| Page | 1 of 6 |
|---|---|
| Certificate No: | LR21217347SF-02 |
| Issue Date: | 07/06/2021 |
| Expiry Date: | 06/06/2026 |
Certificate Of Fire Approval
This is to certify that the product detailed below will be accepted for compliance with the applicable Lloyd’s Register
Rules and Regulations and with the International Convention for the Safety of Life at Sea, (SOLAS), 1974, as
amended, for use on ships and offshore installations classed with Lloyd’s Register, and for use on ships and offshore
installations when authorised by contracting governments to issue the relevant certificates, licences, permits etc.
| Manufacturer | Roxtec International AB |
|---|---|
| Address | Box 540, Karlskrona, 371 23, Sweden |
| Type | CABLE AND PIPE PENETRATION (STANDARD FIRE TEST) |
| Description | Multi Cable and Pipe Penetration Types: R Series in steel and aluminium |
divisions
| Trade Name | R Series |
|---|
| Specified Standard | IMO Res. MSC.307(88) (2010 FTP Code) Annex 1 Part 3 & 11 and section 8. |
IMO Res. MSC.61(67) IMO FTP Code Annex 1 Part 3 & 11
IMO/MSC/Circ. 1120 & 1488
This certificate is not valid for equipment, the design or manufacture of which has been varied or modified from the
specimen tested. The manufacturer should notify Lloyd’s Register North America, Inc. of any modification or
changes to the equipment in order to obtain a valid Certificate.
The Design Appraisal Document and its supplementary Type Approval Terms and Conditions form part of this
Certificate.
This certificate remains valid unless cancelled or revoked, provided the conditions in the attached Design Appraisal
Document are complied with and the equipment remains satisfactory in service.
Bruce McDonald
Fire & Safety Lead Specialist to Lloyd’s
| 1330 Enclave Parkway, Houston, Texas, 77077, | Register North America, Inc. |
|---|---|
| United States | A member of the Lloyd’s Register group |
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and
conditions set out in that contract.
TA02 1.0.0
| Page | 2 of 6 |
|---|---|
| Certificate No: | LR21217347SF-02 |
| Issue Date: | 07/06/2021 |
| Expiry Date: | 06/06/2026 |
| DESIGN APPRAISAL DOCUMENT | Reference: | UKITSO/FIRE/TA/BM/WP42722591 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR21217347SF-02
The undernoted documents have been appraised for compliance with the relevant requirements of International
Conventions, and this Design Appraisal Document forms part of the Certificate.
This Design Appraisal Document forms part of the Certificate.
FIRE TEST REPORTS
SP Technical research institute of Sweden (RISE). Test report numbers P602999 dated 23rd January 2007, P303000
dated 27th January 2007, 4P8662 dated 8th June 205, 4P06068, dated 17 January 2015, 6P02249 dated 17 August 2016,
6P07563 dated 20th December 2016, 7P02167 dated 7th August 2017, 8P04039 dated 06th August 2018, 8P04040 dated
13th August 2018, 8P07092 rev 1 dated 13th August 2018, 8P07092 rev 1 dated 16th January 2020,
DBI Danish Institute of Fire and Security Testing. Test report numbers PGA10723A dated 4th February 2016, PGA10799A
dated 5 February 2016, PGA 10800A dated 18th April 2016, PGA10870A dated 1st November 2016, PGA10871A rev2 dated
16th January 2018, PGA =11301A dated 22 November 2018, PGA11302A rev1 dated 5th November 2018, PGA 11370A
dated 14th January 2019, PGA 11371A dated 20th February 2019,
Centrum Techniki Okretowej ( Ship Design and Research centre S.A Gdansk) Test reports RS-19/B-225/E dated 1st
August 2019, RS-19/B-255/E dated 20th August 2019, RS-18/B-291/E dated 20th August 2018, RS-18/B-291/E dated 13th
September 2018, RS-18/B-484/E dated 10th December 2018, RS-18/B-485/E dated 10th December 2018, RS-19/B-224/E
dated 1st August 2019, RS-17/B-210/E dated 2nd June 2017, RS-18/B-179/E dated 25th June 2018 and Rs-20/B-82/E dated
21st April 2020.
PRESSURE TEST REPORTS
DNV witness reports 40007647-1 dated 13th December 2011, MLM 010238 dated 30th August 2001, N141EX82 rev 1 dated
10th August 2010.
