR 2 Safety in case of fire Reaction to fire Clause 3.1.2.1
Resistance to fire Clause 3.1.2.2 and Annex 2
BWR 3 Hygiene, health and Air permeability Clause 3.1.3.1
environment Water permeability Clause 3.1.3.2
Content and/or release of Clause 3.1.3.3
dangerous substances
BWR 4 Safety in use Mechanical resistance and Clause 3.1.4.1
stability
Resistance to impact and Clause 3.1.4.2
movement
Adhesion Clause 3.1.4.3
BWR 5 Protection against Airborne sound insulation Clause 3.1.5.1
noice
BWR 6 Energy economy and Thermal properties Clause 3.1.6.1
heat retention Water vapour permeability Clause 3.1.6.2
BWR 7 Sustainable use of None Clause 3.1.7
natural resources
General aspects Use category regarding Clause 3.1.8
relating to fitness for environemental conditions
use – Durability and

serviceability

4P02632 ETA 11/0313 of 30/06/2015 – page 3 of 30
Ver.14-2
3.1.1 Mechanical resistance and stability (BWR 1)

Not relevant, no performace assessed (NPA).

3.1.2 Safety in case of fire (BWR 2)

3.1.2.1 Reaction to fire

Roxtec Modular Penetration Sealing System fulfils the requirement for reaction to fire class

B-s1,d0 in accordance with EN 13501-1.

3.1.2.2 Resistance to fire

The Roxtec Modular Penetration Sealing System has been tested in accordance with
EN 1366-3: 2009 and classified in accordance with EN 13501-2, as given in Annex 2.

3.1.3 Hygiene, health and environment (BWR 3)

3.1.3.1 Air permeability

No Performance Assessed (NPA).

3.1.3.2 Water permeability

No Performance Assessed (NPA).

3.1.3.3 Release of dangerous substances

According to the manufacturer’s declaration, the product specification has been compared with
the list of dangerous substances of the European Commission to verify that that it does not
contain such substances above the acceptable limits.

A written declaration in this respect was submitted by the ETA-holder.

Note: In addition to the specific clauses relating to dangerous substances contained in this ETA,
there may be other requirements applicable to the products falling within its scope (e.g.
transposed European legislation and national laws, regulations and administrative provisions).
In order to meet the provisions of the Construction Product Directive, these requirements need
also to be complied with, when and where they apply.

3.1.4 Safety in use (BWR 4)

3.1.4.1 Mechanical resistance and stability

No Performance Assessed (NPA).

3.1.4.2 Resistance to impact and movement

No Performance Assessed (NPA).

3.1.4.3 Adhesion

No Performance Assessed (NPA).

4P02632 ETA 11/0313 of 30/06/2015 – page 4 of 30
Ver.14-2

3.1.5 Protection against noise (BWR 5)

3.1.5.1 Airborne sound insulation

No Performance Assessed (NPA).

3.1.6 Energy economy and heat retention (BWR 6)

3.1.6.1 Thermal properties

The thermal transmittance coefficient (U) has been calculated in accordance to

EN ISO 10077-2 for the G frame system:

G frame + 100 mm stone wool, density 100 kg/m3 U = 0.33 W/(m2K)

G 8+8x2 U = 2.7 W/(m2K)
G 6x1 U = 3.3 W/(m2K)

3.1.6.2 Water vapour permeability

No Performance Assessed (NPA).

3.1.7 Sustainable use of natural resources (BWR 7)

Not relevant, No Performance Assessed (NPA).

3.1.8 General aspects relating to fitness for use - Durability and serviceability
Roxtec Modular Penetration Sealing System has been tested in accordance with EOTA
Technical Report – TR024 – Edition 2009-07 and ETAG 026-2 for the type X and Z2 use

categories. The results were:

Type X for the system with components of stainless steel or galvanised steel: intended for use

at conditions exposed to weathering

Type Z2 for the system with components of coated mild steel: intended for use in internal
conditions with humidity lower than 85 % RH, excluding temperatures below 0°C

4 Assessment and verification of constancy of performance
(hereinafter AVCP) system applied, with reference to its legal

base

According to the decision 1999/454/EC - Commission decision of date 22 June 1999 (OJ L
178/52 of 14/07/99, p. 3, as amended by Decision of the Commission 2001/596/EC of 8
January 2001 (OJ L 209/33 of 2/8/2001, p. 2) the system of assessment and verification of
constancy of performance (see Annex V to the regulation (EU) No 305/2011 and EC delegated
act no. 568/2014 of 18 February 2014) given in the following table applies:

Product(s) Intended use(s) Level(s) or class(es) System(s)
Fire stopping and fire For fire Any 1
sealing products compartmentation
and/or fire protection or

fire performance

4P02632 ETA 11/0313 of 30/06/2015 – page 5 of 30
Ver.14-2
5 Technical details necessary for the implementation of the
AVCP system, as provided for in the applicable EAD
Technical details necessary for the implementation of the AVCP system are laid down in the
control plan deposited at SP Sveriges Tekniska Forskningsinstitut.

