RISEFR AA-125_Rev4-eng-optimized
DOCUMENTATION
RISEFR AA-125
With reference to the national code of building regulations of 27 June 2008 with the Norwegian building regulations of 1 July 2017
and belonging guidance, RISE Fire Research AS document, on the basis of test certificates, evaluations and installation
instructions, that this product meets the requirements of the Norwegian authorities as to the fire related qualities.
Building material: Roxtec Cable and Pipe Penetration Seals
| Product | ROXTEC International AB |
| responsible: | Box 540, 371 23 Karlskrona, Sverige |
The documentation is conditional on that the product is in accordance with the specifications given in the appendix
and that the products is applied and used in accordance with regulations and all important details in this process
follow precisely what is described in a user instruction, which is checked by RISE Fire Research AS. Both the user
instruction and the RISE Fire Research AS Documentation shall follow the product or be available for the
purchaser, user, inspector and the local authority.
The product shall be labelled with RISEFR AA-125, trade name, product responsible and/or manufacturer together
with a reference to the production for traceability. The labelling shall have good visibility.
Detailed product design and principle design of installation details are described in “Standard construction details
for Roxtec Cable and Pipe Penetration Seals, belonging to Documentation RISEFR AA-125”. The version of the
construction details filed at RISE Fire Research AS at any time is a formal part of the approval.
The product must have at least one annual, external inspection related to the internal system for control of quality.
The inspection is adjusted to the type of product and other existing inspection arrangements. Details specified in a
written agreement with RISE Fire Research AS.
First issued: 2002-03-14. A renewal may be issued based on a written application. Termination by the applicant
shall be asked for in writing and with 6 months notice. RISE Fire Research AS as may withdraw this
documentation when irregularities or misuse happens and written instructions are not respected.
Issued: 2017-10-30
Valid until: 2023-01-01
_______________________ _______________________
Asbjørn Østnor, Jan P. Stensaas
Department Manager Documentation Discipline Manager Documentation
This document is an English version of the Norwegian documentation RISEFR AA-125 dated 2017-10-30.
Postadresse Besøksadresse Telefon E-post / web Foretaksnummer
Postboks 4767 Sluppen Tillerbruveien 202 464 18 000 post@RISEFR.no NO 982 930 057 MVA
7465 Trondheim 7092 Tiller www.RISEFR.no
RISEFR AA-125
Appendix 1 to Documentation RISEFR AA-125 av 2017-10-30.
1. Owner of the Documentation thickness ≥ 95 mm. The fire resistance is predicted by
ROXTEC International AB means of fire tests as given in item 7.
Box 540,
371 23 Karlskrona,
SWEDEN, www.roxtec.com
2. Manufacturer
ROXTEC International AB, www.roxtec.com
3. Product Description
Roxtec modules
Cables
Rectangular G- and B-frames are adjusted into the
edge of a masonry wall or floor and filled with
modules of synthetic rubber. Circular R-frames
pressed into moulded or core drilled apertures or
bolted sleeves with flange and filled with blocks of
synthetic rubber. The thickness of the blocks is 60 mm
and is adapted to the number and type of cables that
are required in the penetration. (See fig. 1). Roxtec B-frame Roxtec G-frame
Components: Rectangular/circular frame and blocks
in different sizes.
Pipes
One-sided installed RS PPS/S- and R penetration
system for PVC- and metal pipes in walls. Roxtec RS
PPS/S is a circular penetration system for penetration
of PVC-pipes. Roxtec R has a circular expansion
frame med quadratic shaped seal assembly for metallic Roxtec RS PPS/S frame Roxtec R frame
pipes. The penetration system makes it possible to Fig.1
install adjacent to existing pipes. Examples of use of Roxtec Cable and Pipe Penetration
Seals.
circular tube (RS PPS/S-system) and rectangular 6. Special Conditions for Use and Installation
blocks (R-system). Roxtec Cable and Pipe Penetration Seals shall be
installed according to installation details shown in
4. Fields of Application “Standard Construction Details for Roxtec Cable and
Typical range of use for Roxtec Cable and Pipe Pipe Penetration Seals belonging to RISE Fire
Penetration Seals are penetration seals for cables and Research AS documentation RISEFR AA-125”.
plastic/metallic pipes in fire partitions. Roxtec Cable
and Pipe Penetration Seals can be used in situations 7. Basis for the Documentation
where it is required a corresponding fire resistance of This documentation is based on the properties that are
class ‘EI’ according to TEK (The Norwegian building documented in the following reports:
regulations).  Test report: 71765/A dated 1997-11-03 and 67744
dated 1996-11-19 from Warrington Fire Research
5. Properties og R10046 dated 1990-09-26 from SP The
Table 1 shows the fire resistance of penetration seals Swedish Research Institute, according to ISO 834,
of cables in wall/floors of concrete of thickness ≥ 150 BS 476 and prEN 1366-3.
mm. Table 2 shows the fire resistance to penetration  Test report: P705521 dated 2008-04-21, according
seals of pipes in flexible and concrete walls with a to NS-EN 1366-3:2004, from SP Swedish Research
Institute.
RISEFR AA-125
Table 1 8. Validity
The fire resistance of Roxtec Cable and Pipe Penetration
Seals in penetrations of cables in wall/floor of concrete of
The validity of the appendix is uniquely linked to the
thickness  150 mm (in case of two-sided seals the thick- first page of the document with the requirements,
ness og wall/floor  200 mm). conditions and time stamps that are presented there.
Fire resistance
Frame type Max. conductor
One-/two-sided 9. Technical Management
(Size) area per cable
(minutes)
G (2-8 plus 3 x 185/90 mm² Cu.
Project manager for this approval is Jan P. Stensaas,
combinations) 1 x 150/25 mm² Al.
B (2-8 plus 3 x 185/90 mm² Cu.
3 x 185/90 mm² Cu. 60 / 90
R (70 - 200)
1 x 150/25 mm² Al. 60 / 120
4 x 185/50 mm² Cu. 60 / 120
RS (23 - 150)
Satisfies functional requirement for temperature og integrity.
Can be used in situations where it is required a corre-
sponding fire resistance of class ‘EI’ according to TEK (The
Norwegian building regulations).
Table 2
Seals in penetrations of pipes in flexible and concrete walls
of thickness ≥ 95 mm.
Pipe material, max pipe
Name of pene- Fire
diameter and 1)
tration seal resistance
wall thickness
(diameter (mm)) (minutes)
(mm)
RS PPS/S PVC: Ø 5 – 110,
90
(Ø 31-150) Wall thickness: 0,5–2,0
R (Ø 70-200) Steel, Cu : Ø 10 – 28, 60
2)
400 mm long og 50 mm thick insulation of mineral wool of
minimum density of 100 kg/m3.