LR2090258SF-02 - CERT&DAD_signed-optimized

Certificate No: LR2090258SF-02

Issue Date: 15 Mar 2020
Expiry Date: 14 Mar 2025

Certificate Of Fire Approval

This is to certify that the product detailed below will be accepted for compliance with the applicable Lloyd’s Register
Rules and Regulations and with the International Convention for the Safety of Life at Sea, (SOLAS), 1974, as
amended, for use on ships and offshore installations classed with Lloyd’s Register, and for use on ships and offshore
installations when authorised by contracting governments to issue the relevant certificates, licences, permits etc.

Manufacturer Roxtec International AB
Address Box 540, S-371 23, Karlskrona, Sweden

| Type | Pipe Penetration (Standard Fire Test) |

| Description | Fire Resisting Plastic Pipe Penetration Seals for A Class Bulkheads and Decks |

| Trade Name | Roxtec Sleev-it Pipe Penetration Seals |

| Specified Standard | IMO Res. MSC.307 (88)-(2010 FTP Code) Annex 1 Part 3 |
IMO Res. MSC.61 (67)- (FTP Code) Annex 1 Part 3
IMO MSC/Circ.1120
IMO Res. MSC.307 (88)-(2010 FTP Code) Section 8
IMO MSC.1/Circ.1488

This certificate is not valid for equipment, the design or manufacture of which has been varied or modified from the
specimen tested. The manufacturer should notify Lloyd’s Register Canada Limited of any modification or changes to

the equipment in order to obtain a valid Certificate.

The Design Appraisal Document and its supplementary Type Approval Terms and Conditions form part of this

Certificate.

This certificate remains valid unless cancelled or revoked, provided the conditions in the attached Design Appraisal
Document are complied with and the equipment remains satisfactory in service.

Bruce McDonald
Fire & Safety Lead Specialist to Lloyd’s

237 Brownlow Avenue, Suite 200, Dartmouth, NS. Register Canada Limited
B3B2C7, Canada A member of the Lloyd’s Register group

Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and

conditions set out in that contract.

TA02 1.0.0

Page 2 of 14
Certificate No: LR2090258SF-02
Issue Date: 15 Mar 2020
Expiry Date: 14 Mar 2025
Reference: UKITSO/FIRE/TA/BM/WP41721157

ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2090258SF-02

The undernoted documents have been appraised for compliance with the relevant requirements of International
Conventions, and this Design Appraisal Document forms part of the Certificate.

This Design Appraisal Document forms part of the Certificate.

This Certificate is a renewal and update of SAS F150308/M4

TEST REPORTS

RISE, Research Institute of Sweden, P.O. Box 857, SE-501 15 Boras, Sweden;
5P00771 dated 25th November 2015; 5P00772-1 dated 10th December 2015, 5P08394 dated 2nd March 2016, 5P08395,
dated 17th march 2016; 6P02249 dated 17th August 2017, 7P02024, dated 08th June 2017, 8P04040, dated 13th August

2018, 8P07092 rev 1 dated 16 January 2020,

DGA Techniques Aéronautiques Centre d’Essais Aéronautiques de Toulouse. 47 Rue Saint Jean, BP93123 Balma Cedex

France ;

878/07/A/NP/R 102 dated 19th February 2008, 881/07/A/NP/R-102, 881/07/A dated 19th February 2008
Warrington Fire, Holmesfield Road, Warrington, Cheshire WA1 2DS, UK;
164476/A dated 23rd July 2007, 170080A dated 30th April 2008, 170080B dated 30th April 2008, 175486A dated 31st October
2008, , 177105A dated 6th January 2009, 180251A, dated 26th May 2009, 1883387A, dated 23rd October 2009, 1883387B,
dated 23rd October 2009, 184391A dated 17th December 2009, 190890A dated, 28th May 2010, 198004A, dated 7th December
2010, 303584A dated 7th April 2011, 303585 dated 17th February 2011, 207171A dated 17th June 2011, 309638A dated 20th
September 2011, 309855A dated 5th October 2011, 313700 dated 20th January 2012, 314669 dated 19th January 2011,
314670 dated 25th June 2012, 316943 dated 25th June 2012, 320402A dated 29th October 2012, 324083 dated 27th
November 2012, 325332 dated 14th January 2013, 327509 dated 10th July 2013, 329449 dated 13th August 2013, 330891
dated 5th September 2013, 330891 dated 3rd July 2013, 334429 dated 17th December 2013, 337717 dated 13th May 2014