Issued in Borås on 30.06.2015
By SP Sveriges Tekniska Forskningsinstitut

Lennart Månsson
Certification Manager

4P02632 ETA 11/0313 of 30/06/2015 – page 6 of 30
Ver.14-2
ANNEX 1 Installation and maintenance

A1.1 Installation

Installation of the Roxtec Modular Penetration Sealing System should be performed in accordance to

the following installation instructions:

Insulation placed in cavities is packed in place. Insulation placed around cables is fixed in position by
using a wire which will keep the insulation in place even if exposed to fire.
The insulation around cables is put around the cable with an overlap of approx. 50 mm in order to
avoid gaps in the insulation into the cable. The wire used is placed around the insulation and
tightened, checking for gaps in the insulation towards the cable. As described before, the use of a
wire, is to keep the insulation in place in order to avoid for the insulation to slide of or loosen. The wire
should be placed with an approximate CC distance of 100 mm. In general minimum 2 wires should be
used securing the insulation. After the insulation is secured and tightened around the cables, the
insulation is pushed towards the sealing as much as possible to avoid a gap between insulation of the

seal and insulation of the cables.

A1.1.1 Roxtec R frame

4P02632 ETA 11/0313 of 30/06/2015 – page 7 of 30
Ver.14-2

A1.1.2 Roxtec RS seal

4P02632 ETA 11/0313 of 30/06/2015 – page 8 of 30
Ver.14-2

A1.1.3 Roxtec Wedge/G frame

4P02632 ETA 11/0313 of 30/06/2015 – page 9 of 30
Ver.14-2

Installation options and tools

Packaging space

A1.1.4 Roxtec B frame

Frame assembly

4P02632 ETA 11/0313 of 30/06/2015 – page 10 of 30
Ver.14-2

Installation, casting

Installation, bolting

4P02632 ETA 11/0313 of 30/06/2015 – page 11 of 30
Ver.14-2
B frame, aperture dimensions for bolted installations

Module installation

4P02632 ETA 11/0313 of 30/06/2015 – page 12 of 30
Ver.14-2

13

Installation options and tools

Packing space

A1.1.5 Roxtec H3-seals

4P02632 ETA 11/0313 of 30/06/2015 – page 13 of 30
Ver.14-2

A1.2 Indications to the manufacturer

A1.2.1 Packaging, transport and storage

During storage, the Roxtec Modular Penetration Sealing System or part there of, shall be kept indoors

in its original packaging at room temperature.

No other special measures are required with regard to the packaging, transport and storage.

A1.2.2 Use, maintenance, repair

The Roxtec Modular Penetration Sealing System should be installed and used as described earlier in

this document.

The Roxtec Modular Penetration Sealing System which is damaged should not be used or if damaged
after installation, should be removed and replaced with undamaged components.

4P02632 ETA 11/0313 of 30/06/2015 – page 14 of 30
Ver.14-2

ANNEX 2

Resistance to fire classification of Roxtec Modular Penetration Sealing

System:

A2.1 R frame

A2.1.1 System description

The element R frame in sizes (R 70, R 75, R 100, R 125, R 127, R 150 and R 200) is constructed of a
set of components: a flanged steel frame, stone wool insulation, a sealing compound (Roxtec
Lubricant), screws and a system of elastometric blocks and a compression device. The elastometric
blocks are RM 30 and RM 40 of thickness 60 mm. The element is unsymmetrical with the flange of
the steel sleeves on one side and the stone wool insulation on the other side of the element. The
system is shown in the drawing no. S1022840, see annex 3.1.

A2.1.1.1 Supporting constructions

The floor is to be classified in at least EI 60 in accordance with EN 13501-2

All other information is shown in annex 3.1.

A2.1.1.2 Seal size

Maximum size of the single opening is diameter 202 mm.

A2.1.1.3 Number of penetrations

In cases where several elements are included in a single floor the minimum distance between two

adjacent elements is 200 mm.

