CERTIFICATE OF FIRE APPROVAL

This is to certify that

The product(s) detailed below will be accepted for compliance with the applicable Lloyd’s Register Rules and
Regulations for use on offshore installations classed with Lloyd’s Register, and for use on offshore installations
when authorised by contracting governments to issue the relevant certificates, licences, permits etc.

Manufacturer Roxtec International AB

| Address | Box 540 |
S-371 23 Karlskrona

Sweden

Type CABLE PENETRATION (HYDROCARBON FIRE TEST)

| Equipment Description | Fire Resisting Circular Multiple Cable Penetration – Type: “Roxtec RS frames” for |
restricted applications in H-60 and H-120 Class steel bulkheads and decks.

Specified Standard IMO Fire Test Procedures Code, Annex 1, Part 3
EN 1363-2 Hydrocarbon Time Temperature Curve

The attached Design Appraisal Document forms part of this certificate.
This certificate remains valid unless cancelled or revoked, provided the conditions in the attached Design
Appraisal Document are complied with and the equipment remains satisfactory in service.

Date of issue 7 March 2016 Expiry date 6 March 2021

| Certificate No. | SAS F160132 | Signed | Fire & Safety, MTES |
Lloyd’s Register EMEA

LR427.2013.12

Sheet No 1 of 3 Name S. Abraham
Surveyor to Lloyd’s Register EMEA
A Member of the Lloyd’s Register Group

Note:

This certificate is not valid for equipment, the design or manufacture of which has been varied or modified from
the specimen tested. The manufacturer should notify Lloyd’s Register of any modification or changes to the

equipment in order to obtain a valid Certificate.

Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred to in this clause as
the ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense caused by reliance on the information
or advice in this document or howsoever provided, unless that person has signed a contract with the relevant Lloyd’s Register entity for the provision of this information or
advice and in that case any responsibility or liability is exclusively on the terms and conditions set out in that contract.

This is a copy of an electronic document. In the event of any conflict or ambiguity between the copy and the electronic document,
which is retained and published by Lloyd’s Register, the original electronic and certified version shall always prevail.
Page

Lloyd’s Register EMEA

2 of 3

71 Fenchurch Street, London, EC3M 4BS Document number
Telephone 020 7423 2416 Fax 020 7423 2053 SAS F160132
Email med@lr.org Issue number
1

DESIGN APPRAISAL DOCUMENT

Date Quote this reference on all future communications
5 May 2016 MTES/SFS/TA/SA/WP25742200

ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. SAS F160132

This Design Appraisal Document forms part of the Certificate.

APPROVAL DOCUMENTATION

Danish Institute of Fire and Security Technology, Test Report No. PG11087 dated 12 February 2003.
Danish Institute of Fire and Security Technology, Test Report No. PG11088 dated 18 February 2003.
Det Norske Veritas, Malmo, Watertightness and Gastightness Test Report Nos. MLM 010235 dated 21

August 2001.

CONDITIONS OF CERTIFICATION

1. When used in conjunction with H-60 and H-120 Class bulkheads and decks, when insulated with
approved arrangements suitable for the required rating on the fire hazard side (restricted applications)
2. For applications in H-0 and H-0 (400°C) Class steel bulkheads and decks, penetrations are to be fitted
with the same or equivalent H-120 Class insulation arrangements as those used in the fire tests
(including any insulation fitted on the penetration itself in the tests) for a minimum distance of 450mm
around the penetration, on all fire risk sides in bulkheads and decks and insulation should be extended
to cover the full side(s) and the end face(s) of the steel frame, with an overlap of at least 20mm from the

steel edges

3. The above mentioned H-120 Class insulation arrangements should be additional to any thermal or
acoustic insulation, but may include any fire rated insulation (e.g. H-60) already fitted on the bulkhead
or deck and/or on the penetration itself, such that the total fire rating is H-120
4. Frame types: RS seals
5. Frame sizes: 23-125
6. Consisting of: Circular steel sleeves (welded or bolted) with RS-type (EMC versions included) halogen
free rubber sealing, mounted to the non-fire exposed side in steel bulkheads and non-fire exposed side

(top side) in steel decks

7. Production items are to be manufactured in accordance with a quality control system which shall be
maintained to ensure that items are of the same standard as the approved prototype

NOTES

1. The penetration sizes of 23, 31, 125 were subjected to gas overpressure with a value of 4.0 bar for a
duration of 30 minutes, as detailed in report No. MLM 010235.
2. The penetration sizes 23, 31, 43, 50, 125 were subjected to a hydrostatic pressure test for 60 minutes at
6.0 bar without any leakage, as detailed in report Nos. MLM 010235.

This is a copy of an electronic document. In the event of any conflict or ambiguity between the copy and the electronic document,
which is retained and published by Lloyd’s Register, the original electronic and certified version shall always prevail.
Page

Lloyd’s Register EMEA

3 of 3

71 Fenchurch Street, London, EC3M 4BS Document number
Telephone 020 7423 2416 Fax 020 7423 2053 SAS F160132
Email med@lr.org Issue number
1

DESIGN APPRAISAL DOCUMENT

Date Quote this reference on all future communications
5 May 2016 MTES/SFS/TA/SA/WP25742200

ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. SAS F160132

PLACE OF PRODUCTION

Roxtec International AB

Box 540

S-371 23 Karlskrona

Sweden

Fire & Safety, MTES

Lloyd’s Register EMEA

LR427.2013.12

Saji Abraham

Senior Specialist

Statutory Fire and Safety

Marine Technology and Engineering Services

Lloyd’s Register EMEA

Supplementary Type Approval Terms and Conditions

This certificate and Design Appraisal Document relates to type approval, it certifies that the prototype(s) of the
product(s) referred to herein has/have been found to meet the applicable design criteria for the use specified herein, it
does not mean or imply approval for any other use, nor approval of any products designed or manufactured
otherwise than in strict conformity with the said prototype(s).

This is a copy of an electronic document. In the event of any conflict or ambiguity between the copy and the electronic document,
which is retained and published by Lloyd’s Register, the original electronic and certified version shall always prevail.