LR21431832SF-01-optimized
Certificate No: LR21431832SF-01
Issue Date: 07/12/2021
Expiry Date: 09/11/2026
Certificate Of Fire Approval
This is to certify that the product detailed below will be accepted for compliance with the applicable Lloyd’s
Register Rules and Regulations and with the International Convention for the Safety of Life at Sea, (SOLAS), 1974, as
amended, for use on ships and offshore installations classed with Lloyd’s Register, and for use on ships and offshore
Address Box 540, S-37123, Karkskrona, Sweden
| Type | Pipe Penetration (Standard Fire Test) |
| Description | Pipe Penetration Types: Roxtec RS PPS & RS PPS/S single thermoplastic pipe |
penetration seals for use in A-rated steel and aluminium divisions
Trade Name Roxtec RS PPS & RS PPS/S
| Specified Standard | IMO Res. MSC.307(88) (2010 FTP Code) Annex 1 Part 3, 11 and section 8. |
IMO Res. MSC.61(67) IMO FTP Code Annex 1 Part 3
IMO/MSC/Circ. 1120 & 1488
specimen tested. The manufacturer should notify Lloyd’s Register North America, Inc. of any modification or
changes to the equipment in order to obtain a valid Certificate.
The Design Appraisal Document and its supplementary Type Approval Terms and Conditions form part of this
Certificate.
Bruce McDonald
Technical Authority - Statutory to Lloyd’s
1330 Enclave Parkway, Houston, Texas, 77077, Register North America, Inc.
United States A member of the Lloyd’s Register group
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively,
referred to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or
expense caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the
relevant Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms
and conditions set out in that contract.
TA02 1.0.0
Page 2 of 14
| DESIGN APPRAISAL DOCUMENT | Reference: | UKITSO/FIRE/TA/BM/WP39320227/PRJ11100260551 |
ATTACHMENT TO CERTIFICATE OF TYPE APPROVAL No. LR21431832SF-01
The undernoted documents have been appraised for compliance with the relevant requirements of International
Conventions, and this Design Appraisal Document forms part of the Certificate.
This Certificate is an Amendment of Certificate Number LR21431832SF
FIRE TEST REPORTS
Centrum Techniki Okretowej ( Ship Design and Research centre S.A Gdansk) Test reports numbers; RS-19/B-356/E dated
18th October 2019, RS-19/B-424/E dated 27th November 2019, RS-19/B-256/E dated 20th August 2019, RS-19/B-020/E, RS-
18/B484/E dated 10th December 2018, RS-18/B-293/E dated 13th September 2018, RS-19/B-224/E dated 1st August 2019, RS-
18/B-291/E dated 20th August 2018 and RS-19/B-424/E dated 27th November 2021.
SP Technical research institute of Sweden (RISE). Test report number : P902394 dated 25th May 2009.
DBI Danish Institute of Fire and Security Testing. Test report numbers ; PGA11370A dated 20th February 2019, PGA11302A
dated 16th January 2019, PGA10801A dated 29th August 2016 and PGA 11371A dated 20th February 2019
1. When installed in A-Rated (A-60 & A-0) steel and aluminium decks and bulkheads with approved insulation
arrangements as detailed within Tables 1-6 ( RS-PPS) and tables 7-12 (RS-PPS/S) and their applicable referenced
drawings.
2. Roxtec RS PPS consists of two rubber seals with multidiameter technology, fitted around the plastic pipe and
inserted at each end of a welded or bolted sleeve / coaming, generating a “back to back” arrangement. The two
rubber seals encase a strip of provided intumescent material which is continuously wound around the plastic pipe
before being inserted inside the sleeve / coaming. The sleeve / coaming may be of type “SLRS or “SLFRS”.
3. Penetration details are defined below in Tables 1-6 (RS PPS) and Tables 7-12 (RS PPS/S).
4. Roxtec RS PPS/S consists of a single rubber seal with multidiameter technology, incorporating an integrated strip
of intumescent material and fitted around the plastic pipe and inserted into the end of a sleeve/ coaming. The
sleeve / coaming may be of type “SLRS, “SLFRS” or “SLRSX”.