A2.1.1.4 Cables

See the annex 3.1 and 4.

A2.1.1.5 Insulation of the steel frame and the cables
The insulation shall be made of stone wool with density 100 kg/m3 and CE marked in class A1 in

accordance to EN 13163 or EN 14303.

See also the annex 3.1.

A2.1.1.6 Fire resistant sealant

The fire resistant sealant should be a one-component low-modulus silicone rubber which is to be used
for cable penetrations through floors which is to be fire-rated at least EI 60. The sealant should be
classed for usage on constructions made of concrete.
Reaction to fire performance: requirement R2; hazard level HL1 and HL2 in accordance with CEN/TS

45545-2.

The sealant should be installed according to the supplier’s installation guides.

A2.2.1.1.7 Service support construction

See the annex 3.1.

A2.2.1.1.8 Blank seals

Allowed

A2.1.2 Resistance to fire classification

EI 60 in accordance to EN 13501-2

4P02632 ETA 11/0313 of 30/06/2015 – page 15 of 30
Ver.14-2

A2.2 RS series

A2.2.1 System description

The element RS series (RS 31-RS 125) is constructed of a set of components: a flanged steel sleeve
with a rubber frame, a rubber core and a compression device, stone wool insulation, a sealing
compound (Roxtec Lubricant) and screws. The element is unsymmetrical with the flange of the steel
sleeves on one side and the stone wool insulation on the other side of the elements. The system is
shown in the drawing no. S1022819, see annex 3.2.

A2.2.2.1 Supporting constructions

  • The wall and floor is to be classified in at least EI 60 in accordance with EN 13501-2
  • Flexible walls with timber studs shall be mounted with a minimum distance of 100 mm to the studs,
    the cavities between the aperture framing and the studs shall be closed and minimum 100 mm
    insulation of class A1 or A2 according to EN 13501-1 and shall be provided within the cavities
    between the aperture framing and the studs of the wall.

All other information is shown in annex 3.2.

A2.2.2.1 Seal size

Maximum size of the single opening is diameter 127 mm.

A2.2.2.2 Number of penetrations

In cases where several elements are included in a single wall the minimum distance between two

adjacent elements is 200 mm.

A2.2.2.2.3 Aperture framing

Flexible walls shall be constructed with aperture framing consisting of lintel transoms and lintel studs.
The lintel transoms are mounted between two adjacent studs of the wall and the lintel studs are
mounted between the upper and lower transoms. The lintels are minimum 0,7 mm thick rolled steel
C-studs. The space between the lintels, the boards and the sleeves of the elements is filled with stone
wool insulation of class A1 in accordance to EN 13501-1.

A2.2.2.2.4 Cables

See the annex B2 and C.

A2.2.2.2.5 Insulation of the sleeve and cables

The insulation shall be made of stone wool with density 100 kg/m3 and CE marked in class A1 in

accordance to EN 13163 or EN 14303.

See also the annex 3.2.

A2.2.2.2.6 Fire resistant sealant

The fire resistant sealant should be a one-component low-modulus silicone rubber which is to be used
for cable penetrations through walls and floors which is to be fire-rated at least EI 60. The sealant
should be classed for usage on constructions made of concrete and gypsum.
Reaction to fire performance: requirement R2; hazard level HL1 and HL2 in accordance with CEN/TS

45545-2.

The sealant should be installed according to the supplier’s installation guides.

A2.2.2.7 Service support construction

See the annex 3.2.

A2.2.2.2.8 Blank seals

Allowed.

4P02632 ETA 11/0313 of 30/06/2015 – page 16 of 30
Ver.14-2

A2.2.2.2.9 Resistance to fire classification

EI 60 in accordance to EN 13501-2

4P02632 ETA 11/0313 of 30/06/2015 – page 17 of 30
Ver.14-2

A2.3 G Frame

A2.3.1 System description

The element G Frame is constructed of a set of components: a flanged steel combination frame,
stone wool insulation, a sealing compound (Roxtec Lubricant), screws and a system of elastometric
blocks and one or more compression devices. The elastometric blocks are RM 20, RM 20W40,
RM 30, RM 40, RM 60, RM 90 and RM 120 of 60 mm thickness. The element is unsymmetrical with
the flange of the steel frame on one side and the stone wool insulation on the other side of the
element. The system is shown in the drawing no. S1022839 (EI 60), S1501645 (EI 90) and S1501658

(EI 120), see annex 3.3, 3.4 and 3.5.

