Certificate No: LR21217042SF-02
| Issue Date: | 19/10/2021 |
|---|---|
| Expiry Date: 06/06/2026 |
Certificate Of Fire Approval
This is to certify that the product detailed below will be accepted for compliance with the applicable Lloyd’s
Register Rules and Regulations and with the International Convention for the Safety of Life at Sea, (SOLAS), 1974, as
amended, for use on ships and offshore installations classed with Lloyd’s Register, and for use on ships and offshore
installations when authorised by contracting governments to issue the relevant certificates, licences, permits etc.
| Manufacturer | Roxtec International AB |
|---|---|
| Address | Box 540, Karlskrona, 371 23, Sweden |
| Type | CABLE AND PIPE PENETRATION (STANDARD FIRE TEST) |
| Description | Multi Cable and Pipe Penetration Types: RS Frame in steel and aluminium |
divisions
| Trade Name | RS Frame |
|---|
| Specified Standard | IMO Res. MSC.307(88) (2010 FTP Code) Annex 1 Part 3, 11 and section 8. |
IMO Res. MSC.61(67) IMO FTP Code Annex 1 Part 3
IMO/MSC/Circ. 1120 & 1488
This certificate is not valid for equipment, the design or manufacture of which has been varied or modified from the
specimen tested. The manufacturer should notify Lloyd’s Register North America, Inc. of any modification or
changes to the equipment in order to obtain a valid Certificate.
The Design Appraisal Document and its supplementary Type Approval Terms and Conditions form part of this
Certificate.
This certificate remains valid unless cancelled or revoked, provided the conditions in the attached Design Appraisal
Document are complied with and the equipment remains satisfactory in service.
Bruce McDonald
Fire & Safety Lead Specialist to Lloyd’s
| 1330 Enclave Parkway, Houston, Texas, 77077, | Register North America, Inc. |
|---|---|
| United States | A member of the Lloyd’s Register group |
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively,
referred to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or
expense caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the
relevant Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms
and conditions set out in that contract.
TA02 1.0.0
| Page | 2 of 6 |
|---|---|
| Certificate No: | LR21217042SF-02 |
| Issue Date: | 19/10/2021 |
| Expiry Date: | 06/06/2026 |
| DESIGN APPRAISAL DOCUMENT | Reference: | UKITSO/FIRE/TA/BM/WP44090475/PRJ11100330779 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR21217042SF-02
The undernoted documents have been appraised for compliance with the relevant requirements of International
Conventions, and this Design Appraisal Document forms part of the Certificate.
This Design Appraisal Document forms part of the Certificate.
This Certificate is an Amendment of Certificate Number LR21217042SF
FIRE TEST REPORTS
SP Technical research institute of Sweden (RISE). Test report numbers ;
6P02249 dated 17th August 2016, 6P10024 dated 7th March 2017, 8P07092rev 1 dated 16th January 2020, 8P07094rev1
dated 16th January 2020, 4P06068 dated 17th January 2015, 4P07023 dated 4th February 2015, 6P04351 dated 28th June
2016, 4P08662 dated 8th June 2015, 6P02999 dated January 23rd 2007, 7P02167 dated 7th August 2017, PX05454rev1
dated 8th September 2011, P603000 dated 27th January 2007.
Research Institute of Maritime Engineering (RIME) Test Report Numbers;
09-346(E) dated 11December 2009, 09-345(E) dated 11th December 2009,
DBI Danish Institute of Fire and Security Testing. Test report numbers ;
PGA11371A dated 20th February 2019, PGA10870A dated 13th November 2016, PGA10800A dated 26th May 2016,
PG10871Arev2 dated 16th January 2018, PGB10031A dated 09th July 2020, PGA10723A dated 4thFebruary 2016,
PG10652 dated 3rd July 2015, PGA 11302A dated 16th January 2019, PGA10047A dated 30th November 2020, PGB10032A
dated 1st July 2020, PGA11611A dated 11th January 2020, PGA11301A dated 22nd November 2018, PGB10020A dated 5th
May 2020, PGA10650 dated 18th May 2015, PGA10649 dated 18th May 2015, PGA11610A dated 18th December 2019,
PGB10110A dated 27th April 2021, PGB10110A dated 27th April 2021.
