Certificate No: LR2090258SF-02
| Issue Date: | 15 Mar 2020 |
|---|---|
| Expiry Date: 14 Mar 2025 |
Certificate Of Fire Approval
This is to certify that the product detailed below will be accepted for compliance with the applicable Lloyd’s Register
Rules and Regulations and with the International Convention for the Safety of Life at Sea, (SOLAS), 1974, as
amended, for use on ships and offshore installations classed with Lloyd’s Register, and for use on ships and offshore
installations when authorised by contracting governments to issue the relevant certificates, licences, permits etc.
| Manufacturer | Roxtec International AB |
|---|---|
| Address | Box 540, S-371 23, Karlskrona, Sweden |
| Type | Pipe Penetration (Standard Fire Test) |
| Description | Fire Resisting Plastic Pipe Penetration Seals for A Class Bulkheads and Decks |
| Trade Name | Roxtec Sleev-it Pipe Penetration Seals |
| Specified Standard | IMO Res. MSC.307 (88)-(2010 FTP Code) Annex 1 Part 3 |
IMO Res. MSC.61 (67)- (FTP Code) Annex 1 Part 3
IMO MSC/Circ.1120
IMO Res. MSC.307 (88)-(2010 FTP Code) Section 8
IMO MSC.1/Circ.1488
This certificate is not valid for equipment, the design or manufacture of which has been varied or modified from the
specimen tested. The manufacturer should notify Lloyd’s Register Canada Limited of any modification or changes to
the equipment in order to obtain a valid Certificate.
The Design Appraisal Document and its supplementary Type Approval Terms and Conditions form part of this
Certificate.
This certificate remains valid unless cancelled or revoked, provided the conditions in the attached Design Appraisal
Document are complied with and the equipment remains satisfactory in service.
Bruce McDonald
Fire & Safety Lead Specialist to Lloyd’s
| 237 Brownlow Avenue, Suite 200, Dartmouth, NS. | Register Canada Limited |
|---|---|
| B3B2C7, Canada | A member of the Lloyd’s Register group |
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and
conditions set out in that contract.
TA02 1.0.0
| Page | 2 of 14 |
|---|---|
| Certificate No: | LR2090258SF-02 |
| Issue Date: | 15 Mar 2020 |
| Expiry Date: | 14 Mar 2025 |
| Reference: | UKITSO/FIRE/TA/BM/WP41721157 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2090258SF-02
The undernoted documents have been appraised for compliance with the relevant requirements of International
Conventions, and this Design Appraisal Document forms part of the Certificate.
This Design Appraisal Document forms part of the Certificate.
This Certificate is a renewal and update of SAS F150308/M4
TEST REPORTS
RISE, Research Institute of Sweden, P.O. Box 857, SE-501 15 Boras, Sweden;
5P00771 dated 25th November 2015; 5P00772-1 dated 10th December 2015, 5P08394 dated 2nd March 2016, 5P08395,
dated 17th march 2016; 6P02249 dated 17th August 2017, 7P02024, dated 08th June 2017, 8P04040, dated 13th August
2018, 8P07092 rev 1 dated 16 January 2020,
DGA Techniques Aéronautiques Centre d’Essais Aéronautiques de Toulouse. 47 Rue Saint Jean, BP93123 Balma Cedex
France ;
878/07/A/NP/R 102 dated 19th February 2008, 881/07/A/NP/R-102, 881/07/A dated 19th February 2008
Warrington Fire, Holmesfield Road, Warrington, Cheshire WA1 2DS, UK;
164476/A dated 23rd July 2007, 170080A dated 30th April 2008, 170080B dated 30th April 2008, 175486A dated 31st October
2008, , 177105A dated 6th January 2009, 180251A, dated 26th May 2009, 1883387A, dated 23rd October 2009, 1883387B,
dated 23rd October 2009, 184391A dated 17th December 2009, 190890A dated, 28th May 2010, 198004A, dated 7th December
2010, 303584A dated 7th April 2011, 303585 dated 17th February 2011, 207171A dated 17th June 2011, 309638A dated 20th
September 2011, 309855A dated 5th October 2011, 313700 dated 20th January 2012, 314669 dated 19th January 2011,
314670 dated 25th June 2012, 316943 dated 25th June 2012, 320402A dated 29th October 2012, 324083 dated 27th
November 2012, 325332 dated 14th January 2013, 327509 dated 10th July 2013, 329449 dated 13th August 2013, 330891
dated 5th September 2013, 330891 dated 3rd July 2013, 334429 dated 17th December 2013, 337717 dated 13th May 2014
BRE, Bucknall’s lane Garston, Watford Hertfordshire, UK;
223968 dated 5th September 2006, 223969A dated 15th September 2006
Danish Institution of Fire and Security Technology, Jemholmen 12, DK-2650 Hvidovre Denmark;
PGA10801A dated 29th August 2016, PGA10870A dated 13th December 2016, PGA 11388A dated 14th August 2019,
PGA11611A 11 January 2020,
Centrum Techniki Okretowej S.A, 65 Szczecinska, 80-392 Gdasnk, Poland;
RS-19/B-356/E dated 18th October 2019, RS-19/B-424/E, dated 27th November 2019, RS-18/B-265/E, dated 17th September
2018, RS-18/B-423/E dated 19th November 2011, RS-20/B-081/E dated 31st March 2020.