A2.3.1.1 Supporting constructions

EI 60

  • The wall and floor is to be classified in at least EI 60 in accordance with EN 13501-2
  • Flexible walls with timber studs shall be mounted with a minimum distance of 100 mm to the studs,
    the cavities between the aperture framing and the studs shall be closed and minimum 100 mm
    insulation of class A1 or A2 according to EN 13501-1 and shall be provided within the cavities
    between the aperture framing and the studs of the wall.
    All other information is shown in annex 3.3, 3.4 and 3.5.

EI 90, EI 120

  • The wall and floor shall be of conrete or masonry of a thickness equal or greater than 150 mm and a
    density equal or greater than 550 kg/m3 and is to be classified in at least EI 90/EI 120 in accordance

with EN 13501-2.

A2.3.1.2 Seal size

EI 60

Maximum size of single frame opening (width x height): 120 x 278 mm (equal to size 8).

EI 90, EI 120

Maximum size of single frame opening (width x height): 120 x 278 mm (equal to size 8) provided the
total amount of cross sections of the services does not exceed 60 % of the penetration area.

A2.3.1.3 Number of penetrations

EI 60

Any number of single openings in rigid walls and rigid floors.
Up to 4 x 1 or 2 x 2 single openings when mounted in flexible walls.
The minimum distance between two adjacent single frames or combination frames is 200 mm.

EI 90, EI 120

Any number of single openings in rigid walls and rigid floors.
The minimum distance between two adjacent single frames or combination frames is 200 mm.

A2.3.1.4 Aperture framing

Flexible walls shall be constructed with aperture framing consisting of lintel transoms and lintel studs.
The lintel transoms are mounted between two adjacent studs of the wall and the lintel studs are
mounted between the upper and lower transoms. The lintels are minimum 0.7 mm thick rolled steel
C-studs. The space between the lintels, the boards and the frames of the elements is filled with stone
wool insulation of class A1 in accordance to EN 13501-1.

4P02632 ETA 11/0313 of 30/06/2015 – page 18 of 30
Ver.14-2

A2.3.1.5 Cables

EI 60

See the annex 3.3 and 4.

EI 90, EI 120

See the annex 3.4, 3.5 and 4.

A2.3.1.6 Insulation of the steel frame and the cables
The insulation shall be made of stone wool with density 100 kg/m3 and CE marked in class A1 in

accordance to EN 13163 or EN 14303.

See also the annex 3.3, 3.4 and 3.5.

A2.3.1.7 Fire resistant sealant

EI 60

The fire resistant sealant should be a one-component low-modulus silicone rubber which is to be used
for cable penetrations through walls and floors which is to be fire-rated EI 60. The sealant should be
classed for usage on constructions made of concrete and gypsum.
Reaction to fire classification: requirement R2; hazard level HL1 and HL2 in accordance with CEN/TS

45545-2.

The sealant should be installed according to the supplier’s installation guides.

See also the annex 3.3.

EI 90, EI 120

The fire resistant sealant should be a one-component low-modulus silicone rubber which is to be used
for cable penetrations through walls and floors which is to be fire-rated EI 90/EI 120. The sealant
should be classed for usage on constructions made of concrete and gypsum.
Reaction to fire performance: requirement R2; hazard level HL1 and HL2 in accordance with CEN/TS

45545-2.

The sealant should be installed according to the supplier’s installation guides.

See also the annex 3.4 and 3.5.

A2.3.1.8 Service support construction

See the annex 3.3, 3.4 and 3.5.

Max distance 450 mm between the seal and the first support.

A2.3.1.9 Blank seals

Allowed.

A2.3.2 Resistance to fire classification

EI 60, EI 90 and EI 120 in accordance to EN 13501-2.

4P02632 ETA 11/0313 of 30/06/2015 – page 19 of 30
Ver.14-2

A2.4 B Frame

A2.4.1 System description

The element B Frame is constructed of a set of components: a flanged steel combination frame, stone
wool insulation, a sealing compound (Roxtec Lubricant), screws and a system of elastometric blocks
and one or more compression devices. The elastometric blocks are RM 20, RM 20W40, RM 30,
RM 40, RM 60, RM 90 and RM 120 of 60 mm thickness. The element is unsymmetrical with the
flange of the steel frame on one side and the stone wool insulation on the other side of the element.
The system is shown in the drawing no. S1022839 (EI 60) and S1501645 (EI 90), see annex 3.3 and

3.4.