Centrum Techniki Okretowej ( Ship Design and Research centre S.A Gdansk) Test reports numbers;
RS-18/B-022/E dated, 29th January 2018, RS-18/B-484/E dated 10th December 2018, RS-18/B-485/E dated 10th December
2018, RS-17/B-396/E dated 31st October 2017, RS-18/B-023/E dated 29th January 2018, RS-19/B-224/E dated 1st August
2019, RS-17/B-395/E dated 30th October 2017, RS-18/B-555/E dated 15th January 2018, RS-20/B-017/E dated 23rd
January 2020, RS-17/B-210/E dated 2nd June 2017, RS-20/B-191/E dated 5th June 2020, RS-18/B292/E dated 13th
September 2018, RS-18/B293/E dated 13th September 2018, RS-18/B-181/E dated 7th May 2018, RS-20/B-181/E dated
31st March 2020, RS-19/B-356/E dated 18th October 2019, RS-19/B-355/E dated 16th October 2019, RS-20/B-410/E dated
17th December 2020, RS-19/B-020/E dated 27th May 2019, RS-21/B-241/E dated 30th June 2021.
PRESSURE TEST REPORTS
Pressure witness reports, N141EX8Z dated 10th August 2017, N1421782 dated 1st September 20
20.
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and
conditions set out in that contract.
| Page | 3 of 6 |
|---|---|
| Certificate No: | LR21217042SF-02 |
| Issue Date: | 19/10/2021 |
| Expiry Date: | 06/06/2026 |
| DESIGN APPRAISAL DOCUMENT | Reference: | UKITSO/FIRE/TA/BM/WP44090475/PRJ11100330779 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR21217042SF-02
CONDITIONS OF CERTIFICATION
| 1. | “Roxtec sealing system with multidiameter technology: RS-series (steel/aluminium)” consisting of a sleeve, |
|---|---|
| bolted, welded or attached through expansion (SL X) to a steel/aluminium section. Sleeve is fitted with a | |
| Roxtec RS series seal (standard, Ex or EMC) in sizes 23-1125. | |
| 2. | Penetration details are defined below in Tables 1-6. |
| — | — |
| 3. | Production items are to be manufactured in accordance with a quality control system which shall be |
| maintained to ensure that items are of the same standard as the approved prototype. | |
| 4. | The certificate holder is solely responsible for the products supplied under this Certificate and to ensure |
| — | — |
| that their products, whether manufactured by themselves or their licensee manufacturers, if agreed by | |
| Lloyd’s Register, are fully compliant with the relevant statutory regulations and Lloyd’s Register Class rules | |
| as applicable and designed, manufactured and installed to the same quality and specifications as the | |
| prototype tested, including components that are designed and manufactured by third parties. | |
| 5. | The test laboratory is solely responsible for all tests performed within the scope of this certificate and to |
| — | — |
| ensure that the testing is conducted in full compliance with the relevant test standard, approved | |
| operational procedures, statutory regulations and Lloyd’s Register requirements as applicable and to meet |
client objectives as per contractual agreements.
Steel Bulkheads A-60
Cable/Pipe
| Sleeve Type | Penetration size | Cable/Pipe | Outer diameter (OD) | Collar Position | Drawing Reference |
|---|---|---|---|---|---|
| [mm] |
| SL | RS23-RS125 | Cable | 10-88 | Centre-line, exposed or unexposed. | S1561774 |
|---|
| SL | RS23-RS400 | Steel Pipe | 6-330 | Centre-line, exposed or unexposed. | S1561020 |
| SL | RS23-RS644 | Steel Pipe | 6-558 | Unexposed | S1561020 |
| SL | RS23-RS300 | Copper Pipe | 6-225 | Centre-line, exposed or unexposed. | S1561052 |
| SL | RS25-RS500 | CuNi 90:10 Pipe | 10-420 | Centre-line, exposed or unexposed. | S1561128 |
| SL | RS50-RS1125 | Fibreglass Composite Pipe | 25-1040 | Centre-line, exposed or unexposed. | S1569740 |
| SL | RS43-RS100 | Pipe Bundle (steel) | 16-50 | Centre-line, exposed or unexposed. | S1561205 |
| SLA | RS25-RS75 | Cable | 10-32 | Exposed or unexposed | S1561776 |
| SLA | RS25-RS75 | Steel Pipe | 6-30 | Exposed or unexposed | S1561137 |
| SLA | RS25-RS75 | Copper Pipe | 6-34 | Exposed or unexposed | S1569744 |
| SL X | RS25-RS200 | Steel pipe | 6-168 | Unexposed | S1561185 |
| SL X | RS25 | Steel pipe | 6 | Exposed | S1561185 |
Table 1 RS series A-60 penetrations in Steel bulkheads
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and
conditions set out in that contract.