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and conditions
set out in that contract.
| Page | 3 of 14 |
|---|---|
| Certificate No: | LR2090258SF-02 |
| Issue Date: | 15 Mar 2020 |
| Expiry Date: | 14 Mar 2025 |
| Reference: | UKITSO/FIRE/TA/BM/WP41721157 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2090258SF-02
APPROVAL DOCUMENTATION
Lloyds Register witness statement on pressure testing
DNV witness statement on pressure testing LDN-08-045 dated 9th May 2008
CONDITIONS OF CERTIFICATION
| 1. | Production items are to be manufactured in accordance with a quality control system which shall be maintained |
|---|---|
| to ensure that items are of the same standard as the approved prototype | |
| 2. | The certificate holder is solely responsible for the products supplied under this Certificate and to ensure that their |
| — | — |
| products, whether manufactured by themselves or their licensee manufacturers, if agreed by Lloyd’s Register, are | |
| fully compliant with the relevant statutory regulations and Lloyd’s Register Class rules as applicable and designed, | |
| manufactured and installed to the same quality and specifications as the prototype tested, including components | |
| that are designed and manufactured by third parties | |
| 3. | The penetration system is a steel collar which is welded (fully or tack welded) or bolted and fits around plastic |
| — | — |
| pipes, the collar contains intumescent material which activates upon exposure to heat. The intumescent material | |
| closes the plastic pipe providing a fire-resistant seal. A layer of Sleev-it marine fire rated sealant or equivalent can | |
| be installed to fill the annular gap between the collar and the pipe. | |
| 4. | Tables below give penetration details for inclusion in A-0 and A60 steel bulkheads and decks |
| — | — |
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and conditions
set out in that contract.
| Page | 4 of 14 |
|---|---|
| Certificate No: | LR2090258SF-02 |
| Issue Date: | 15 Mar 2020 |
| Expiry Date: | 14 Mar 2025 |
| Reference: | UKITSO/FIRE/TA/BM/WP41721157 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2090258SF-02
Steel Bulkheads A-60
| Pipe Material | Max | Collar | Insulation Details for A-60 | Drawing |
|---|---|---|---|---|
| Pipe O.D. range | Installation | Reference | ||
| (mm) | Side |
| ABS | 114mm | Insulated or non- | No additional | insulation | S1557740 |
| insulated | required |
| PB | 16mm-160mm | Insulated or non- | No additional | insulation | S1557766 |
| insulated | required |
| PE/HDPE | 50mm-225mm | Insulated or non- | No additional | insulation | S1559656 |
| insulated | required |
| 226mm-315mm | Insulated or non- | An additional 200mm ring of | S1559656 |
| insulated | A60 insulation is to be |
installed around the collar or
the pipe : see insulation
drawing
| PP/PPR/PPML/PPFR | 32mm-200mm | Insulated or non- | No additional | insulation | S1560085 |
|---|---|---|---|---|---|
| insulated | required | ||||
| PVC | 12mm-200mm | Insulated or non- | No additional | insulation | S1560092 |
| (inc uPVC & cPVC) | insulated | required | |||
| 201mm-225mm | Insulated | side | No additional | insulation | S1560092 |
| only | required | ||||
| 226mm-270mm | Insulated | side | Additional | insulation | S1560308 |
| only | required to cover longer | ||||
| length of seal when installed | |||||
| on the insulated side - See | |||||
| Note 5 and insulation | |||||
| drawing | |||||
| 271mm-322mm | Insulated or non- | Additional | insulation | S1560308 | |
| — | — | — | — | — | |
| insulated | required to cover longer | ||||
| length of seal when installed | |||||
| on the insulated side - See | |||||
| Note 5 and insulation | |||||
| drawing |
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and conditions
set out in that contract.
