No. LAB087222CS/001
This is to certify that the product identified below satisfies the requirements of the
standard quoted under “Reference standard”
| Description | Devices for the passage of pipes through A or B Class |
| divisions | |
| Type | Roxtec RS PPS/S Seal |
| ROMBVAGEN 2, BOX 540 | |
| SE-37123 Karlskrona |
| Manufacturer | ROXTEC INTERNATIONAL AB - ROXTEC SERVICES |
| Place of manufacture | AB |
| Reference standards | IMO Res. MSC.307(88)-(2010 FTP Code) - MSC.429(98) - |
| MSC.1/CIRC.736 |
Issued in Genoa on October 19, 2022. This Certificate is valid until August 28, 2027
No. LAB087222CS/001
Enclosure - Page 1 of 1
Roxtec RS PPS /S S eal
Circular stainless steel penetration seal type RS PPS/S for plastic pipes through bulkheads. The penetration is composed
of two Roxtec seals and an intumescent sealing strip in the middle fitted on each side of a steel sleeve symmetrically
welded to the bulkhead.
The penetration is to be insulated, on both the exposed and unexposed side of the bulkhead, with 2 layers (thickness 45
mm each) of mineral wool Rockwool type SeaRox WM 620, having a density of 90 kg/m3, cut in a circular pattern
with a width of 250 mm measured from the sleeve; the sleeve is to be insulated, on both the exposed and unexposed
side, with 2 layers of mineral wool Rockwool type SeaRox WM 620, having a density of 90 kg/m3, extending flush
with end of sleeve.
Fire resistant A-60 Class plastic pipe penetrations through steel bulkheads.
Type RS PPS/S size 43 mm; thermoplastic pipes having diameter 16 mm, with a sleeve thickness of 4 mm.
Type RS PPS/S size from 43 up to 150 mm; thermoplastic pipes having diameter ranging from 16 to 110 mm, with a
sleeve thickness of 6.5 mm.
Watertightness pressure test of 2 bar; work pressure less or equal to 1.33 bar.
Roxtec drawing No. S1584159 dated 13 October 2022 (to be regarded only as far as transit insulation) and Roxtec
drawings enclosed to the Test Report as per Danish Institute of Fire and Security Technology (DBI) No. PGB10164A
dated 20 July 2022.
Statement as per Danish Institute of Fire and Security Technology (DBI) No. PGB10164B dated 21 July 2022.
Fire resistance and watertightness Tests as per Danish Institute of Fire and Security Technology (DBI) No.
PGB10164A dated 20 July 2022 according to IMO 2010 FTP Code, MSC.429(98).