| Page | 4 of 6 |
|---|---|
| Certificate No: | LR21217042SF-02 |
| Issue Date: | 19/10/2021 |
| Expiry Date: | 06/06/2026 |
| DESIGN APPRAISAL DOCUMENT | Reference: | UKITSO/FIRE/TA/BM/WP44090475/PRJ11100330779 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR21217042SF-02
Steel Decks A-60
Cable/Pipe
| Sleeve Type | Penetration size | Cable/Pipe | Outer diameter (OD) | Collar Position | Drawing Reference |
|---|---|---|---|---|---|
| [mm] |
| SL | RS23-RS125 | Cable | 10-88 | Centre-line, exposed or unexposed. | S1561774 |
|---|
| SL | RS23-RS400 | Steel Pipe | 6-330 | Centre-line, exposed or unexposed. | S1561020 |
| SL | RS23-RS644 | Steel Pipe | 6-558 | Unexposed | S1561020 |
| SL | RS23-RS300 | Copper Pipe | 6-225 | Centre-line, exposed or unexposed. | S1561052 |
| SL | RS25-RS500 | CuNi 90:10 | 10-420 | Centre-line, exposed or unexposed. | S1561073 |
| SL | RS50-RS1125 | Fibreglass Composite Pipe | 25-1040 | Centre-line, exposed or unexposed. | S1569741 |
| SL | RS43-RS100 | Pipe Bundle (steel) | 16-50 | Centre-line, exposed or unexposed. | S1561205 |
| SLA | RS25-RS75 | Cable | 10-32 | Exposed or unexposed | S1561776 |
| SLA | RS25-RS75 | Steel Pipe | 6-30 | Unexposed | S1561137 |
| SLA | RS25-RS75 | Copper Pipe | 6-34 | Unexposed | S1569744 |
| SL X | RS25-RS200 | Steel Pipe | 6-168 | Exposed or unexposed | S1561185 |
Table 2 RS series A-60 penetrations in Steel Decks
Steel Bulkheads A-0
Cable/Pipe
| Sleeve Type | Penetration size | Cable/Pipe | Outer diameter (OD) | Collar Position | Drawing Reference |
|---|---|---|---|---|---|
| [mm] |
| SL | RS23-RS125 | Cable | 10-88 | Centre-line, exposed or unexposed. | S1561780 |
|---|
| SL | RS23-RS400 | Steel Pipe | 6-330 | Centre-line, exposed or unexposed. | S1561212 |
| SL | RS23-RS644 | Steel Pipe | 6-558 | Unexposed | S1561212 |
| SL | RS23-RS300 | Copper Pipe | 6-225 | Centre-line, exposed or unexposed. | S1561217 |
| SL | RS25-RS500 | CuNi 90:10 Pipe | 10-420 | Centre-line, exposed or unexposed. | S1561349 |
| SL | RS50-RS1125 | Fibreglass Composite Pipe | 25-1040 | Centre-line, exposed or unexposed. | S1569741 |
| SL | RS43-RS100 | Pipe Bundle (steel) | 16-50 | Centre-line, exposed or unexposed. | S1561500 |
| SLA | RS25-RS75 | Cable | 10-32 | Exposed or unexposed | S1561783 |
| SLA | RS25-RS75 | Steel Pipe | 6-30 | Exposed or unexposed | S1561494 |
| SLA | RS25-RS75 | Copper Pipe | 6-34 | Exposed or unexposed | S1569745 |
| SL X | RS25-RS200 | Steel pipe | 6-168 | Unexposed | S1561497 |
| SL X | RS25 | Steel pipe | 6 | Exposed | S1561497 |
Table 3 RS series A-0 penetrations in Steel bulkheads
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and
conditions set out in that contract.