| Page | 5 of 14 |
|---|---|
| Certificate No: | LR2090258SF-02 |
| Issue Date: | 15 Mar 2020 |
| Expiry Date: | 14 Mar 2025 |
| Reference: | UKITSO/FIRE/TA/BM/WP41721157 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2090258SF-02
Steel Bulkheads A-60 (cont.)
| PVDF | 169mm | Insulated or non- | No additional | insulation | S1560129 |
|---|---|---|---|---|---|
| insulated | required | ||||
| PE-AL-PE | 16mm-32mm | Insulated or non- | No additional | insulation | S1560134 |
| (multi-layer pipe | insulated | required | |||
| which may or may | |||||
| 33mm-63mm | Insulated or non- | Additional | insulation | S1560134 | |
| — | — | — | — | — | |
| not be insulated | |||||
| insulated | required along length of pipe | ||||
| — | — | ||||
| with an insulation | |||||
| : see insulation drawing |
jacket)
| Beverage multi-pipe | 75mm-99mm | Insulated | side | No additional | insulation | S1560148 |
|---|---|---|---|---|---|---|
| (with | outer | only | required | |||
| insulated | jacket | |||||
| 100mm | Insulated or non- | No additional | insulation | S1560148 | ||
| passing through fire | ||||||
| insulated | required | |||||
| — | — | |||||
| collar/seal) | ||||||
| Preinsulated Pipes | 75mm-315mm | non-insulated | Additional wrap of A-60 rated | S1559819 | ||
| — | — | — | — | — | ||
| (Outer | Diameter | side only | insulation around the pipe on | |||
| including | the insulated side. Complete | |||||
| outershell/jacket) | length of insulation from the | |||||
| structure to equal 300mm : | ||||||
| see insulation drawing |
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and conditions
set out in that contract.
| Page | 6 of 14 |
|---|---|
| Certificate No: | LR2090258SF-02 |
| Issue Date: | 15 Mar 2020 |
| Expiry Date: | 14 Mar 2025 |
| Reference: | UKITSO/FIRE/TA/BM/WP41721157 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2090258SF-02
Steel Decks A-60
| Pipe Material | Max | Collar | Insulation Details for A-60 | Drawing |
|---|---|---|---|---|
| Pipe O.D. range | Installation | Reference | ||
| (mm) | Side |
| ABS | 110mm-219mm | Underside | No | additional | insulation | S1557740 |
required
| PB | 16mm-125mm | Topside | No | additional | insulation | S1557766 |
|---|---|---|---|---|---|---|
| required | ||||||
| 125mm-225mm | Underside | No | additional | insulation | S1557766 | |
| — | — | — | — | — | — | |
| or topside | required | |||||
| PE/HDPE | 25mm-225mm | Underside | No | additional | insulation | S1559656 |
| or topside | required | |||||
| 226mm-320mm | Underside | Additional insulation required to | S1561005 | |||
| cover longer length of seal when | ||||||
| installed on the insulated side - | ||||||
| See Note 5 and insulation | ||||||
| drawing | ||||||
| PP/PPR/PPML/PPFR | 16mm-110mm | Underside | No | additional | insulation | S1560085 |
| — | — | — | — | — | — | — |
| or topside | required | |||||
| 111mm-225mm | Underside | No | additional | insulation | S1560085 | |
| required | ||||||
| 226mm-320mm | Underside | Additional insulation required to | S1561005 | |||
| — | — | — | — | |||
| cover longer length of seal when | ||||||
| installed on the insulated side - | ||||||
| See Note 5 and insulation | ||||||
| drawing | ||||||
| PVC | 21mm-225mm | Underside | No | additional | insulation | S1560122 |
| — | — | — | — | — | — | — |
| (inc uPVC & cPVC) | or topside | required | ||||
| 226mm-321mm | Underside | Additional insulation required to | S1561005 | |||
| or topside | cover longer length of seal when | |||||
| installed on the insulated side - | ||||||
| See Note 5 and insulation | ||||||
| drawing |
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and conditions
set out in that contract.
