CERTIFICATE OF FIRE APPROVAL
This is to certify that
The product(s) detailed below will be accepted for compliance with the applicable Lloyd’s Register Rules and
Regulations for use on offshore installations classed with Lloyd’s Register, and for use on offshore installations
when authorised by contracting governments to issue the relevant certificates, licences, permits etc.
| Manufacturer | Roxtec International AB |
|---|
| Address | Box 540 |
S-371 23 Karlskrona
Sweden
| Type | PIPE AND CABLE PENETRATION JET FIRE PROTECTION SYSTEM |
|---|
| Description | Multi Cable and Pipe (Rectangular) Transit - Type: “Roxtec RM Module Multi-Diameter |
Penetration Seals” for Jet Fire applications
| Specified Standard | Health & Safety Executive, Offshore Technology Report OTI 95 634 |
|---|---|
| “Jet Fire Resistance Test of Passive Fire Protection Materials” |
The attached Design Appraisal Document forms part of this certificate.
This certificate remains valid unless cancelled or revoked, provided the conditions in the attached Design
Appraisal Document are complied with and the equipment remains satisfactory in service.
| Date of issue | 7 March 2016 | Expiry date 6 March 2021 |
|---|
| Certificate No. | SAS F160134 | Signed |
Fire & Safety, MTES
Lloyd’s Register EMEA
LR427.2013.12
| Sheet No | 1 of 4 | Name | S. Abraham |
|---|---|---|---|
| Surveyor to Lloyd’s Register EMEA | |||
| A Member of the Lloyd’s Register Group |
Note:
This certificate is not valid for equipment, the design or manufacture of which has been varied or modified from
the specimen tested. The manufacturer should notify Lloyd’s Register of any modification or changes to the
equipment in order to obtain a valid Certificate.
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred to in this clause as
the ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense caused by reliance on the information
or advice in this document or howsoever provided, unless that person has signed a contract with the relevant Lloyd’s Register entity for the provision of this information or
advice and in that case any responsibility or liability is exclusively on the terms and conditions set out in that contract.
This is a copy of an electronic document. In the event of any conflict or ambiguity between the copy and the electronic document,
which is retained and published by Lloyd’s Register, the original electronic and certified version shall always prevail.
Page
Lloyd’s Register EMEA
2 of 4
| 71 Fenchurch Street, London, EC3M 4BS | Document number |
|---|---|
| Telephone 020 7423 2416 Fax 020 7423 2053 | SAS F160134 |
| Email med@lr.org | Issue number |
| 1 |
DESIGN APPRAISAL DOCUMENT
| Date | Quote this reference on all future communications |
|---|---|
| 5 May 2016 | MTES/SAS/TA/SA/WP25742200 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. SAS F160134
This Design Appraisal Document forms part of the Certificate.
APPROVAL DOCUMENTATION
SINTEF, Norwegian Fire Research Laboratory, Norway, Fire Test Report No. NBL-107332, dated 3 June
2005.
CONDITIONS OF CERTIFICATION
| 1. | Integrity and insulation performance criteria to be assessed from the test results below |
|---|---|
| 2. | Consisting of: a double layer of rectangular “Roxtec RM Module Multi-Diameter Penetration Seals” |
| fitted into a suitably insulated division approved for the same fire performance rating, as described |
below
| 3. | Applications in each case to be approved by Lloyd’s Register at the design stage |
|---|---|
| 4. | Production items are to be manufactured in accordance with a quality control system which shall be |
| maintained to ensure that items are of the same standard as the approved prototype |
TEST RESULTS
| Duration of Test: | 122 minutes |
|---|
| Integrity: | 122 minutes – No flaming observed on the unexposed face |
Insulation:
| Thermocouple No. | Thermocouple Position | Time to Reach 180oC (mins) |
|---|---|---|
| 1* | Penetration Seal | 66 |
| 5* | Bulkhead (Unexposed Side) | 57 |
| 11-18 | Steel Pipe Penetrations | >122 |
| 19-28 | Cable Penetrations | >122 |
Maximum Temperature Rise
| 1* | After 30 minutes of exposure ~ 127oC |
|---|---|
| 5* | After 60 minutes of exposure ~ 193oC |
| 5* | After 90 minutes of exposure ~ 289oC |
| 5* | After 120 minutes of exposure ~ 313oC |
- Thermocouples 1 and 5 are positioned 25mm away from the outer surface of the insulation surrounding
the unexposed side of the penetration.