A2.4.1.1 Supporting constructions

EI 60

  • The wall and floor is to be classified in at least EI 60 in accordance with EN 13501-2
  • Flexible walls with timber studs shall be mounted with a minimum distance of 100 mm to the studs,
    the cavities between the aperture framing and the studs shall be closed and minimum 100 mm
    insulation of class A1 or A2 according to EN 13501-1 and shall be provided within the cavities
    between the aperture framing and the studs of the wall.

All other information is shown in annex 3.3.

EI 90

The floor is to be classified in at least EI 90 in accordance with EN 13501-2.

A2.4.1.2 Seal size

Maximum size of single frame opening (width x height): 120 x 278 mm (equal to size 8).

A2.4.1.3 Number of penetrations

EI 60

Any number of single openings in rigid walls and rigid floors. Up to B 8 x 4 in flexible walls. Minimum
200 mm between two adjacent single frames or combination frames.

EI 90

Any number of single openings in rigid floors. Minimum 200 mm between two adjacent single frames

or combination frames.

A2.4.1.4 Aperture framing

Flexible walls shall be constructed with aperture framing consisting of lintel transoms and lintel studs.
The lintel transoms are mounted between two adjacent studs of the wall and the lintel studs are
mounted between the upper and lower transoms. The lintels are minimum 0.7 mm thick rolled steel
C-studs. The space between the lintels, the boards and the frames of the elements is filled with stone
wool insulation of class A1 in accordance to EN 13501-1.

A2.4.1.5 Cables

EI 60

See the annex 3.3 and 4.

EI 90

See the annex 3.4 and 4.

A2.4.1.6 Insulation of the steel frame and the cables
The insulation shall be made of stone wool with density 100 kg/m3 and CE marked in class A1 in

accordance to EN 13163 or EN 14303.

See also the annex 3.3.

4P02632 ETA 11/0313 of 30/06/2015 – page 20 of 30
Ver.14-2

A2.4.1.7 Fire resistant sealant

EI 60

The fire resistant sealant should be a one-component low-modulus silicone rubber which is to be used
for cable penetrations through walls and floors which is to be fire-rated EI 60. The sealant should be
classed for usage on constructions made of concrete and gypsum.
Reaction to fire performance: requirement R2; hazard level HL1 and HL2 in accordance with CEN/TS

45545-2.

The sealant should be installed according to the supplier’s installation guides.

See also the annex 3.3.

EI 90

The fire resistant sealant should be a one-component low-modulus silicone rubber which is to be used
for cable penetrations through floors which is to be fire-rated EI 90. The sealant should be classed for

usage on constructions made of concrete.

Reaction to fire performance: requirement R2; hazard level HL1 and HL2 in accordance with CEN/TS

45545-2.

The sealant should be installed according to the supplier’s installation guides.

See also the annex 3.4.

A2.4.1.8 Service support construction

See the annex 3.3 and 3.4.

A2.4.1.9 Blank seals

Allowed

A2.4.2 Resistance to fire classification

EI 60 and EI 90 in accordance to EN 13501-2.

4P02632 ETA 11/0313 of 30/06/2015 – page 21 of 30
Ver.14-2

A2.5 H3-seals

A2.5.1 System description

The element H3-seal (size 150 and 200 mm) is a circular seal adapted for three cables. The seal can
be installed directly in core-drilled or casted aperture or in a welded sleeve. The cables are insulated
with stone wool and the remaining cavity is filled up with stone wool. The element is unsymmetrical
with the flange of the steel frame on one side and the stone wool insulation on the other side of the
element. The system is shown in the drawing no. 1501809, see annex 3.6.

A2.5.1.1 Supporting constructions

EI 60

The wall and floor is to be classified in at least EI 60 in accordance with EN 13501-2.

EI 90

The floor is to be classified in at least EI 90 in accordance with EN 13501-2.

A2.5.1.2 Seal size

Maximum size of opening (diameter): 200 mm.

A2.5.1.3 Number of penetrations

EI 60

Any number of single openings in rigid walls and rigid floors. Minimum 200 mm between two adjacent

transits.

EI 90

Any number of single openings in rigid floors. Minimum 200 mm between two adjacent transits.

A2.5.1.4 Aperture framing

-

A2.5.1.5 Cables

EI 60/EI 90

See the annex 3.6.

A2.5.1.6 Insulation of the steel frame and the cables
The insulation shall be made of stone wool with density 100 kg/m3 and CE marked in class A1 in

accordance to EN 13163 or EN 14303.