| Page | 7 of 14 |
|---|---|
| Certificate No: | LR2090258SF-02 |
| Issue Date: | 15 Mar 2020 |
| Expiry Date: | 14 Mar 2025 |
| Reference: | UKITSO/FIRE/TA/BM/WP41721157 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2090258SF-02
Steel Decks A-60 (cont.)
| PVDF | 40mm-169mm | Underside | No | additional | insulation | S1560129 |
|---|---|---|---|---|---|---|
| or topside | required | |||||
| PE-AL-PE | 16mm-63mm | Underside | No | additional | insulation | S1560134 |
| (multi-layer pipe | or topside | required | ||||
| which may or may |
not be insulated
with an insulation
jacket)
| Beverage multi-pipe | 75mm-100mm | Underside | No | additional | insulation | S1560148 |
|---|---|---|---|---|---|---|
| (with | outer | or topside | required | |||
| insulated | jacket | |||||
| passing through fire |
collar/seal)
| Preinsulated Pipes | 75mm-315mm | Underside | Two additional 100mm rings of | S1559819 |
|---|---|---|---|---|
| (Outer | Diameter | A60 insulation are to be installed | ||
| including | around the collar and/or pipe : | |||
| outershell/jacket) | see insulation drawing |
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and conditions
set out in that contract.
| Page | 8 of 14 |
|---|---|
| Certificate No: | LR2090258SF-02 |
| Issue Date: | 15 Mar 2020 |
| Expiry Date: | 14 Mar 2025 |
| Reference: | UKITSO/FIRE/TA/BM/WP41721157 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2090258SF-02
Steel Bulkheads A-0
| Pipe Material | Max | Collar | Insulation Details for A-0 | Drawing |
|---|---|---|---|---|
| Pipe O.D. range | Installation | Reference | ||
| (mm) | Side |
| ABS | 114mm | Either | An additional 200mm ring | S1557740 |
of A60 insulation is to be
installed around the collar
or the pipe
| PB | 16mm-125mm | Either | No additional insulation | S1557766 |
|---|---|---|---|---|
| required | ||||
| 126mm-160mm | Either | An additional 200mm ring | S1557766 | |
| — | — | — | — | |
| of A60 insulation is to be | ||||
| installed around the collar | ||||
| or the pipe | ||||
| PE/HDPE | 50mm-225mm | Either | An additional 200mm ring | S1559656 |
| — | — | — | — | — |
| of A60 insulation is to be | ||||
| installed around the collar | ||||
| or the pipe | ||||
| 226mm-315mm | Either | Additional | insulation | S1560308 |
| — | — | — | — | — |
| required to cover longer | ||||
| length of seal when | ||||
| installed on the insulated | ||||
| side - See Note 5 and | ||||
| insulation drawing | ||||
| PP/PPR/PPML/PPFR | 20mm-169mm | Either | No additional insulation | S1560085 |
| — | — | — | — | — |
| required | ||||
| 170mm-200mm | Either | An additional 200mm ring | S1560085 | |
| — | — | — | — | |
| of A60 insulation is to be | ||||
| installed around the collar | ||||
| or the pipe |
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and conditions
set out in that contract.