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and
conditions set out in that contract.
| Page | 3 of 6 |
|---|---|
| Certificate No: | LR21217347SF-02 |
| Issue Date: | 07/06/2021 |
| Expiry Date: | 06/06/2026 |
| DESIGN APPRAISAL DOCUMENT | Reference: | UKITSO/FIRE/TA/BM/WP42722591 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR21217347SF-02
CONDITIONS OF CERTIFICATION
- “Roxtec sealing system with multidiameter technology: R-series (steel/aluminium)” consisting of a sleeve, bolted,
welded or attached through expansion (RX) to a steel/aluminium section. Sleeve is fitted with a Roxtec R frame
(standard, Ex or EMC) in sizes 50-200. The R frame is filled with Roxtec (standard, Ex or EMC) halogen free RM
modules.
2. Penetration details are defined below in Tables 1-6
- Production items are to be manufactured in accordance with a quality control system which shall be maintained to
ensure that items are of the same standard as the approved prototype - The certificate holder is solely responsible for the products supplied under this Certificate and to ensure that their
products, whether manufactured by themselves or their licensee manufacturers, if agreed by Lloyd’s Register, are
fully compliant with the relevant statutory regulations and Lloyd’s Register Class rules as applicable and designed,
manufactured and installed to the same quality and specifications as the prototype tested, including components
that are designed and manufactured by third parties
- The test laboratory is solely responsible for all tests performed within the scope of this certificate and to ensure that
the testing is conducted in full compliance with the relevant test standard, approved operational procedures,
statutory regulations and Lloyd’s Register requirements as applicable and to meet client objectives as per
contractual agreements
Steel Bulkheads A-60
Cable/Pipe
| Sleeve Type | Penetration size | Cable/Pipe | Outer diameter (OD) | Collar Position | Drawing Reference |
|---|---|---|---|---|---|
| [mm] |
| SL | R50-R200 | Cable | 10-67 | Centre-line, exposed or unexposed | S1553819 |
|---|
| SL | R50-R200 | Steel Pipe | 6-54 | Centre-line, exposed or unexposed | S1553894 |
| SL | R70-R200 | Cu pipe | 10-54 | Centre-line, exposed or unexposed | S1553980 |
| SLA | R50-R100 | Cable | 10-50 | Unexposed | S1553824 |
| SLA | R50 | Cable | 10 | Exposed | S1553824 |
| SL X | R70-R200 | Cable | 10-67 | Unexposed | S1553819 |
| SL X | R70-R200 | Steel Pipe | 6-53 | Unexposed | S1553861 |
Table 1 R series A-60 penetrations in Steel bulkheads
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and
conditions set out in that contract.
| Page | 4 of 6 |
|---|---|
| Certificate No: | LR21217347SF-02 |
| Issue Date: | 07/06/2021 |
| Expiry Date: | 06/06/2026 |
| DESIGN APPRAISAL DOCUMENT | Reference: | UKITSO/FIRE/TA/BM/WP42722591 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR21217347SF-02
Steel Decks A-60
Cable/Pipe
| Sleeve Type | Penetration size | Cable/Pipe | Outer diameter (OD) | Collar Position | Drawing Reference |
|---|---|---|---|---|---|
| [mm] |
| SL | R50-R200 | Cable | 10-67 | Centre-line, exposed or unexposed | S1553819 |
|---|
| SL | R50-R200 | Steel Pipe | 6-95 | Centre-line, exposed or unexposed | S1553894 |
| SL | R50-R200 | Cu pipe | 8-54 | Centre-line, exposed or unexposed | S1553980 |
| SL A | R50-R100 | Cable | 10-50 | Exposed or unexposed (Topside or underside) | S1553824 |
| SL X | R75-R200 | Cable | 10-83 | Exposed (Underside) | S1553819 |
| SL X | R70-R200 | Steel Pipe | 6-54 | Exposed (Underside) | S1553861 |
Table 2 R series A-60 penetrations in Steel Decks
Steel Bulkheads A-0
Cable/Pipe