5. For applications in A-15 and A-30 rated steel divisions, insulation levels as per A-60 should be applied.
6. For penetrations in A-0 aluminium divisions additional insulation along the pipe may not be necessary, reference
should be made to the applicable installation drawing to ensure the division is suitably insulated to ensure division
integrity.
7. Production items are to be manufactured in accordance with a quality control system which shall be maintained
to ensure that items are of the same standard as the approved prototype.
Lloyd’s Register Group Limited, its affiliates and subsidiaries and their respective officers, employees or agents are, individually and collectively, referred
to in this clause as ‘Lloyd’s Register’. Lloyd’s Register assumes no responsibility and shall not be liable to any person for any loss, damage or expense
caused by reliance on the information or advice in this document or howsoever provided, unless that person has signed a contract with the relevant
Lloyd’s Register entity for the provision of this information or advice and in that case any responsibility or liability is exclusively on the terms and
Page 3 of 14
8. The certificate holder is solely responsible for the products supplied under this Certificate and to ensure that their
products, whether manufactured by themselves or their licensee manufacturers, if agreed by Lloyd’s Register, are
fully compliant with the relevant statutory regulations and Lloyd’s Register Class rules as applicable and designed,
manufactured and installed to the same quality and specifications as the prototype tested, including components
that are designed and manufactured by third parties.
9. The test laboratory is solely responsible for all tests performed within the scope of this certificate and to ensure
that the testing is conducted in full compliance with the relevant test standard, approved operational procedures,
statutory regulations and Lloyd’s Register requirements as applicable and to meet client objectives as per
contractual agreements.
Table 1. RS- PPS series A-60 penetrations in Steel bulkheads
Steel Bulkheads A-60
Max Collar
Pipe Material Pipe O.D. range
(mm) Side
150mm ring around the penetration on both
ABS 16mm-140mm Symetrical S1570248
sides of the bulkhead
PB 16mm-140mm Symetrical S1570248
Sleeve insulation plus insulation to cover the
PE/HDPE 16mm-355mm Symetrical S1570248
edge of the seal
150mm ring around the penetration on the
PP/PPR/PPML/PPFR 16mm-125mm Symetrical S1570248
insulated side of the bulkhead
PVC (inc uPVC & cPVC) 16mm-160mm Symetrical insulated side plus a 200mm wrap of S1570248
insulation around the pipe
16mm Symetrical insulated side plus a 400mm wrap of S1570266
PE-AL-PE insulation around the pipe
(multilayer pipe) 200mm ring around the penetration on the
17mm-160mm Symetrical insulated side plus a 600mm wrap of S1570266
Pre-insulated thermoplastic
pipes (OD - including outer 90mm-315mm Symetrical S1570266
shell / jacket) edge of the seal
Page 4 of 14
Table 2. RS-PPS series A-60 penetrations in Steel Decks
Steel Decks A-60
Max Collar
(mm) Side
100mm ring around the penetration on the
ABS 16mm-140mm Symmetrical S1570248
underside of the deck
PB 16mm-110mm Symmetrical S1570248
PE/HDPE 16mm-355mm Symmetrical S1570248
edge of the seal on the underside of the deck
PP/PPR/PPML/PPFR 16mm-125mm Symmetrical S1570248
PVC (inc uPVC & cPVC) 16mm-160mm Symmetrical S1570248
PVDF 16mm-125mm Symmetrical S1570248
PE-AL-PE 100mm ring around the penetration on the
(multi-layer pipe) underside of the deck
Pre-insulated plastic bundle
pipes (with outer insulated 100mm ring around the penetration on the
75mm-96mm Symmetrical
jacket passing through fire underside of the deck
collar/seal)
pipes (with or without outer Additional 100mm wrap of insulation around
68-96mm Symmetrical
insulated jacket passing the pipe on the underside of the deck
through fire collar/seal)
