CERTIFICATE OF FIRE APPROVAL

This is to certify that

The product(s) detailed below will be accepted for compliance with the applicable Lloyd’s Register Rules and
Regulations for use on offshore installations classed with Lloyd’s Register, and for use on offshore installations
when authorised by contracting governments to issue the relevant certificates, licences, permits etc.

Manufacturer Roxtec International AB

| Address | Box 540 |
S-371 23 Karlskrona

Sweden

Type CABLE PENETRATION (HYDROCARBON FIRE TEST)

| Equipment Description | Fire Resisting Single or Multi Cable (Rectangular) Penetration– |
Types: “S-, S BTB, SO-, SF-, SFO, SK-, and SR” for restricted applications in H Class
steel bulkheads and decks

Specified Standard (UK) Department of Energy hydrocarbon time/temperature relationship.
IMO Resolution A.754 (18) Performance Criteria

The attached Design Appraisal Document forms part of this certificate.
This certificate remains valid unless cancelled or revoked, provided the conditions in the attached Design
Appraisal Document are complied with and the equipment remains satisfactory in service.

Date of issue 21 March 2016 Expiry date 20 March 2021

| Certificate No. | SAS F160133 | Signed | Fire & Safety, MTES |
Lloyd’s Register EMEA

LR427.2013.12

Sheet No 1 of 3 Name S. Abraham
Surveyor to Lloyd’s Register EMEA
A Member of the Lloyd’s Register Group

Note:

This certificate is not valid for equipment, the design or manufacture of which has been varied or modified from
the specimen tested. The manufacturer should notify Lloyd’s Register of any modification or changes to the

equipment in order to obtain a valid Certificate.

Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred to in this clause as
the ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense caused by reliance on the information
or advice in this document or howsoever provided, unless that person has signed a contract with the relevant Lloyd’s Register entity for the provision of this information or
advice and in that case any responsibility or liability is exclusively on the terms and conditions set out in that contract.

This is a copy of an electronic document. In the event of any conflict or ambiguity between the copy and the electronic document,
which is retained and published by Lloyd’s Register, the original electronic and certified version shall always prevail.
Page

Lloyd’s Register EMEA

2 of 3

71 Fenchurch Street, London, EC3M 4BS Document number
Telephone 020 7423 2416 Fax 020 7423 2053 SAS F160133
Email med@lr.org Issue number
1

DESIGN APPRAISAL DOCUMENT

Date Quote this reference on all future communications
5 May 2016 MTES/SFS/TA/SA/WP25742200

ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. SAS F160133

This Design Appraisal Document forms part of the Certificate.

APPROVAL DOCUMENTATION

SINTEF Energy, Norwegian Fire Research Laboratory, Norway, Fire Test Reports No: 250000.20/90.313,
dated 9 November 1990 and No: SB 846007.06/970706 dated 19 September 1997. SP Technical Research
Centre, Boras, Sweden; Fire Test Report no: P703775 dated 07 December 2007.

CONDITIONS OF CERTIFICATION

1. When used in conjunction with H-60 and H-120 Class steel bulkheads and decks, when insulated with
approved arrangements suitable for the required rating on the fire hazard side (restricted applications)
2. For applications in H-0 and H-0 (400°C) Class steel bulkheads and decks, penetrations are to be
fitted with the same or equivalent H-120 Class insulation arrangements as those used in the fire tests
(including any insulation fitted on the penetration itself in the tests) for a minimum distance of
450mm around the penetration, on all fire risk sides in bulkheads and decks and insulation should
be extended to cover the full side(s) and the end face(s) of the steel frame, with an overlap of at least
20mm from the steel edges. The above mentioned H-120 Class insulation arrangements should be
additional to any thermal or acoustic insulation, but may include any fire rated insulation (e.g. H-60)
already fitted on the bulkhead or deck and/or on the penetration itself, such that the total fire rating

is H-120

The above requirements do not apply to “S6 BTB (Back To Back) penetrations” (maximum frame size:
120mm wide x 220mm high x 200mm deep) and they are accepted for applications in H-0 Class steel

bulkheads, when fitted to the non-fire exposed side

3. The “S 8+8x3”penetrations are accepted for applications in H-60 Class steel bulkheads, when fitted
with an approved H-60 Class insulation system on the bulkhead and over the steel coaming on all
fire risk sides of bulkheads and insulation should be extended to fully cover the side(s) and face(s) of
the outer steel perimeter coaming as well as the internal steel members, with an overlap of at least

