Certificate No:
TAF00000HK
| TYPE APPROVAL CERTIFICATE | Revision No: |
|---|---|
| 9 |
This is to certify:
That the Class A and B Penetration
with type designation(s)
Roxtec sealing system: Sleev-it steel divisions
Issued to
Roxtec International AB
Karlskrona, Sweden
is found to comply with
DNV statutory interpretations DNV-SI-0364 – SOLAS interpretations, Edition July 2021
DNV rules for classification – Ships
DNV offshore standards
Application :
Approved for use as a plastic pipe penetration system in class A-0 and A-60 steel bulkheads and decks.
Products approved by this certificate are accepted for installation on all vessels classed by DNV.
Issued at Høvik on 2023-04-11
for DNV
| This Certificate is valid until 2027-04-26. | Digitally Signed By: Permoda, Jowita |
|---|---|
| DNV local unit: Malmö | |
| DNV Gdynia, Poland |
Approval Engineer: Marcin Tobiasz
Jowita Permoda
Head of Section
This Certificate is subject to terms and conditions overleaf. Any significant change in design or construction may render this Certificate invalid.
The validity date relates to the Type Approval Certificate and not to the approval of equipment/systems installed.
LEGAL DISCLAIMER: Unless otherwise stated in the applicable contract with the holder of this document, or following from mandatory law, the liability of DNV AS, its
parent companies and their subsidiaries as well as their officers, directors and employees (“DNV”) arising from or in connection with the services rendered for the
purpose of the issuance of this document or reliance thereon, whether in contract or in tort (including negligence), shall be limited to direct losses and under any
circumstance be limited to 300,000 USD.
| Form code: TA 251 | Revision: 2022-12 | www.dnv.com | Page 1 of 6 |
|---|---|---|---|
| Job Id: | 262.1-016326-11 | ||
| Certificate No: | TAF00000HK | ||
| Revision No: | 9 |
Product description
“Roxtec sealing system: Sleev-it steel divisions”
consist of a steel collar casing lined with intumescent material on the inside and a flange. It is available in FC MAR (fire
penetration seal) and WT MAR (Fire/Watertight penetration seal) versions depending on application.
The Sleev-it is installed onto a steel division by welding (FC/WT MAR) or bolting (FC MAR) depending on version.
Marine graded sealant is applied during the installation to achieve a cold smoke seal.
Application/Limitation
Approved for use as a plastic pipe penetration system in class A-60 steel bulkheads and decks according to tables
below.
Approved for use in class A-0, A-15 and A-30 when the penetration system is insulated as A-60 and in addition the
division is to be insulated with A-60 insulation at least 200 mm around the penetration.
Other applications are subject to case-by-case approval.
Table 1: Approved pipe penetration in A-60 steel bulkhead
| Sleev-it size | Pipe | Pipe diameter | Seal |
|---|---|---|---|
| Insulation drawing | |||
| (OD) [mm] | material | (OD) [mm] | position |
| — | — | — | — |
| 28 - 286 | ABS | 16 - 225 | Uninsulated side |
| 28 | ABS | 16 | Insulated side |
| 28 – 198 | PB | 16 - 160 | Either |
| 28 – 286 | PE | 16 - 225 | Either |
| 28 – 240 | PP | 16 - 200 | Either |
| 32 - 248 | PVC | 12 - 200 | Either |
| 207 | PVDF | 169 | Either |
| 102 - 125 | Beverage multipipe | 75 - 100 | Either |
| 28 - 48 | PE/ALU/PE | 16 - 32 | Either |
| 48 - 85 | PE/ALU/PE | 33 - 63 | Either |
| 248 - 350 | PVC | 201 - 271 | Insulated side |
| 248 - 350 | PVC | 201 - 271 | Insulated side |
| 286 - 391 | PE | 226 - 315 | Insulated side |
| 102 - 391 | Pre-insulated pipe | 75 - 315 | Uninsulated side |
| Multi pipe1) | |||
| 36 - 102 | 20 - 41 | Either | S1508739 Rev. A |
| — | — | — | — |
| PVC, PP |
1) Penetration type FC MAR-75M
Table 2: Approved pipe penetration in A-60 steel deck
| Sleev-it size | Pipe | Pipe diameter | Seal |
|---|---|---|---|
| Insulation drawing | |||
| (OD) [mm] | material | (OD) [mm] | position |