See also the annex 3.6.

A2.5.1.7 Fire resistant sealant

EI 60

The fire resistant sealant should be a one-component low-modulus silicone rubber which is to be used
for cable penetrations through walls and floors which is to be fire-rated EI 60. The sealant should be
classed for usage on constructions made of concrete.
Reaction to fire performance: requirement R2; hazard level HL1 and HL2 in accordance with CEN/TS

45545-2.

The sealant should be installed according to the supplier’s installation guides.

See also the annex 3.6.

EI 90

The fire resistant sealant should be a one-component low-modulus silicone rubber which is to be used
for cable penetrations through floors which is to be fire-rated EI 90. The sealant should be classed for

usage on constructions made of concrete.

Reaction to fire performance: requirement R2; hazard level HL1 and HL2 in accordance with CEN/TS

45545-2.

4P02632 ETA 11/0313 of 30/06/2015 – page 22 of 30
Ver.14-2
The sealant should be installed according to the supplier’s installation guides.

See also the annex 3.6.

A2.5.1.8 Service support construction

See the annex 3.6.

A2.5.1.9 Blank seals

Allowed

A2.5.2 Resistance to fire classification

EI 60 and EI 90 in accordance to EN 13501-2.

4P02632 ETA 11/0313 of 30/06/2015 – page 23 of 30
Ver.14-2

ANNEX 3.1 R frame EI 60

ETA 11/0313 of 30/06/2015

page 24 of 30

ANNEX 3.2 RS EI 60

ETA 11/0313 of 30/06/2015

page 25 of 30

ANNEX 3.3 B/G EI 60

ETA 11/0313 of 30/06/2015

page 26 of 30

ANNEX 3.4 B/G EI 90

ETA 11/0313 of 30/06/2015

page 27 of 30

ANNEX 3.5 G EI 120

ETA 11/0313 of 30/06/2015

page 28 of 30

ANNEX 3.6 H3 EI 60, EI 90

ETA 11/0313 of 30/06/2015

page 29 of 30

ANNEX 4 - Services

Cable Dimensions Designation Standard Insulation /
type sheath
material
A1 5 x 1,5 mm2 bfb HD 603.3 PVC / PVC b)
A2 5 x 1,5 mm2 bff HD 22.4 EPR / PO d)
A3 5 x 1,5 mm2 bfdb HD 604.5 XLPE / EVA f)
B 1 x 95 mm2 bbff HD 603.3 HD 603.3
C1 4 x 95 mm2 HD 22.4 PVC / PVC b)
C2 4 x 95 mm2 H07RN-F 4G95 HD 22.4 EPR / PO d)
C3 4 x 95 mm2 YMz1Kmbzh 0,6/1 kV 4G95 HD 604.5 XLPE / EVA f)
PVIK-LS-HF 4x95

N2XH-J 4x95SM or N2XH-O

4x95SM

n.n.

E-NGNG-J 4x95SM or E-3G3G-J

4x95SM or

E-NGNG-O 4x95SM or E-3G3G-

O 4x95SM

D1 4 x 185 E-YCWY 4x185SM/95 HD 603.3 PVC / PVC b)
mm2 MCMK 4x815/95
NYCWY 4x185SM/95

PFSP CU 4x185/95

FKKJ 4x185/95 S

D2 4 x 185 H07RN-F 4G185 EPR / PO d)
mm2
D3 4 x 185 YMz1Kmbzh 0,6/1 kV 4G185 svs HD 604.5
mm2 PVIK-LS-HF 4x185
N2XH-J 4x185SM or N2XH-O

4x185SM

n.n.

E-NGNG-J 4x185SM or E-3G3G-

J 4x185SM or

E-NGNG-O 4x185SM or E-3G3G-

O 4x185SM

E 1 x 185 E-YY-J 1x185RM or E-YY-O HD 603.3 PVC / PVC b)
mm2 1x185RM
NYY-J 1x185RM or NYY-O

1x185RM

VV 1x185

TT 1x185 RM 0,6/1 kV

F 20 x 2 mm2 - PE / PE m)
x 0,6 mm

screened

b) PVC = Polyvinyl chloride

d) EPR = Ethylene-propylene rubber compound, PO = Polyolefin, synthetic rubber compound
f) XLPE = Cross-linked Polyethylene, EVA = Ethylene-vinyl-acetate copolymer compound

m) PE = Polyethylene, solid or cellular

4P02632 ETA 11/0313 of 30/06/2015 – page 30 of 30
Ver.14-2