pipes (OD - including outer 90mm-315mm Symmetrical S1570266
shell / jacket) edge of the seal on the underside of the deck
Page 5 of 14
Table 3. RS- PPS series A-0 penetrations in Steel bulkheads
Steel Bulkheads A-0
Max Collar
(mm) Side
An additional 200mm ring of insulation is to
be installed around the sleeve plus two
16mm-31mm Symetrical S1570334
further 150mm rings of insulation (one on
each side of the bulkhead)
ABS 32mm-110mm Symetrical No additional insulation required S1570334
111mm-140mm Symetrical S1570334
PB 16mm-140mm Symetrical S1570334
Sleeve insulation and insulation to cover the
edge of the seal, plus an additional 200mm
PE/HDPE 16mm-355mm Symetrical S1570334
ring of insulation to be installed around the
sleeve
Additional 200mm and 150mm rings of
PP/PPR/PPML/PPFR 16mm-125mm Symetrical insulation are to be installed around the S1570334
sleeve
insulation to be installed around the sleeve
PVC (inc uPVC & cPVC) 16mm-160mm Symetrical S1570334
plus a 200mm wrap of insulation around the
pipe
16mm-32mm Symetrical No additional insulation required S1570360
| PE-AL-PE | Two additional 200mm rings of insulation are |
| (multilayer pipe) | to be installed around the sleeve plus a wrap |
| 33mm-160mm | Symetrical | of insulation around the pipe. Complete | S1570360 |
length of insulation from the structure to
equal 600mm : see insulation drawing
pipes (OD - including outer 90mm-315mm Symetrical S1570360
shell / jacket) ring of insulation to be installed around the
sleeve
Page 6 of 14
Table 4. RS-PPS series A-0 penetrations in Steel Decks
Steel Decks A-0
Max Collar
(mm) Side
Additional 200mm and 100mm rings of
ABS 16mm-140mm Symmetrical insulation are to be installed around the S1570334
sleeve on the underside of the deck
PB 16mm-110mm Symmetrical insulation are to be installed around the S1570334
PE/HDPE 16mm-355mm Symmetrical S1570334
PP/PPR/PPML/PPFR 16mm-125mm Symmetrical insulation are to be installed around the S1570334
PVC (inc uPVC & cPVC) 16mm-160mm Symmetrical insulation are to be installed around the S1570334
PVDF 16mm-125mm Symmetrical insulation are to be installed around the S1570334
16mm-32mm Symmetrical No additional insulation required S1570360
PE-AL-PE
(multi-layer pipe)
be installed around the sleeve plus a 100mm
33mm-110mm Symmetrical S1570360
long wrap of insulation around the pipe on
the underside of the deck.
Pre-insulated plastic bundle Additional 200mm and 100mm rings of
collar/seal) sleeve on the underside of the deck
| Pre-insulated plastic bundle | An additional 200mm ring of insulation is to |
| pipes (with or without outer | be installed around the sleeve plus a 100mm |
| 68-96mm | Symmetrical | S1570360 |
| insulated jacket passing | long wrap of insulation around the pipe on |
| through fire collar/seal) | the underside of the deck. |
pipes (OD - including outer 90mm-315mm Symmetrical S1570360
Page 7 of 14
Table 5. RS-PPS series A-Class penetrations in Aluminium Bulkheads (A-0 and A-60)
Aluminium Bulkheads A-0 and A-60
Max Collar
(mm) Side
150mm ring of insulation around the
PP/PPR/PPML/PPFR 16mm-110mm Symmetrical S1570292
penetration
PE/HDPE 16mm-355mm Symmetrical S1570292
edge of the seal
PVC (inc uPVC & cPVC) 16mm-160mm Symmetrical S1570292
penetration
PE-AL-PE 100mm ring of insulation around the
(multi-layer pipe) penetration
pipes (OD - including outer 90mm-315mm Symmetrical S1570292
Table 6. RS-PPS series A-Class penetrations in Aluminium Decks (A-0 and A-60)
Aluminium Decks A-0 and A-60
Max Collar
(mm) Side
PVC (inc uPVC & cPVC) 16mm-160mm Symetrical S1570292
PE-AL-PE Additional 450mm wrap of insulation around
16mm-110mm Symetrical
(multi-layer pipe) the pipe on the underside of the deck
Page 8 of 14
Table 7. RS- PPS/S series A-60 penetrations in Steel bulkheads
Max Collar
(mm) Details
| PE/HDPE | 16mm-110mm | Symmetrical | No additional insulation required | S1570748 |
