LAB259217CS-003-optimized
No. LAB259217CS/003
Description Devices for the passage of electric cables and pipes
through A or B Class divisions
Type Roxtec R Series
ROMBVAGEN 2, P.O. BOX 540
SE-37123 KARLSKRONA
Place of manufacture ROMBVAGEN 2, P.O. BOX 540
SE-37123 KARLSKRONA
Issued in Genoa on February 2, 2018. This Certificate is valid until February 7, 2023
No. LAB259217CS/003
Enclosure - Page 1 of 3
Roxtec R S eries
Devices, composed of halogen free material packing system, for the passage of steel pipes having diameter ranging
from 8 up to 54 mm and electric cables having diameter ranging from 10 up to 28 mm through A Class aluminium
bulkheads and decks. The aluminium bulkheads and decks are insulated by means of two layers of mineral wool with
aluminium foil, 30 mm thick each and having density of 130 kg/m3 on the exposed side (decks) and on both sides
(bulkhead). The division insulation covers also the transits that may be fitted with additional insulation as described in
the following tables:
BULKHEADS - PIPE PENETRATION
TYPE OF TRANSITS - PIPE ADDITIONAL INSULATION TRANSIT FIXING AND NOTES
DIAMETER
R70 - pipe diameter 10 mm Mineral wool cylinder, two layers 30 The penetration is fixed to the
mm thick each (compressed to 50 bulkhead plate in the middle; the
mm), having density of 125 kg/m3 additional insulation is fitted on the
and length of 300 mm unexposed side.
R200 - pipe diameter ranging from 10 Mineral wool cylinder, two layers 30 The penetration is fixed to the
mm up to 54 mm mm thick each (compressed to 50 bulkhead plate in the middle; the
DECKS - PIPE PENETRATION
DIAMETER
R70 - pipe diameter 8 mm Mineral wool cylinder with steel net, The penetration may be fixed to the
one layer 50 mm thick, density of 100 deck plate in the middle, exposed or
kg/m3 and length of 400 mm unexposed side; the additional
insulation is fitted on the exposed side.
R200 - pipe diameter ranging from 12 Mineral wool cylinder, two layers 30 The penetration may be fixed to the
mm up to 54 mm mm thick each (compressed to 50 deck plate in the middle, exposed or
mm), having density of 125 kg/m3 unexposed side; the additional
and length of 300 mm insulation is fitted on the exposed side.
No. LAB259217CS /003
Enclosure - Page 2 of 3
BULKHEADS - CABLE TRANSITS
Transit type Minimum fill Maximum fill Cables - Cables - ADDITIONAL TRANSIT
% % Minimum Maximum INSULATION FIXING AND
diameter (mm) diameter (mm) NOTES
R70 4 4 10 10 No additional The penetration
insulation is fixed to the
bulkhead plate
in the middle.
R200 10 10 10 28 No additional The penetration
bulkhead plate
in the middle.
DECKS - CABLE TRANSITS
R50 5 5 10 10 No additional The penetration
deck plate on
unexposed side.
Fire resistant A-60 Class pipe and cable penetrations through load-bearing aluminium bulkheads and decks.
Enclosure - Page 3 of 3
Roxtec drawings enclosed in SP Test Report No. P603001 dated 23 January 2007, DANAK Test Reports No. PG11955
and No. PG11898 dated 17 April 2009 and CTO Test Report No. RS-17/B-210/E dated 2 June 2017.
Tests as per SP Test Report No. P603001 dated 23 January 2007 and DANAK Test Reports No. PG11955 and No.
PG11898 dated 17 April 2009 issued according to IMO Res. A.754 (18) and CTO Test Report No. RS-17/B-210/E
dated 2 June 2017 issued according to 2010 FTP Code.
Genoa 2/02/2018