No. LAB180318CS/001
| Description | Devices for the passage of electric cables through A or B |
| Class divisions | |
| Type | Roxtec S Series - Steel Bulkhead |
| ROMBVAGEN 2, P.O. BOX 540 | |
| SE-37123 KARLSKRONA |
| Place of manufacture | ROMBVAGEN 2, P.O. BOX 540 |
| Reference standards | IMO Res. MSC.307(88)-(2010 FTP Code) |
Issued in Genoa on December 19, 2018. This Certificate is valid until December 18, 2023
No. LAB180318CS/001
Enclosure - Page 1 of 3
Roxtec S S eries - S teel Bulkhead
Devices for the passage of electric cables having diameter ranging from 10 up to 86 mm through A Class bulkheads.
The transits are composed of a steel frame having thickness of 10 mm fillet welded to the bulkhead plate and filled with
EPDM halogen free material packing system; on the upper part it is installed one module fitted with a screw expander.
Fire resistant A-60 Class cable transits through A Class bulkheads as per following tables:
Bulkhead insulated by means of two layers of mineral wool (certified non combustible in compliance to 2010 FTP
Code) 50+40 mm thick and having density of 125 kg/m3
| TYPE OF TRANSITS | Fill | Cable diameter | ADDITIONAL | TRANSIT FIXING |
| % | INSULATION | AND NOTES | ||
| S 8+8x10 | 4 | from 10 up to 86 mm | Mineral wool, two | The penetration is |
| layers, 50+40 mm | fixed to the bulkhead | |||
| thick, having density plate in the middle; the | ||||
| of 125 kg/m3 and | additional insul. is | |||
| width of 200 mm all fitted on the bulkhead | ||||
| around | insulated side. | |||
| S 1x1 EX | 2 | 10 mm | Mineral wool, two | The penetration is |
| SF 8x2 EX | 14 | from 10 up to 86 mm | Mineral wool, two | The penetration is |
No. LAB180318CS /001
Enclosure - Page 2 of 3
Code) 30+30 mm thick and having density of 125 kg/m3
| S 1x1 | 26 | 45 mm | Mineral wool, two | The penetration is |
| layers 30 mm thick fixed to the bulkhead | ||||
| each having density of plate in the middle; the | ||||
| 125 kg/m3 and width | additional insul. is | |||
| of 200 mm all around fitted on the bulkhead | ||||
| insulated side. | ||||
| S 8x1 | 31 | from 21 up to 53 mm | Mineral wool, two | The penetration is |
| S 8+8x3 | 28 | from 21 up to 53 mm | Mineral wool, two | The penetration is |
| and, three layers, on | insulated side. | |||
| the modules fitted | ||||
| with a screw expander | ||||
| SRC r40 8x1 | 31 | from 31 up to 53 mm | Mineral wool, two | The penetration is |
| SR 8x1 | 31 | from 21 up to 53 mm | Mineral wool, two | The penetration is |
| each having density of plate on the exposed | ||||
| 125 kg/m3 and width side; the additional | ||||
| of 200 mm all around insul. is fitted on the | ||||
| bulkhead insulated | ||||
| side. |
Enclosure - Page 3 of 3
Roxtec drawings enclosed in SP Test Report No. 6P02516 dated 29 August 2016 and Research Institute of Marine
Engineering Test Report No. 09-344 dated 11 December 2009.
Tests as per SP Test Report No. 6P02516 dated 29 August 2016 and Research Institute of Marine Engineering Test
Report No. 09-344 dated 11 December 2009 issued according to IMO 2010 FTP Code and IMO Res. A.754 (18).