| Page | 9 of 14 |
|---|---|
| Certificate No: | LR2090258SF-02 |
| Issue Date: | 15 Mar 2020 |
| Expiry Date: | 14 Mar 2025 |
| Reference: | UKITSO/FIRE/TA/BM/WP41721157 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2090258SF-02
Steel Bulkheads A-0
| PVC | 12mm-160mm | Either | No additional insulation | S1560092 |
|---|---|---|---|---|
| (inc uPVC & cPVC) | required | |||
| 161mm-225mm | Either | An additional 200mm ring | S1560092 | |
| of A60 insulation is to be | ||||
| installed around the collar | ||||
| or the pipe | ||||
| 226mm-322mm | Either | Additional | insulation | S1560308 |
| — | — | — | — | — |
| required to cover longer | ||||
| length of seal when | ||||
| installed on the insulated | ||||
| side - See Note 5 and | ||||
| insulation drawing | ||||
| PVDF | 169mm | Either | An additional 200mm ring | S1560129 |
| — | — | — | — | — |
| of A60 insulation is to be | ||||
| installed around the collar | ||||
| or the pipe | ||||
| PE-AL-PE | 16mm-63mm | Either | No additional insulation | S1560134 |
| — | — | — | — | — |
| (multi-layer pipe | required | |||
| which may or may |
not be insulated
with an insulation
jacket)
| Beverage multi-pipe | 75mm-100mm | Either | An additional 200mm ring | S1560148 |
|---|---|---|---|---|
| (with | outer | of A60 insulation is to be | ||
| insulated | jacket | installed around the collar | ||
| passing through fire | or the pipe | |||
| collar/seal) | ||||
| Preinsulated Pipes | 75mm-315mm | Collar | to | be |
| — | — | — | — | — |
| (Outer | Diameter | placed on the | of A60 insulation is to be | |
| including | high fire risk side | installed around the pipe | ||
| outershell/jacket) | plus an additional wrap of | |||
| A-60 rated insulation | ||||
| around the pipe on the | ||||
| insulated side. Complete | ||||
| length of insulation from | ||||
| the structure to equal | ||||
| 300mm : see insulation | ||||
| drawing |
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and conditions
set out in that contract.
| Page | 10 of 14 |
|---|---|
| Certificate No: | LR2090258SF-02 |
| Issue Date: | 15 Mar 2020 |
| Expiry Date: | 14 Mar 2025 |
| Reference: | UKITSO/FIRE/TA/BM/WP41721157 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2090258SF-02
Steel Decks A-0
| Pipe Material | Max | Collar | Insulation Details for A-0 | Drawing |
|---|---|---|---|---|
| Pipe O.D. range | Installation | Reference | ||
| (mm) | Side |
| ABS | 110mm-219mm | Underside | An additional 200mm ring of | S1557740 |
A60 insulation is to be installed
around the collar
| PB | 16mm-124mm | Topside | An additional 200mm ring of | S1557766 |
|---|---|---|---|---|
| A60 insulation is to be installed | ||||
| around the pipe | ||||
| 125mm-225mm | Underside | or | An additional 200mm ring of | S1557766 |
| — | — | — | — | — |
| topside | A60 insulation is to be installed | |||
| around the collar or pipe on the | ||||
| insulated side | ||||
| PE/HDPE | 25mm-225mm | Underside | or | An additional 200mm ring of |
| — | — | — | — | — |
| topside | A60 insulation is to be installed | |||
| around the collar or pipe on the | ||||
| insulated side | ||||
| 226mm-320mm | Underside | Additional insulation required | S1561005 | |
| — | — | — | — | |
| to cover longer length of seal | ||||
| when installed on the insulated | ||||
| side - See Note 5 and insulation | ||||
| drawing |
| PP/PPR/PPML/PPFR | 16mm-110mm | Underside | or | An additional 200mm ring of | S1560085 |
|---|---|---|---|---|---|
| topside | A60 insulation is to be installed | ||||
| around the collar or pipe on the | |||||
| insulated side | |||||
| 111mm-225mm | Underside | An additional 200mm ring of | S1560085 | ||
| — | — | — | — | ||
| A60 insulation is to be installed | |||||
| around the collar | |||||
| 226mm-320mm | Underside | Additional insulation required | S1561005 | ||
| — | — | — | — | ||
| to cover longer length of seal | |||||
| when installed on the insulated | |||||
| side - See Note 5 and insulation | |||||
| drawing |
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and conditions
set out in that contract.