BRE, Bucknall’s lane Garston, Watford Hertfordshire, UK;

223968 dated 5th September 2006, 223969A dated 15th September 2006
Danish Institution of Fire and Security Technology, Jemholmen 12, DK-2650 Hvidovre Denmark;
PGA10801A dated 29th August 2016, PGA10870A dated 13th December 2016, PGA 11388A dated 14th August 2019,

PGA11611A 11 January 2020,

Centrum Techniki Okretowej S.A, 65 Szczecinska, 80-392 Gdasnk, Poland;
RS-19/B-356/E dated 18th October 2019, RS-19/B-424/E, dated 27th November 2019, RS-18/B-265/E, dated 17th September
2018, RS-18/B-423/E dated 19th November 2011, RS-20/B-081/E dated 31st March 2020.

Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and conditions

set out in that contract.

Page 3 of 14
Certificate No: LR2090258SF-02
Issue Date: 15 Mar 2020
Expiry Date: 14 Mar 2025
Reference: UKITSO/FIRE/TA/BM/WP41721157

ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2090258SF-02

APPROVAL DOCUMENTATION

Lloyds Register witness statement on pressure testing

DNV witness statement on pressure testing LDN-08-045 dated 9th May 2008

CONDITIONS OF CERTIFICATION

1. Production items are to be manufactured in accordance with a quality control system which shall be maintained
to ensure that items are of the same standard as the approved prototype
2. The certificate holder is solely responsible for the products supplied under this Certificate and to ensure that their
products, whether manufactured by themselves or their licensee manufacturers, if agreed by Lloyd’s Register, are
fully compliant with the relevant statutory regulations and Lloyd’s Register Class rules as applicable and designed,
manufactured and installed to the same quality and specifications as the prototype tested, including components
that are designed and manufactured by third parties
3. The penetration system is a steel collar which is welded (fully or tack welded) or bolted and fits around plastic
pipes, the collar contains intumescent material which activates upon exposure to heat. The intumescent material
closes the plastic pipe providing a fire-resistant seal. A layer of Sleev-it marine fire rated sealant or equivalent can
be installed to fill the annular gap between the collar and the pipe.
4. Tables below give penetration details for inclusion in A-0 and A60 steel bulkheads and decks

Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and conditions

set out in that contract.

Page 4 of 14
Certificate No: LR2090258SF-02
Issue Date: 15 Mar 2020
Expiry Date: 14 Mar 2025
Reference: UKITSO/FIRE/TA/BM/WP41721157

ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2090258SF-02

Steel Bulkheads A-60

Pipe Material Max Collar Insulation Details for A-60 Drawing
Pipe O.D. range Installation Reference
(mm) Side

| ABS | 114mm | Insulated or non- | No additional | insulation | S1557740 |
| insulated | required |
| PB | 16mm-160mm | Insulated or non- | No additional | insulation | S1557766 |
| insulated | required |
| PE/HDPE | 50mm-225mm | Insulated or non- | No additional | insulation | S1559656 |
| insulated | required |
| 226mm-315mm | Insulated or non- | An additional 200mm ring of | S1559656 |
| insulated | A60 insulation is to be |
installed around the collar or
the pipe : see insulation
drawing

PP/PPR/PPML/PPFR 32mm-200mm Insulated or non- No additional insulation S1560085
insulated required
PVC 12mm-200mm Insulated or non- No additional insulation S1560092
(inc uPVC & cPVC) insulated required
201mm-225mm Insulated side No additional insulation S1560092
only required
226mm-270mm Insulated side Additional insulation S1560308
only required to cover longer
length of seal when installed
on the insulated side - See
Note 5 and insulation
drawing
271mm-322mm Insulated or non- Additional insulation S1560308
insulated required to cover longer
length of seal when installed
on the insulated side - See
Note 5 and insulation
drawing

Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and conditions

set out in that contract.