| PP/PPR/PPML/PPFR | 16mm-110mm | Symmetrical | No additional insulation required | S1570748 |
| PE-AL-PE | 150mm ring around the penetration on the |
| 16mm-63mm | Symmetrical | S1570768 |
| (multi-layer pipe) | insulated side |
67mm-96mm Symmetrical No additional insulation required S1570768
collar/seal)
pipes (OD - including outer 75mm-110mm Symmetrical S1570768
shell / jacket) insulated side
Page 9 of 14
Table 8. RS-PPS/S series A-60 penetrations in Steel Decks
Steel Decks A-60
Max Collar
(mm) Details
| ABS | 16mm-110mm | Symmetrical | No additional insulation required | S1570748 |
150mm ring around the pipe on the
PVC (inc uPVC & cPVC) 16mm-114mm Symmetrical S1570748
Symmetrical plus
16mm-32mm No additional insulation required S1570768
above & below deck
PE-AL-PE
(multi-layer pipe)
Additional 200mm wrap of insulation around
33mm - 75mm Symmetrical S1570768
75mm-110mm Symmetrical No additional insulation required S1570768
collar/seal)
Page 10 of 14
Table 9. RS- PPS/S series A-0 penetrations in Steel bulkheads
Steel Bulkheads A-0
Max Collar
(mm) Details
PE/HDPE 16mm-110mm Symmetrical S1571336
16mm-63mm Symmetrical No additional insulation required S1571336
PP/PPR/PPML/PPFR
64mm-110mm Symmetrical S1571336
PE-AL-PE
16mm-63mm Symmetrical insulation are to be installed around the S1571354
(multi-layer pipe)
sleeve
pipes (with outer insulated An additional 200mm ring of insulation is to
jacket passing through fire be installed around the sleeve
collar/seal)
Pre-insulated thermoplastic Additional 200mm and 150mm rings of
shell / jacket) sleeve
Page 11 of 14
Table 10. RS-PPS/S series A-0 penetrations in Steel Decks
Steel Decks A-0
Max Collar
(mm) Details
ABS 16mm-110mm Symmetrical be installed around the pipe on the S1571336
PE/HDPE 16mm-110mm Symmetrical be installed around the pipe on the S1571336
PP/PPR/PPML/PPFR 16mm-110mm Symmetrical be installed around the pipe on the S1571336
PVC (inc uPVC & cPVC) 16mm-114mm Symmetrical insulation are to be installed around the S1571336
sleeve and pipe on the underside of the deck
Symmetrical plus
16mm-32mm be installed around the sleeve on the S1571354
above & below deck
PE-AL-PE
(multi-layer pipe) An additional 200mm ring of insulation is to
underside of the deck plus an additional
200mm wrap of insulation around the pipe
Pre-insulated plastic bundle An additional 200mm ring of insulation is to
collar/seal) underside of the deck
Page 12 of 14
Table 11. RS-PPS/S series A-Class penetrations in Aluminium Bulkheads (A-0 and A-60)
Max Collar
(mm) Details
| PP/PPR/PPML/PPFR | 16mm-110mm | Symmetrical | No additional insulation required | S1570774 |
| PE/HDPE | 16mm-110mm | Symmetrical | No additional insulation required | S1570774 |
Additional wrap of insulation around the
PE-AL-PE pipe. Complete length of insulation from the
16mm-63mm (A-60) Symmetrical
(multi-layer pipe) structure to equal 250mm : see insulation
drawing
PE-AL-PE
16mm-75mm (A-0) Symmetrical No additional insulation requried S1570774
(multi-layer pipe)
pipes (OD - including outer 75mm-110mm Symmetrical No additional insulation required S1570774
shell / jacket)
Page 13 of 14
Table 12. RS-PPS/S series A-Class penetrations in Aluminium Decks (A-0 and A-60)
Max Collar
(mm) Details
PE-AL-PE pipe on the underside of the deck. Complete
(multi-layer pipe) length of insulation from the structure to
equal 250mm : see insulation drawing
shell / jacket)
NOTES
1. Penetrations underwent a hydrostatic pressure test of 6 bar and pneumatic pressure test of 4 bar, for a period of
30 minutes without leakage, as detailed in testing witness reports SKM-04-4088 and MLM010247 and MLM020133.
Page 14 of 14
S-371 23 Karlskrona
Bruce McDonald
Technical Authority-Statutory
Lloyd’s Register Americas
product(s) referred to herein has/have been found to meet the applicable design criteria for the use specified herein,
it does not mean or imply approval for any other use, nor approval of any products designed or manufactured