NOTE
The above jet fire test results may be applied for the cable and pipe penetration device when used in a
bulkhead or deck application, subject to both the penetration device and the bulkhead or deck being fitted
with the same insulation arrangements as those used in the fire test.
This is a copy of an electronic document. In the event of any conflict or ambiguity between the copy and the electronic document,
which is retained and published by Lloyd’s Register, the original electronic and certified version shall always prevail.
Page
Lloyd’s Register EMEA
3 of 4
| 71 Fenchurch Street, London, EC3M 4BS | Document number |
|---|---|
| Telephone 020 7423 2416 Fax 020 7423 2053 | SAS F160134 |
| Email med@lr.org | Issue number |
| 1 |
DESIGN APPRAISAL DOCUMENT
| Date | Quote this reference on all future communications |
|---|---|
| 5 May 2016 | MTES/SAS/TA/SA/WP25742200 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. SAS F160134
DESCRIPTION OF THE TEST SPECIMEN
Panel test in accordance with OTI 95 634, comprising of a 10mm thick mild steel plate penetrated with 5
cables (outside diameters: 10, 18, 24, 29 and 79mm) and 4 steel pipes (outside diameters: 10, 18, 25, and
30mm).
The cables and pipes penetrate the panel through two layers of type “RM Modules” comprised of 60mm
thick elastomer blocks, stay plates and compression wedges, contained in rectangular steel frames, separated
by a space of 230mm filled with ceramic fibre insulation “Firemaster X-607” of nominal density 128kg/m3
and fixed within a steel support box 10 mm thick of approximate dimensions 539mm x 305mm x 350mm
(LxHxD).
The unexposed side of the panel was insulated with 125mm “Firemaster X-607, nominal density of
128kg/m3. The back and sides of the penetration box are insulated with 100mm thick “Firemaster X-607”,
nominal density 96kg/m3, retained by 3mm stainless steel pins and spring washers.
SCOPE
Although the test has been designed to reproduce conditions similar to those found in a large-scale jet fire
resulting from realistic release of hydrocarbons, it cannot guarantee a specific degree of protection from the
myriad of possible jet fires. The Jet Fire Resistance Test, or indeed large-scale demonstrations, cannot
therefore be used to confer a universal resistance rating for a specified time in the way that a standard
furnace test confers a hydrocarbon rating. Hence, this test does not give a rating analogous to the “H” rating
derived from the hydrocarbon fire resistance test but is seen as a complimentary test.
Although the method specified has been designed to simulate some of the conditions which occur in an
actual jet fire, it cannot reproduce them all exactly. The results of this test do not guarantee safety but may be
used as elements of a fire risk assessment for structures or plant. This should take into account all of the
other factors which are pertinent to an assessment of the fire hazard for a particular end use.
This is a copy of an electronic document. In the event of any conflict or ambiguity between the copy and the electronic document,
which is retained and published by Lloyd’s Register, the original electronic and certified version shall always prevail.
Page
Lloyd’s Register EMEA
4 of 4
| 71 Fenchurch Street, London, EC3M 4BS | Document number |
|---|---|
| Telephone 020 7423 2416 Fax 020 7423 2053 | SAS F160134 |
| Email med@lr.org | Issue number |
| 1 |
DESIGN APPRAISAL DOCUMENT
| Date | Quote this reference on all future communications |
|---|---|
| 5 May 2016 | MTES/SAS/TA/SA/WP25742200 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. SAS F160134
PLACE OF PRODUCTION
Roxtec International AB
Box 540
S-371 23 Karlskrona
Sweden
Fire & Safety, MTES
Lloyd’s Register EMEA
LR427.2013.12
Saji Abraham
Senior Specialist
Statutory Fire and Safety
Marine Technology and Engineering Services
Lloyd’s Register EMEA
Supplementary Type Approval Terms and Conditions
This certificate and Design Appraisal Document relates to type approval, it certifies that the prototype(s) of the
product(s) referred to herein has/have been found to meet the applicable design criteria for the use specified herein, it
does not mean or imply approval for any other use, nor approval of any products designed or manufactured
otherwise than in strict conformity with the said prototype(s).
This is a copy of an electronic document. In the event of any conflict or ambiguity between the copy and the electronic document,
which is retained and published by Lloyd’s Register, the original electronic and certified version shall always prevail.