| Page | 5 of 6 |
|---|---|
| Certificate No: | LR21217042SF-02 |
| Issue Date: | 19/10/2021 |
| Expiry Date: | 06/06/2026 |
| DESIGN APPRAISAL DOCUMENT | Reference: | UKITSO/FIRE/TA/BM/WP44090475/PRJ11100330779 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR21217042SF-02
Steel Decks A-0
Cable/Pipe
| Sleeve Type | Penetration size | Cable/Pipe | Outer diameter (OD) | Collar Position | Drawing Reference |
|---|---|---|---|---|---|
| [mm] |
| SL | RS23-RS125 | Cable | 10-88 | Centre-line, exposed or unexposed. | S1561780 |
|---|
| SL | RS23-RS400 | Steel Pipe | 6-330 | Centre-line, exposed or unexposed. | S1561212 |
| SL | RS23-RS644 | Steel Pipe | 6-558 | Unexposed | S1561212 |
| SL | RS23-RS300 | Copper Pipe | 6-225 | Centre-line, exposed or unexposed. | S1561217 |
| SL | RS25-RS500 | CuNi 90:10 | 10-420 | Centre-line, exposed or unexposed. | S1561242 |
| SL | RS50-RS1125 | Fibreglass Composite Pipe | 25-1040 | Centre-line, exposed or unexposed. | S1569741 |
| SL | RS43-RS100 | Pipe Bundle (steel) | 16-50 | Centre-line, exposed or unexposed. | S1561500 |
| SLA | RS25-RS75 | Cable | 10-32 | Exposed or unexposed | S1561783 |
| SLA | RS25-RS75 | Steel Pipe | 6-30 | Unexposed | S1561495 |
| SLA | RS25-RS75 | Copper Pipe | 6-34 | Unexposed | S1569745 |
| SL X | RS25-RS200 | Steel Pipe | 6-168 | Exposed or unexposed | S1561497 |
Table 4 RS series A-0 penetrations in Steel Decks
Aluminium Bulkheads A-60
Cable/Pipe
| Sleeve Type | Penetration size | Cable/Pipe | Outer diameter (OD) | Collar Position | Drawing Reference |
|---|---|---|---|---|---|
| [mm] |
| SL | RS23-RS125 | Cable | 10-88 | Centre-line, exposed or unexposed. | S1561775 |
|---|
| SL A | RS25-RS100 | Cable | 10-50 | Exposed or Unexposed | S1561779 |
Table 5. Rs series penetrations in Aluminium Bulkheads
Aluminium Decks A-60
Cable/Pipe
| Sleeve Type | Penetration size | Cable/Pipe | Outer diameter (OD) | Collar Position | Drawing Reference |
|---|---|---|---|---|---|
| [mm] |
| SL | RS23-RS125 | Cable | 10-86 | Centre-line, exposed or unexposed. | S1561775 |
|---|
| SL A | RS25-RS100 | Cable | 10-50 | Unexposed | S1561779 |
Table 6. RS series A-60 penetrations in Aluminium Decks
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and
conditions set out in that contract.
| Page | 6 of 6 |
|---|---|
| Certificate No: | LR21217042SF-02 |
| Issue Date: | 19/10/2021 |
| Expiry Date: | 06/06/2026 |
| DESIGN APPRAISAL DOCUMENT | Reference: | UKITSO/FIRE/TA/BM/WP44090475/PRJ11100330779 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR21217042SF-02
Notes
| 1. | Penetrations underwent a hydrostatic and pneumatic pressure test as detailed below; |
|---|
| Penetration type / sleeve | Hydrostatic Pressure | Pneumatic Pressure |
| RS23-RS644 | 6bar | 3bar |
| SL Sleeve | 6bar | 3bar |
| SL A Sleeve | 4bar | 1.5bar |
| SL X Sleeve | 6bar | 3bar |
| Bolted sleeve | 5 bar | 2.5bar |
PLACE OF PRODUCTION
Roxtec International AB
Box 540
S-371 23 Karliskrona
Sweden
Bruce McDonald
TSC Manager - Americas, Marine
Lloyd’s Register Americas
Lloyd’s Register EMEA
Supplementary Type Approval Terms and Conditions
This certificate and Design Appraisal Document relates to type approval, it certifies that the prototype(s) of the product(s)
referred to herein has/have been found to meet the applicable design criteria for the use specified herein, it does not mean
or imply approval for any other use, nor approval of any products designed or manufactured otherwise than in strict
conformity with the said prototype(s).
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and