Page 5 of 14
Certificate No: LR2090258SF-02
Issue Date: 15 Mar 2020
Expiry Date: 14 Mar 2025
Reference: UKITSO/FIRE/TA/BM/WP41721157

ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2090258SF-02

Steel Bulkheads A-60 (cont.)

PVDF 169mm Insulated or non- No additional insulation S1560129
insulated required
PE-AL-PE 16mm-32mm Insulated or non- No additional insulation S1560134
(multi-layer pipe insulated required
which may or may
33mm-63mm Insulated or non- Additional insulation S1560134
not be insulated
insulated required along length of pipe
with an insulation
: see insulation drawing

jacket)

Beverage multi-pipe 75mm-99mm Insulated side No additional insulation S1560148
(with outer only required
insulated jacket
100mm Insulated or non- No additional insulation S1560148
passing through fire
insulated required
collar/seal)
Preinsulated Pipes 75mm-315mm non-insulated Additional wrap of A-60 rated S1559819
(Outer Diameter side only insulation around the pipe on
including the insulated side. Complete
outershell/jacket) length of insulation from the
structure to equal 300mm :
see insulation drawing

Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and conditions

set out in that contract.

Page 6 of 14
Certificate No: LR2090258SF-02
Issue Date: 15 Mar 2020
Expiry Date: 14 Mar 2025
Reference: UKITSO/FIRE/TA/BM/WP41721157

ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2090258SF-02

Steel Decks A-60

Pipe Material Max Collar Insulation Details for A-60 Drawing
Pipe O.D. range Installation Reference
(mm) Side

| ABS | 110mm-219mm | Underside | No | additional | insulation | S1557740 |
required

PB 16mm-125mm Topside No additional insulation S1557766
required
125mm-225mm Underside No additional insulation S1557766
or topside required
PE/HDPE 25mm-225mm Underside No additional insulation S1559656
or topside required
226mm-320mm Underside Additional insulation required to S1561005
cover longer length of seal when
installed on the insulated side -
See Note 5 and insulation
drawing
PP/PPR/PPML/PPFR 16mm-110mm Underside No additional insulation S1560085
or topside required
111mm-225mm Underside No additional insulation S1560085
required
226mm-320mm Underside Additional insulation required to S1561005
cover longer length of seal when
installed on the insulated side -
See Note 5 and insulation
drawing
PVC 21mm-225mm Underside No additional insulation S1560122
(inc uPVC & cPVC) or topside required
226mm-321mm Underside Additional insulation required to S1561005
or topside cover longer length of seal when
installed on the insulated side -
See Note 5 and insulation
drawing

Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and conditions

set out in that contract.

Page 7 of 14
Certificate No: LR2090258SF-02
Issue Date: 15 Mar 2020
Expiry Date: 14 Mar 2025
Reference: UKITSO/FIRE/TA/BM/WP41721157

ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2090258SF-02

Steel Decks A-60 (cont.)

PVDF 40mm-169mm Underside No additional insulation S1560129
or topside required
PE-AL-PE 16mm-63mm Underside No additional insulation S1560134
(multi-layer pipe or topside required
which may or may

not be insulated

with an insulation

jacket)

Beverage multi-pipe 75mm-100mm Underside No additional insulation S1560148
(with outer or topside required
insulated jacket
passing through fire

collar/seal)

Preinsulated Pipes 75mm-315mm Underside Two additional 100mm rings of S1559819
(Outer Diameter A60 insulation are to be installed
including around the collar and/or pipe :
outershell/jacket) see insulation drawing

Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and conditions

set out in that contract.

