CERTIFICATE OF FIRE APPROVAL
This is to certify that
The product(s) detailed below will be accepted for compliance with the applicable Lloyd’s Register Rules and
Regulations for use on offshore installations classed with Lloyd’s Register, and for use on offshore installations
when authorised by contracting governments to issue the relevant certificates, licences, permits etc.
| Address | Box 540 |
S-371 23 Karlskrona
| Type | CABLE PENETRATION (HYDROCARBON FIRE TEST) |
| Equipment Description | Single Cable Circular Penetration for H-60 Bulkheads – Types: “RS-23 to RS-125” |
(36mm to 138mm sleeve diameter)
| Specified Standard | IMO Resolution A.754(18) |
| NPD Hydrocarbon Time/Temperature Curve |
| Date of issue | 7 March 2016 | Expiry date 6 March 2021 |
| Certificate No. | SAS F160135 | Signed |
Fire & Safety, MTES
Lloyd’s Register EMEA
LR427.2013.12
| Sheet No | 1 of 3 | Name | S. Abraham |
| Surveyor to Lloyd’s Register EMEA | |||
| A Member of the Lloyd’s Register Group |
Note:
This certificate is not valid for equipment, the design or manufacture of which has been varied or modified from
the specimen tested. The manufacturer should notify Lloyd’s Register of any modification or changes to the
Page
2 of 3
| 71 Fenchurch Street, London, EC3M 4BS | Document number |
| Telephone 020 7423 2416 Fax 020 7423 2053 | SAS F160135 |
| Email med@lr.org | Issue number |
| 1 |
DESIGN APPRAISAL DOCUMENT
| Date | Quote this reference on all future communications |
| 5 May 2016 | MTES/SFS/TA/SA/WP25742200 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. SAS F160135
APPROVAL DOCUMENTATION
SINTEF Energy, Norwegian Fire Research Laboratory, Norway, Fire Test Report No. 22N007.12A, dated 16
September 1999
| 1. | When used in conjunction with H-60 Class steel bulkheads only, with approved insulation |
| arrangements | |
| 2. | For applications in H-0 and H-0 (400°C) Class steel bulkheads, penetrations are to be fitted with the |
| same or equivalent H-120 Class insulation arrangements as those used in the fire tests (including any | |
| insulation fitted on the penetration itself in the tests) for a minimum distance of 450mm around the | |
| penetration, on all fire risk sides in bulkheads and insulation should be extended to cover the full | |
| side(s) and the end face(s) of the steel frame, with an overlap of at least 20mm from the steel edges | |
| 3. | The above mentioned H-120 Class insulation arrangements should be additional to any thermal or |
| acoustic insulation, but may include any fire rated insulation (e.g. H-60) already fitted on the bulkhead | |
| and/or on the penetration itself, such that the total fire rating is H-120 | |
| 4. | Consists of: Roxtec RS seals fitted around cables and enclosed in a steel sleeve that is welded to the non- |
| fire exposed side of the steel bulkhead | |
| 5. | The penetrations to be insulated on the non-fire exposed side with bulkhead insulation (75mm thick, |
| 128kg/m3 density) CARBOLANE DURABLANKETS or equivalent. An additional 250mm diameter | |
| ring of the same bulkhead insulation to be also fitted around the penetration and insulation extended to | |
| fully cover the face of the transit on the non-fire exposed side. All retained to the division by welded |
steel pins and washers
| 6. | EMC type penetrations EMC RS-23 to EMC RS-125 also acceptable |
| 7. | Production items are to be manufactured in accordance with a quality control system which shall be |
| maintained to ensure that items are of the same standard as the approved prototype |
Page
3 of 3
| 1 |
S-37123 Karlskrona
Fire & Safety, MTES
LR427.2013.12
Saji Abraham
Senior Specialist
Statutory Fire and Safety