| Page | 11 of 14 |
|---|---|
| Certificate No: | LR2090258SF-02 |
| Issue Date: | 15 Mar 2020 |
| Expiry Date: | 14 Mar 2025 |
| Reference: | UKITSO/FIRE/TA/BM/WP41721157 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2090258SF-02
Steel Decks A-0 (Cont)
| PVC | 16mm-50mm | Underside | or | No | additional | insulation | S1560122 |
|---|---|---|---|---|---|---|---|
| (inc uPVC & cPVC) | topside | required | |||||
| 51mm-225mm | Underside | or | An additional 200mm ring of | S1560122 | |||
| topside | A60 insulation is to be installed | ||||||
| around the collar or pipe on the | |||||||
| insulated side | |||||||
| 226mm-321mm | Underside | or | Additional insulation required | S1561005 | |||
| — | — | — | — | — | |||
| topside | to cover longer length of seal | ||||||
| when installed on the insulated | |||||||
| side - See Note 5 and insulation | |||||||
| drawing | |||||||
| PVDF | 40mm-169mm | Underside | or | An additional 200mm ring of | S1560129 | ||
| — | — | — | — | — | — | ||
| topside | A60 insulation is to be installed | ||||||
| around the collar or pipe on the | |||||||
| insulated side | |||||||
| PE-AL-PE | 16mm-31mm | Underside | An additional 200mm ring of | S1560134 | |||
| — | — | — | — | — | |||
| (multi-layer pipe | A60 insulation is to be installed | ||||||
| which may or may | around the collar on the | ||||||
| not be insulated | insulated side | ||||||
| with an insulation | |||||||
| 16mm-31mm | Topside | No | additional | insulation | S1560134 | ||
| — | — | — | — | — | — | ||
| jacket) | |||||||
| required | |||||||
| 32mm-63mm | Underside | or | No | additional | insulation | S1560134 | |
| — | — | — | — | — | — | — | |
| topside | required | ||||||
| Beverage multi-pipe | 75mm-100mm | Underside | or | An additional 200mm ring of | S1560148 | ||
| (with | outer | topside | A60 insulation is to be installed | ||||
| insulated | jacket | around the collar or pipe on the | |||||
| passing through fire | insulated side | ||||||
| collar/seal) | |||||||
| Preinsulated Pipes | 75mm-315mm | Underside | A 200mm ring of A60 insulation | S1560316 | |||
| — | — | — | — | — | |||
| (Outer | Diameter | is to be installed around the | |||||
| including | collar/seal plus two additional | ||||||
| outershell/jacket) | 100mm rings of A60 insulation | ||||||
| around the collar and/or pipe : | |||||||
| see insulation drawing |
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and conditions
set out in that contract.
| Page | 12 of 14 |
|---|---|
| Certificate No: | LR2090258SF-02 |
| Issue Date: | 15 Mar 2020 |
| Expiry Date: | 14 Mar 2025 |
| Reference: | UKITSO/FIRE/TA/BM/WP41721157 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2090258SF-02
| 5. | When installed from the insulated side and when insulation is required (per the insulation drawing), the full length |
|---|---|
| of the Fire Collar (seal) should be fully insulated. Should extra insulation be required, it should either be a 200mm | |
| ring of A-60 rated insulation fitted around the seal, or an A-60 rated insulation wrap around the Fire Collar. Please | |
| see applicable insulation drawing reference in the tables | |
| 6. | Two pipes; 160mm dia. PB and 16mm uPVC fitted with Sleev-it pipe penetrations and Sleev-it marine fire rated |
| — | — |
| sealant or equivalent, were subjected to a hydrostatic test and an air pressure test of 1 bar and 0.02 bar respectively | |
| and no leakage was reported after 30 minutes, as detailed in the DNV Test Report No.LDN-08-045 dated 31 January |
- In all cases, the sealant was applied to seal the penetration on both sides of the penetration and the test
pressures were applied from either side
| 7. | Two pipes; 110mm dia. uPVC and 16mm PE fitted with Sleev-it pipe penetrations, type: “Sleev-it WT” comprising |
|---|---|
| Sleev-it EPDM rubber seals, type: “SLV EDPM Grommet”, were subjected to a hydrostatic test and an air pressure | |
| test at 3.5 bar and 1 bar respectively and no leakage was reported after 30 minutes, as detailed in Lloyd’s Register | |
| Test Witness Certificate No: SOU 0901586/1 dated 08 January 2010. The “Sleev-it WT” may be fitted on any one |
side of the division
| 8. | The above penetration systems are not to be used for penetrating tank boundaries |
|---|
| 9. | When requested to be used in watertight bulkheads on passenger ships and Special Purpose Ships (SPS), the above |
penetration systems should be verified for compliance with the requirements given in SOLAS Chapter II-1 Reg.13.2.3
(2009 issue). The above penetration systems have not been approved according to this paragraph
-
All sleev-it collars are suitable for protection of B-15 penetrations.