Page 8 of 14
Certificate No: LR2090258SF-02
Issue Date: 15 Mar 2020
Expiry Date: 14 Mar 2025
Reference: UKITSO/FIRE/TA/BM/WP41721157

ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2090258SF-02

Steel Bulkheads A-0

Pipe Material Max Collar Insulation Details for A-0 Drawing
Pipe O.D. range Installation Reference
(mm) Side

| ABS | 114mm | Either | An additional 200mm ring | S1557740 |
of A60 insulation is to be
installed around the collar
or the pipe

PB 16mm-125mm Either No additional insulation S1557766
required
126mm-160mm Either An additional 200mm ring S1557766
of A60 insulation is to be
installed around the collar
or the pipe
PE/HDPE 50mm-225mm Either An additional 200mm ring S1559656
of A60 insulation is to be
installed around the collar
or the pipe
226mm-315mm Either Additional insulation S1560308
required to cover longer
length of seal when
installed on the insulated
side - See Note 5 and
insulation drawing
PP/PPR/PPML/PPFR 20mm-169mm Either No additional insulation S1560085
required
170mm-200mm Either An additional 200mm ring S1560085
of A60 insulation is to be
installed around the collar
or the pipe

Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and conditions

set out in that contract.

Page 9 of 14
Certificate No: LR2090258SF-02
Issue Date: 15 Mar 2020
Expiry Date: 14 Mar 2025
Reference: UKITSO/FIRE/TA/BM/WP41721157

ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2090258SF-02

Steel Bulkheads A-0

PVC 12mm-160mm Either No additional insulation S1560092
(inc uPVC & cPVC) required
161mm-225mm Either An additional 200mm ring S1560092
of A60 insulation is to be
installed around the collar
or the pipe
226mm-322mm Either Additional insulation S1560308
required to cover longer
length of seal when
installed on the insulated
side - See Note 5 and
insulation drawing
PVDF 169mm Either An additional 200mm ring S1560129
of A60 insulation is to be
installed around the collar
or the pipe
PE-AL-PE 16mm-63mm Either No additional insulation S1560134
(multi-layer pipe required
which may or may

not be insulated

with an insulation

jacket)

Beverage multi-pipe 75mm-100mm Either An additional 200mm ring S1560148
(with outer of A60 insulation is to be
insulated jacket installed around the collar
passing through fire or the pipe
collar/seal)
Preinsulated Pipes 75mm-315mm Collar to be
(Outer Diameter placed on the of A60 insulation is to be
including high fire risk side installed around the pipe
outershell/jacket) plus an additional wrap of
A-60 rated insulation
around the pipe on the
insulated side. Complete
length of insulation from
the structure to equal
300mm : see insulation
drawing

Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and conditions

set out in that contract.

Page 10 of 14
Certificate No: LR2090258SF-02
Issue Date: 15 Mar 2020
Expiry Date: 14 Mar 2025
Reference: UKITSO/FIRE/TA/BM/WP41721157

ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2090258SF-02

Steel Decks A-0

Pipe Material Max Collar Insulation Details for A-0 Drawing
Pipe O.D. range Installation Reference
(mm) Side

| ABS | 110mm-219mm | Underside | An additional 200mm ring of | S1557740 |
A60 insulation is to be installed
around the collar

PB 16mm-124mm Topside An additional 200mm ring of S1557766
A60 insulation is to be installed
around the pipe
125mm-225mm Underside or An additional 200mm ring of S1557766
topside A60 insulation is to be installed
around the collar or pipe on the
insulated side
PE/HDPE 25mm-225mm Underside or An additional 200mm ring of
topside A60 insulation is to be installed
around the collar or pipe on the
insulated side
226mm-320mm Underside Additional insulation required S1561005
to cover longer length of seal
when installed on the insulated
side - See Note 5 and insulation
drawing
PP/PPR/PPML/PPFR 16mm-110mm Underside or An additional 200mm ring of S1560085
topside A60 insulation is to be installed
around the collar or pipe on the
insulated side
111mm-225mm Underside An additional 200mm ring of S1560085
A60 insulation is to be installed
around the collar
226mm-320mm Underside Additional insulation required S1561005
to cover longer length of seal
when installed on the insulated
side - See Note 5 and insulation
drawing

Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and conditions

set out in that contract.