| — | — | — | — |
| 28 - 286 | PE | 25 - 225 | Either |
| 36 - 143 | PP | 20 - 110 | Either |
| 28 - 158 | PB | 25 - 125 | Either |
| 28 - 198 | PVC | 25 - 160 | Either |
| 69 - 213 | PVDF | 48 - 166 | Either |
| 28 - 85 | PE/ALU/PE | 16 - 63 | Either |
| 102 - 125 | Beverage multipipe | 75 - 100 | Either |
| Multi pipe1) | |||
| 36 - 69 | 22 - 50 | Either | S1508739 Rev. A 1 |
| — | — | — | — |
| PP, PVC | |||
| 36 - 69 | PE/ALU/PE, PVC, PP | 22 - 50 | Either |
| — | — | — | — |
| 198 - 400 | PVC | >160 - 321 | Either |
| Form code: TA 251 | Revision: 2022-12 | www.dnv.com | Page 2 of 6 |
| Job Id: | 262.1-016326-11 |
| Certificate No: | TAF00000HK |
| Revision No: | 9 |
| Sleev-it size | Pipe | Pipe diameter | Seal |
Insulation drawing
| (OD) [mm] | material | (OD) [mm] | position |
|---|---|---|---|
| 28 - 286 | ABS | 16 - 225 | Underside |
| 28 | ABS | 16 | Either |
| 28 - 41 | PB | 16 - 24 | Underside |
| 158 - 248 | PB | >125 - 200 | Underside |
| 28 - 41 | PE | 16 - 24 | Underside |
| 286 - 400 | PE | >225 - 320 | Underside |
| 28 - 36 | PP | 16 - 19 | Underside |
| 143 - 400 | PP | >110 - 320 | Underside |
| 28 - 41 | PVC | 16 - 24 | Underside |
| 102 - 391 | Pre-insulated pipe | 75 - 315 | Underside |
| 69 - 143 | PP | 50 - 110 | Underside |
- Penetration type FC MAR-75M
Table 3: Approved pipe penetration in A-0 steel bulkhead
| Sleev-it size | Pipe | Pipe diameter | Seal |
|---|---|---|---|
| Insulation drawing | |||
| (OD) [mm] | material | (OD) [mm] | position |
| — | — | — | — |
| 28 - 286 | ABS | 16 - 225 | Uninsulated side |
| 28 | ABS | 16 | Insulated side |
| 28 - 198 | PB | 15 - 160 | Insulated side |
| 28 - 286 | PE | 16 - 225 | Either |
| 286 - 391 | PE | > 225 - 315 | Either |
| 36 - 207 | PP | 20 - 169 | Either |
| 36 | PP | 20 | Either |
| 28 - 56 | PP | 16 - 39 | Either |
| 28 - 85 | PE/ALU/PE | 16 - 63 | Either |
| 207 - 248 | PP | 170 - 200 | Either |
| 102 - 125 | Beverage multipipe | 75 - 100 | Either |
| 28 - 198 | PVC | 16 - 160 | Either |
| 198 - 248 | PVC | > 160 - 200 | Either |
| 248 - 350 | PVC | > 200 - 271 | Insulated side |
| 102 - 391 | Pre-insulated pipe | 75 - 315 | Uninsulated side | S1552430 Rev. A |
|---|
- Georg Fischer COOL-FIT 2.0 or equivalent
Table 4: Approved pipe penetration in A-0 steel deck
| Sleev-it size | Pipe | Pipe diameter | Seal |
|---|---|---|---|
| Insulation drawing | |||
| (OD) [mm] | material | (OD) [mm] | position |
| — | — | — | — |
| 28 - 286 | ABS | 16 - 225 | Underside |
| 28 | ABS | 16 | Either |
| 28 - 41 | PB | 16 - 24 | Underside |
| 158 - 248 | PB | >125 - 200 | Underside |
| 28 - 41 | PE | 16 - 24 | Underside |
| 286 - 400 | PE | >225 - 320 | Underside |
| 28 - 36 | PP | 16 - 19 | Underside |
| 143 - 400 | PP | >110 - 320 | Underside |
| 28 - 69 | PVC | 16 - 50 | Underside |
| Form code: TA 251 | Revision: 2022-12 | www.dnv.com | Page 3 of 6 |
| Job Id: | 262.1-016326-11 |
| Certificate No: | TAF00000HK |
| Revision No: | 9 |
| Sleev-it size | Pipe | Pipe diameter | Seal |
Insulation drawing
| (OD) [mm] | material | (OD) [mm] | position |
|---|---|---|---|
| 28 - 69 | PVC | 16 - 50 | Either |
| 85 | PVC | 63 | Topside |
| 69 - 400 | PVC | >50 - 321 | Either |
| 41 - 158 | PB | 25 - 125 | Either |
| 41 - 158 | PE | 25 - 225 | Either |
| 36 - 143 | PP | 20 - 110 | Either |
| 198 - 400 | PVC | >160 - 321 | Either |
| 69 - 213 | PVDF | 48 - 166 | Either |
| 28 - 85 | PE/ALU/PE | 16 - 63 | Either |
| 102 - 125 | Beverage multipipe | 75 - 100 | Either |
| 102 - 391 | Pre-insulated pipe1) | 75 - 315 | Underside |
- Georg Fischer COOL-FIT 2.0 or equivalent
Pipe reference list
| ABS | Acrylonitrile Butadiene Styrene |
|---|---|
| PB | Polybutylene |
| PE | Polyethylene |
| PP | Polypropylene (including PP, PPr and three-layer PP) |
| PVC | Polyvinyl Chloride (including PVC-C and PVC-U) |
| PVDF | Polyvinylidene Fluoride |
| Composite pipes made of outer/inner PE layer and intermediate |
PE/ALU/PE
Al thin-walled pipe.
