MERB00007FN-Rev-0-optimized
MERB00007FN
Roxtec GK Firestop Sealing Kit, GK FS SK KIT sizes 89, 127, 140, 168, 200x150, 250x170, 219, 244,
This Certificate is valid until 2026-12-16.
Form code: MER 201.GBR Revision: 2022-09 www.dnv.com Page 1 of 3
Certificate No: MERB00007FN
“GK FS SK sealing kit“ consisting of a fiberglass cloth with built in heat activated intumescent material to be wrapped
around cable bundles and fitted into circular or oval aluminium pipe sleeves. Folded back on each side with ends sealed
off to create a cold smoke tight seal and secured by metal cable ties.
“GK FS SK sealing kit“ is intended to be used for bundled cables or as a blank fire stop solution. The installation shall
be made in symmetrically welded or bolted pipe sleeves.
GK FS SK sealing kit ROUND A-60:
The coaming is welded or bolted symmetrically of the deck/bulkhead.
Installation details according to drawings Roxtec No. S1566086, S1566087
Application Size Ø (mm) Length (mm) Tested Tested maximum Tested cable
minimum filling rate (%) maximum
filling rate diameter (mm)
Bulkhead 84 - 244 105 - 205 0 68 50
Deck 84 - 244 105 - 205 0 68 50
GK FS SK sealing kit OVAL A-60:
Application Size (mm) Length Tested Tested Tested cable
(Ø x L) (mm) minimum maximum maximum
filling rate filling rate diameter (mm)
Bulkhead 200x150 - 250x170 105 - 205 0 68 50
Deck 200x150 - 250x170 105 - 205 0 68 50
*Definition filing ratio:
Cable filing ratio = (The sum cross section of the cables) / (the inside cross section area of Coaming)
*Cross sectional of the cable=R2 x3.14
*R=Radius of Cable and the Seal.
Water- / Gas- tightness: Not applicable
Approved for use as a blank, single or multiple cables penetration system (combined in one or more cable bundles) in
class A-60 aluminium bulkheads and decks. Other applications are subject to case-by-case approval. Approved for use
in class A-0, A-15 and A-30 when the penetration system is insulated as A-60. In addition the division is to be insulated
with A-60 insulation at least 200 mm around the penetration.
The insulation material used has to be approved according to the UK Marine Equipment Regulation and bear the MER
Mark of Conformity.
Maximum filling ratio of 68%.
In general approved maximum cable diameter: 50 mm.
The bolted sleeves shall be installed with screws + spring washer.
Sleeves with lengths L=105 to 205mm with or without intumescent strips can be used.
The systems must not be installed in bulkheads and decks if water- and gas- tightness is required.
Form code: MER 201.GBR Revision: 2022-09 www.dnv.com Page 2 of 3
Each product is to be supplied with its manual for installation, use and maintenance.
Test Reports A60 Fire Class:
PGB10016A - A60 Aluminium Deck, date 2020-06-03, DBI Copenhagen Denmark,
RS-20/B-082/E – A60 Aluminium Bulkhead, Date 2020-04-21, CTO Gdansk, Poland
Test Reports Cold Smoke:
Roxtec No. 29092016-01, dated 2016-09-29; No. 22032017-01, dated 2017-03-22; No. 14122016-01,
dated 2016-12-14, 8P07092 A-class steel deck, SP Technical Research Institute of Sweden, 8P07094 A-class steel
Bulkhead, SP Technical Research Institute of Sweden
Installation Drawings:
Roxtec No. S1566086 dated 2021-04-14, S1566087 dated 2021-11-24
General Arrangement Drawings:
Roxtec No. S1543766 dated 2019-10-23, S1535797 dated 2019-10-22
Sleeve Drawings:
Roxtec No. S1535700 dated 2020-02-13, S1550433 dated 2019-12-17, S1540158 dated 2019-12-20
- IMO Res. MSC.307(88)-(2010 FTP Code), Annex 1: Part 3,
- MSC.1/Circ. 1488
For identification to this type examination certificate the product or packing is to be marked with manufacturer’s name
and address, type designation, fire-technical rating and the Mark of Conformity (see page 1).
Form code: MER 201.GBR Revision: 2022-09 www.dnv.com Page 3 of 3