Page 11 of 14
Certificate No: LR2090258SF-02
Issue Date: 15 Mar 2020
Expiry Date: 14 Mar 2025
Reference: UKITSO/FIRE/TA/BM/WP41721157

ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2090258SF-02

Steel Decks A-0 (Cont)

PVC 16mm-50mm Underside or No additional insulation S1560122
(inc uPVC & cPVC) topside required
51mm-225mm Underside or An additional 200mm ring of S1560122
topside A60 insulation is to be installed
around the collar or pipe on the
insulated side
226mm-321mm Underside or Additional insulation required S1561005
topside to cover longer length of seal
when installed on the insulated
side - See Note 5 and insulation
drawing
PVDF 40mm-169mm Underside or An additional 200mm ring of S1560129
topside A60 insulation is to be installed
around the collar or pipe on the
insulated side
PE-AL-PE 16mm-31mm Underside An additional 200mm ring of S1560134
(multi-layer pipe A60 insulation is to be installed
which may or may around the collar on the
not be insulated insulated side
with an insulation
16mm-31mm Topside No additional insulation S1560134
jacket)
required
32mm-63mm Underside or No additional insulation S1560134
topside required
Beverage multi-pipe 75mm-100mm Underside or An additional 200mm ring of S1560148
(with outer topside A60 insulation is to be installed
insulated jacket around the collar or pipe on the
passing through fire insulated side
collar/seal)
Preinsulated Pipes 75mm-315mm Underside A 200mm ring of A60 insulation S1560316
(Outer Diameter is to be installed around the
including collar/seal plus two additional
outershell/jacket) 100mm rings of A60 insulation
around the collar and/or pipe :
see insulation drawing

Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and conditions

set out in that contract.

Page 12 of 14
Certificate No: LR2090258SF-02
Issue Date: 15 Mar 2020
Expiry Date: 14 Mar 2025
Reference: UKITSO/FIRE/TA/BM/WP41721157

ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2090258SF-02

5. When installed from the insulated side and when insulation is required (per the insulation drawing), the full length
of the Fire Collar (seal) should be fully insulated. Should extra insulation be required, it should either be a 200mm
ring of A-60 rated insulation fitted around the seal, or an A-60 rated insulation wrap around the Fire Collar. Please
see applicable insulation drawing reference in the tables
6. Two pipes; 160mm dia. PB and 16mm uPVC fitted with Sleev-it pipe penetrations and Sleev-it marine fire rated
sealant or equivalent, were subjected to a hydrostatic test and an air pressure test of 1 bar and 0.02 bar respectively
and no leakage was reported after 30 minutes, as detailed in the DNV Test Report No.LDN-08-045 dated 31 January
  1. In all cases, the sealant was applied to seal the penetration on both sides of the penetration and the test

pressures were applied from either side

7. Two pipes; 110mm dia. uPVC and 16mm PE fitted with Sleev-it pipe penetrations, type: “Sleev-it WT” comprising
Sleev-it EPDM rubber seals, type: “SLV EDPM Grommet”, were subjected to a hydrostatic test and an air pressure
test at 3.5 bar and 1 bar respectively and no leakage was reported after 30 minutes, as detailed in Lloyd’s Register
Test Witness Certificate No: SOU 0901586/1 dated 08 January 2010. The “Sleev-it WT” may be fitted on any one

side of the division

8. The above penetration systems are not to be used for penetrating tank boundaries

| 9. | When requested to be used in watertight bulkheads on passenger ships and Special Purpose Ships (SPS), the above |
penetration systems should be verified for compliance with the requirements given in SOLAS Chapter II-1 Reg.13.2.3
(2009 issue). The above penetration systems have not been approved according to this paragraph