| Beverage multipipe | Bundle of plastic pipes covered with thermal insulation |
|---|---|
| Pre-insulated pipe | Thermoplastic pipe with integrated thermal insulation |
Cold service piping insulated with Armaflex rubber insulation layer is to be locally interrupted through the penetration
system.
Standard design is one pipe is routed through each Roxtec Sleev-it penetration. For multi-pipe application, the
penetration type “SLV75M and FC-MAR75M” shall be used.
The insulation material used has to be approved according to the Marine Equipment Directive and bear the Mark of
Conformity.
Each product is to be supplied with its manual for installation and maintenance.
For applications where water and or gas tightness is requested Sleev-it type WT is to be used exclusively. This type is
approved for application in steel bulkheads or decks limited to a pressure of 2,33 bar water tightness and 0,67 bar gas
tightness.
The penetration system is generally not to be used for penetrating boundaries of tanks.
The pipe penetrations are not approved for use in watertight bulkheads on passenger ships and special purpose ships
(SPS).
Type Approval documentation
Installation instructions:
| ASS2012012001201 D | Installation instruction Roxtec Sleev-it – Waterproof penetration seal |
|---|---|
| ASS2012012001301 D | Installation instruction Roxtec Sleev-it – Fire penetration seal |
Bulkhead Class A-60:
Test report No. 164476A dated 2007-07-23 from Bodycote Warringtonfire, UK
Test report No. 164476B dated 2007-06-26 from Bodycote Warringtonfire, UK
Test report No. 180251A dated 2009-02-16 from Bodycote Warringtonfire, UK
Test report No. 177105A dated 2008-11-04 from Bodycote Warringtonfire, UK
| Form code: TA 251 | Revision: 2022-12 | www.dnv.com | Page 4 of 6 |
|---|---|---|---|
| Job Id: | 262.1-016326-11 | ||
| Certificate No: | TAF00000HK | ||
| Revision No: | 9 |
Test report No. 183387A dated 2009-06-12 from Exova Warringtonfire, UK
Test report No. 309855A dated 2011-10-05 from Exova Warringtonfire, UK
Test report No. 303585A dated 2011-02-17 from Exova Warringtonfire, UK
Test report No. 198004A dated 2010-12-07 from Exova Warringtonfire, UK
Test report No. 303584A dated 2011-04-07 from Exova Warringtonfire, UK
Test report No. 316943 dated 2012-04-26 from Exova Warringtonfire, UK
Test report No. 314670 dated 2012-06-25 from Exova Warringtonfire, UK
Test report No. 324083 dated 2013-04-24 from Exova Warringtonfire, UK
Test report No. 30717A dated 2011-06-17 from Exova Warringtonfire, UK
Test report No. RS-18/B-264/E dated 2018-09-14 from CTO S.A, Poland
Test report No. RS-19/B-424/E dated 2019-11-27 from CTO S.A, Poland
Test report No. RS-21/B-241/E dated 2021-06-30 from CTO S.A, Poland
Test report No. PGB10030A dated 2020-07-16 from DBI, Denmark
Test report No. 881/07/A/NP/R 102 dated 2007-03-21 from DGA
Test report No. 5P08394 dated 2016-03-02 from SP, Sweden
Test report No. RS-21/B-241/E dated 2021-06-30 from CTO S.A, Poland
Test report No. PGB10167A dated 2022-03-03 from DBI, Denmark
Deck Class A-60:
Test report No. 170080B dated 2008-01-21 from Bodycote Warringtonfire, UK
Test report No. 175486A dated 2008-08-11 from Bodycote Warringtonfire, UK
Test report No. 170080A dated 2008-01-21 from Bodycote Warringtonfire, UK
Test report No. 175486B dated 2008-08-11 from Bodycote Warringtonfire, UK
Test report No. 170080B dated 2008-01-21 from Bodycote Warringtonfire, UK
Test report No. 190890A_2 dated 2010-03-02 from Exova Warringtonfire, UK
Test report No. 309638A dated 2011-08-03 from Exova Warringtonfire, UK
Test report No. 325332 dated 2013-01-13 from Exova Warringtonfire, UK
Test report No. 188626 dated 2009-12-22 from Exova Warringtonfire, UK