| Sleeve Type | Penetration size | Cable/Pipe | Outer diameter (OD) | Collar Position | Drawing Reference |
|---|---|---|---|---|---|
| [mm] |
| SL | R50-R200 | Cable | 10-67 | Centre-line, exposed or unexposed | S1553898 |
|---|
| SL | R50-R200 | Steel Pipe | 6-54 | Centre-line, exposed or unexposed | S1553907 |
| SL | R50-R200 | Cu pipe | 8-54 | Centre-line, exposed or unexposed | S1553977 |
| SL A | R50 | Cable | 10 | Exposed | S1554009 |
| SL A | R50-R100 | Cable | 10-50 | Unexposed | S1554009 |
Table 3 R series A-0 penetrations in Steel bulkheads
Steel Decks A-0
Cable/Pipe
| Sleeve Type | Penetration size | Cable/Pipe | Outer diameter (OD) | Collar Position | Drawing Reference |
|---|---|---|---|---|---|
| [mm] |
| SL | R50-200 | Cable | 10-39 | Centre-line, exposed or unexposed | S1553898 |
|---|
| SL | R50-200 | Steel Pipe | 6-95 | Centre-line, exposed or unexposed | S1553988 |
| SL | R50-200 | Cu pipe | 8-54 | Centre-line, exposed or unexposed | S1553977 |
| SL A | R50-R100 | Cable | 10-50 | Exposed or unexposed (Topside) | S1554009 |
Table 4 R series A-0 penetrations in Steel Decks
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and
conditions set out in that contract.
| Page | 5 of 6 |
|---|---|
| Certificate No: | LR21217347SF-02 |
| Issue Date: | 07/06/2021 |
| Expiry Date: | 06/06/2026 |
| DESIGN APPRAISAL DOCUMENT | Reference: | UKITSO/FIRE/TA/BM/WP42722591 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR21217347SF-02
Aluminium Bulkheads A-60
Cable/Pipe
| Sleeve Type | Penetration size | Cable/Pipe | Outer diameter (OD) | Collar Position | Drawing Reference |
|---|---|---|---|---|---|
| [mm] |
| SL | R70-R200 | Cable | 10-28 | Centre-line, exposed or unexposed | S1559533 |
|---|
| SL A | R50-R100 | Cable | 10-50 | Exposed or unexposed | S1559534 |
| SL X | R70-R200 | Cable | 13-50 | unexposed | S1559533 |
Table 5. R series A-60 penetrations in Aluminium Bulkheads
Aluminium Decks A-60
Cable/Pipe
| Sleeve Type | Penetration size | Cable/Pipe | Outer diameter (OD) | Collar Position | Drawing Reference |
|---|---|---|---|---|---|
| [mm] |
| SL | R50-R200 | Cable | 10-67 | Centre-line, exposed or unexposed | S1559533 |
|---|
| SL A | R50-R100 | Cable | 10-50 | Unexposed (Upperside) | S1559534 |
| SL X | R70-R200 | Cable | 10-50 | Exposed (Underside) | S1559533 |
Table 6. R series A-60 penetrations in Aluminium Decks
Notes
| 1. | The following penetrations underwent a hydrostatic and pneumatic pressure test. |
|---|
| Penetration type | Hydrostatic Pressure | Pneumatic Pressure |
| R50 – R200 | 6 bar | 3 bar |
| Bolted Sleeve | 5 bar | 2.5 bar |
| SLA Sleeves | 4 bar | 1.5 bar |
| SLX Sleeve | 6 bar | 3 bar |
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and
conditions set out in that contract.
| Page | 6 of 6 |
|---|---|
| Certificate No: | LR21217347SF-02 |
| Issue Date: | 07/06/2021 |
| Expiry Date: | 06/06/2026 |
| DESIGN APPRAISAL DOCUMENT | Reference: | UKITSO/FIRE/TA/BM/WP42722591 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR21217347SF-02
PLACE OF PRODUCTION
Roxtec International AB
Box 540
S-371 23 Karlskrona
Sweden
Bruce McDonald
Fire & Safety Lead Specialist to Lloyd’s
Register North America, Inc.
A member of the Lloyd’s Register group
Supplementary Type Approval Terms and Conditions
This certificate and Design Appraisal Document relates to type approval, it certifies that the prototype(s) of the product(s)
referred to herein has/have been found to meet the applicable design criteria for the use specified herein, it does not mean
or imply approval for any other use, nor approval of any products designed or manufactured otherwise than in strict
conformity with the said prototype(s).
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and