  1. All sleev-it collars are suitable for protection of B-15 penetrations.

  2. A modified arrangement of the Roxtec Sleev-it pipe penetration called the “Roxtec Sleev-it Transition Collar” may
    be used to protect a plastic pipe transition / connection to a steel pipe. The Roxtec Sleev-it Transition collar is
    secured to the steel pipe using a Sleev-it Rising Clamp. The tables below detail both the horizontal installation
    when plastic pipe is transitioned to a steel pipe in close proximity to a steel bulkhead and also, deck installations
    when attached to a steel Scupper / Collecting / Drainage Pot as detailed within the applicable insulation drawings

referenced within the tables

Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and conditions

set out in that contract.

Page 13 of 14
Certificate No: LR2090258SF-02
Issue Date: 15 Mar 2020
Expiry Date: 14 Mar 2025
Reference: UKITSO/FIRE/TA/BM/WP41721157

ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2090258SF-02

Steel Bulkheads A-60

Max Collar
Pipe Material Pipe O.D. range
(mm) Side

Transition Collar and steel pipe up to the bulkhead

Insulated side S1560502
insulation to be fully wrapped in A-60 insulation.
Steel pipe to plastic pipe transition - installed

50-75mm (steel) to

PP/PPR/PPML/PPFR less than 450mm away from a bulkhead
50-90mm (plastic)
penetration
Steel pipe on the insulated side to be fully wrapped
Non-insulated side S1560502
in A-60 insulation for a distance of 450mm mm.

Steel Decks A-60

Pipe O.D. - Steel Pipe Collar
Pipe Material to Plastic Pipe
(mm) Side

Steel pipe to plastic pipe transition where
steel pipe forms part of or connects to a
Scupper Pot to be fully insulated with A-60

50-90mm (steel) to stainless steel Scupper / Collecting /
PP/PPR/PPML/PPFR Underside
50-90mm (plastic) Drainage Pot (with or without "drainage
Transition Collar
bell") - Both horizontal (elbow) and vertical
(straight) connections

Steel Decks A-0

Pipe O.D. - Steel Pipe Collar
Pipe Material to Plastic Pipe
(mm) Side

Steel pipe to plastic pipe transition where
steel pipe forms part of or connects to a
Scupper Pot to be fully insulated with A-60 rated

50-90mm (steel) to stainless steel Scupper / Collecting /
PP/PPR/PPML/PPFR Underside
50-90mm (plastic) Drainage Pot (with or without "drainage
Transition Collar
bell") - Both horizontal (elbow) and vertical
(straight) connections

Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and conditions

set out in that contract.

Page 14 of 14
Certificate No: LR2090258SF-02
Issue Date: 15 Mar 2020
Expiry Date: 14 Mar 2025
Reference: UKITSO/FIRE/TA/BM/WP41721157

ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR2090258SF-02

1. Approved Installation Variations for Sleev-it penetrations are given below;

a) Drawing S1528866 Revision (A) and associated Amendment to Installation Instructions Roxtec Sleev-it Fire
Penetration Seal ASS2012001301 (DOC-001830 Rev A).
b) Drawing S1538623 Revision (A) - PVC insert sleeve.
c) Drawing S1036168 Revision (B) - Sleev-it WT Deck Penetration (Wavin SI Tech PPr pipe). Design variation
referenced by Information Drawing S1029962 revision (A)

PLACE OF PRODUCTION

Roxtec International AB

Box 540

S-371 23 Karlskrona

Sweden

Bruce McDonald

Lead Fire and Safety Specialist

Lloyd’s Register Americas

Supplementary Type Approval Terms and Conditions

This certificate and Design Appraisal Document relates to type approval, it certifies that the prototype(s) of the product(s)
referred to herein has/have been found to meet the applicable design criteria for the use specified herein, it does not mean
or imply approval for any other use, nor approval of any products designed or manufactured otherwise than in strict

conformity with the said prototype(s).

Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and conditions

set out in that contract.