-
A modified arrangement of the Roxtec Sleev-it pipe penetration called the “Roxtec Sleev-it Transition Collar” may
be used to protect a plastic pipe transition / connection to a steel pipe. The Roxtec Sleev-it Transition collar is
secured to the steel pipe using a Sleev-it Rising Clamp. The tables below detail both the horizontal installation
when plastic pipe is transitioned to a steel pipe in close proximity to a steel bulkhead and also, deck installations
when attached to a steel Scupper / Collecting / Drainage Pot as detailed within the applicable insulation drawings
referenced within the tables
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and conditions
set out in that contract.
| Page | 13 of 14 |
|---|---|
| Certificate No: | LR2090258SF-02 |
| Issue Date: | 15 Mar 2020 |
| Expiry Date: | 14 Mar 2025 |
| Reference: | UKITSO/FIRE/TA/BM/WP41721157 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2090258SF-02
Steel Bulkheads A-60
| Max | Collar |
|---|---|
| Pipe Material | Pipe O.D. range |
| (mm) | Side |
Transition Collar and steel pipe up to the bulkhead
| Insulated side | S1560502 |
|---|---|
| insulation to be fully wrapped in A-60 insulation. | |
| Steel pipe to plastic pipe transition - installed |
50-75mm (steel) to
| PP/PPR/PPML/PPFR | less than 450mm away from a bulkhead |
|---|---|
| 50-90mm (plastic) | |
| penetration | |
| Steel pipe on the insulated side to be fully wrapped | |
| Non-insulated side | S1560502 |
| — | — |
| in A-60 insulation for a distance of 450mm mm. |
Steel Decks A-60
| Pipe O.D. - Steel Pipe | Collar |
|---|---|
| Pipe Material | to Plastic Pipe |
| (mm) | Side |
Steel pipe to plastic pipe transition where
steel pipe forms part of or connects to a
Scupper Pot to be fully insulated with A-60
| 50-90mm (steel) to | stainless steel Scupper / Collecting / |
|---|---|
| PP/PPR/PPML/PPFR | Underside |
| 50-90mm (plastic) | Drainage Pot (with or without "drainage |
| Transition Collar | |
| bell") - Both horizontal (elbow) and vertical | |
| (straight) connections |
Steel Decks A-0
| Pipe O.D. - Steel Pipe | Collar |
|---|---|
| Pipe Material | to Plastic Pipe |
| (mm) | Side |
Steel pipe to plastic pipe transition where
steel pipe forms part of or connects to a
Scupper Pot to be fully insulated with A-60 rated
| 50-90mm (steel) to | stainless steel Scupper / Collecting / |
|---|---|
| PP/PPR/PPML/PPFR | Underside |
| 50-90mm (plastic) | Drainage Pot (with or without "drainage |
| Transition Collar | |
| bell") - Both horizontal (elbow) and vertical | |
| (straight) connections |
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and conditions
set out in that contract.
| Page | 14 of 14 |
|---|---|
| Certificate No: | LR2090258SF-02 |
| Issue Date: | 15 Mar 2020 |
| Expiry Date: | 14 Mar 2025 |
| Reference: | UKITSO/FIRE/TA/BM/WP41721157 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2090258SF-02
| 1. | Approved Installation Variations for Sleev-it penetrations are given below; |
|---|
a) Drawing S1528866 Revision (A) and associated Amendment to Installation Instructions Roxtec Sleev-it Fire
Penetration Seal ASS2012001301 (DOC-001830 Rev A).
b) Drawing S1538623 Revision (A) - PVC insert sleeve.
c) Drawing S1036168 Revision (B) - Sleev-it WT Deck Penetration (Wavin SI Tech PPr pipe). Design variation
referenced by Information Drawing S1029962 revision (A)
PLACE OF PRODUCTION
Roxtec International AB
Box 540
S-371 23 Karlskrona
Sweden
Bruce McDonald
Lead Fire and Safety Specialist
Lloyd’s Register Americas
Supplementary Type Approval Terms and Conditions
This certificate and Design Appraisal Document relates to type approval, it certifies that the prototype(s) of the product(s)
referred to herein has/have been found to meet the applicable design criteria for the use specified herein, it does not mean
or imply approval for any other use, nor approval of any products designed or manufactured otherwise than in strict
conformity with the said prototype(s).
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and conditions