Test report No. 314669 dated 2012-04-26 from Exova Warringtonfire, UK
Test report No. 320402A dated 2012-10-29 from Exova Warringtonfire, UK
Test report No. 329449 dated 2013-08-13 from Exova Warringtonfire, UK
Test report No. 334429 dated 2013-12-17 from Exova Warringtonfire, UK
Test report No. RS-18/B-265/E dated 2018-09-17 from CTO, Poland
Test report No. PGB10032A dated 2020-07-01 from DBI, Denmark
Test report No. PGB10047A dated 2020-11-30 from DBI, Denmark
Test report No. PGA10871A dated 2018-01-18 from DBI, Denmark
Test report No. 6P02249 dated 2016-05-17 from SP, Sweden
Test report No. 6P10022 dated 2017-03-07 from SP, Sweden
Test report No. 878/07/A/NP/R 102 dated 2007-03-28 from DGA
Test report No. PGA11611A dated 2020-01-11 from DBI, Denmark
Test report No. RS-22/B-153/E dated 2022-05-04 from CTO S.A, Poland
Test report No. PGB10172A dated 2022-06-17 from DBI, Denmark
Bulkhead Class A-0
Test report No. 198004A dated 2010-12-07 from Exova Warringtonfire, UK
Test report No. 324083 dated 2013-04-24 from Exova Warringtonfire, UK
Test report No. 303584A dated 2011-04-07 from Exova Warringtonfire, UK
Test report No. 337717 dated 2014-05-13 from Exova Warringtonfire, UK
Test report No. 307171/A dated 2011-05-26 from Exova Warringtonfire, UK
Test report No. 8P07092 Rev.1 dated 2020-01-16 from SP, Sweden
Test report No. RS-19/B-423/E dated 2019-11-19 from CTO, Poland
Test report No. RS-20/B-081/E dated 2020-03-31 from CTO, Poland
Deck Class A-0
Test report No. PGA11388A dated 2019-08-14 from DBI, Denmark
Test report No. PGB10110A dated 2021-04-27 from DBI, Denmark
Test report No. 8P07092, Rev.1 dated 2020-01-16 from RISE, Sweden
Miscellaneous documents:
Excel spread sheet “Test Review-Sleeve-it”, 2020
Indicative test No. 189958 dated 9 February 2010 (EDPM rubber seal)
Assessment No. 184391/A (Alu deck), 17 December 2009
(Sleev-it WT-MAR, type A)
Drawing 320420A,29 October 2012 and Assessment report No. 336024, 18 December 2013
| Form code: TA 251 | Revision: 2022-12 | www.dnv.com | Page 5 of 6 |
|---|---|---|---|
| Job Id: | 262.1-016326-11 | ||
| Certificate No: | TAF00000HK | ||
| Revision No: | 9 |
Water and gas tightness reports
Survey report LDN-08-045 dated 2008-05-09 from DNV London
Test witness certificate no. SOU 0901586/1 dated 2010-01-08 from Lloyd’s Register
Drawing No. S1026329, Rev. H dated 2016-10-11
Drawing No. S1026339, Rev. E dated 2016-11-15
Drawing No. S1036341, Rev. A dated 2013-11-15
Drawing No. SLV 342A dated 2010-02-02
Drawing No. S1508739 Rev. A dated 2015-12-17
Drawing No. S1508747 Rev. A dated 2015-12-18
Drawing No. S1508746 Rev. A dated 2015-12-18
Drawing No. S1036417 Rev. A dated 2013-11-19
Drawing No. S1552357 Rev A dated 2020-02-12
Drawing No. S1552408 Rev A dated 2020-02-13
Drawing No. S1552430 Rev A dated 2020-02-13
Drawing No. S1508740 Rev. A dated 2015-12-17
Drawing No. S1508742 Rev. A dated 2015-12-18
Drawing No. S1508750 Rev. A dated 2015-12-18
Drawing No. S1508751 Rev. A dated 2015-12-18
Drawing No. S1553615 Rev. A dated 2020-03-13
Drawing No. S1516429 Rev. A dated 2016-10-17
Drawing No. S1585224 Rev. A dated 2022-11-08
Drawing No. S1586443 Rev. A dated 2022-11-29
Tests carried out
Tested in accordance with IMO 2010 FTP Code Part 3.
Marking of product
The product or packing is to be marked with name of manufacturer, type designation and fire-technical rating.
Periodical assessment
DNV’s surveyor is to be given permission to perform Periodical Assessments at any time during the validity of this
certificate and at least every second year. The arrangement is to be in accordance with procedure described in Class
Programme DNV-CP-0338, Section 4.
| Form code: TA 251 | Revision: 2022-12 | www.dnv.com | Page 6 of 6 |
|---|