50mm from the steel edges

4. The “S 1x1” penetrations are accepted for applications in H-120 class steel bulkheads, when fitted
with an approved H-120 Class insulation system on the bulkhead and over the steel coaming on all
fire risk sides of bulkheads and insulation should be extended to fully cover the side(s) and face(s) of
the steel coaming, with an overlap of at least 50mm from the steel edges
5. The “S6” (120mm wide x 220mm high x 60mm deep) penetrations are accepted for applications in H-
120 Class steel bulkheads, when fitted to the non-fire exposed side and H-120 Class insulation on the
fire exposed side of the bulkhead extended to cover the face of the steel coaming with an overlap of

50mm from the steel edges

6. The types “S 2x1” to “S 8x1” and “S 6x2” penetrations are accepted for applications in H-60 and H-
120 Class steel decks, when fitted to the non-fire exposed side (top side) and insulation fitted to the
underside of deck extended to cover the face of the steel coaming with an overlap of at least 50mm
from the steel edges(“S 8x1” and “S 6x2” penetrations to be fully insulated on the underside for H-

120 Class steel deck applications)

This is a copy of an electronic document. In the event of any conflict or ambiguity between the copy and the electronic document,
which is retained and published by Lloyd’s Register, the original electronic and certified version shall always prevail.
Page

Lloyd’s Register EMEA

3 of 3

71 Fenchurch Street, London, EC3M 4BS Document number
Telephone 020 7423 2416 Fax 020 7423 2053 SAS F160133
Email med@lr.org Issue number
1

DESIGN APPRAISAL DOCUMENT

Date Quote this reference on all future communications
5 May 2016 MTES/SFS/TA/SA/WP25742200

ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. SAS F160133

7. Consists of: Roxtec “S” steel frames 10mm thick, filled with 60mm deep RM modules around the cables
and welded to the steel bulkhead or deck
8. “S6 BTB (Back To Back) penetrations" consists of: two “S6” penetration seals enclosed in a
rectangular steel coaming (maximum size: 120mm wide x 220mm high x 200mm deep) and

separated by an 80mm air gap

9. Used with EMC Rox Kit or Rox Kit (assembly parts), or EMC Rox Wedge Kit or Rox Wedge Kit
(alternative assembly parts), EMC Roxylon modules or Roxylon modules (multi diameter modules or

solid modules)

  1. Production items are to be manufactured in accordance with a quality control system which shall be
    maintained to ensure that items are of the same standard as the approved prototype

PLACE OF PRODUCTION

Roxtex International AB

Box 540

S-37123 Karlskrona

Sweden

Fire & Safety, MTES

Lloyd’s Register EMEA

LR427.2013.12

Saji Abraham

Senior Specialist

Statutory Fire and Safety

Marine Technology and Engineering Services

Lloyd’s Register EMEA

Supplementary Type Approval Terms and Conditions

This certificate and Design Appraisal Document relates to type approval, it certifies that the prototype(s) of the
product(s) referred to herein has/have been found to meet the applicable design criteria for the use specified herein, it
does not mean or imply approval for any other use, nor approval of any products designed or manufactured
otherwise than in strict conformity with the said prototype(s).

This is a copy of an electronic document. In the event of any conflict or ambiguity between the copy and the electronic document,
which is retained and published by Lloyd’s Register, the original electronic and certified version shall always prevail.