TAF00001N7-optimized
TAF00001N7
Roxtec GK Firestop Sealing Kit, GK FS SK KIT sizes 89, 127, 140, 168, 200x150, 250x170, 219, 244,
DNV statutory interpretations DNV-SI-0364 – SOLAS interpretations, Edition July 2021
DNV rules for classification – Ships
DNV offshore standards
Approved for use as penetration system for approved ship cables in aluminium A60 class divisions
Product(s) approved by this certificate is/are accepted for installation on all vessels classed by DNV.
Issued at Hamburg on 2021-12-17
This Certificate is valid until 2026-12-16. Digitally Signed By: Schaarmann, Arne
DNV local station: Sweden CMC
Signing Date: 2021-12-17
Approval Engineer: Carsten Hunsalz
Arne Schaarmann
Form code: TA 251 Revision: 2021-03 www.dnv.com Page 1 of 3
Job Id: 262.1-036180-1
Certificate No: TAF00001N7
“GK FS SK sealing kit“ consisting of a fiberglass cloth with built in heat activated intumescent material to be wrapped
around cable bundles and fitted into circular or oval aluminium pipe sleeves. Folded back on each side with ends sealed
off to create a cold smoke tight seal and secured by metal cable ties.
“GK FS SK sealing kit“ is intended to be used for bundled cables or as a blank fire stop solution. The installation shall
be made in symmetrically welded or bolted pipe sleeves.
GK FS SK sealing kit ROUND A-60:
The coaming is welded or bolted symmetrically of the deck/bulkhead.
Installation details according drawings Roxtec No. S1566086, S1566087
Application Size Ø (mm) Length (mm) Tested Tested maximum Tested cable
minimum filling rate (%) maximum
filling rate diameter (mm)
Bulkhead 84 - 244 105 - 205 0 68 50
Deck 84 - 244 105 - 205 0 68 50
GK FS SK sealing kit OVAL A-60:
Application Size (mm) Length Tested Tested Tested cable
(Ø x L) (mm) minimum maximum maximum
filling rate filling rate diameter (mm)
Bulkhead 200x150 - 250x170 105 - 205 0 68 50
Deck 200x150 - 250x170 105 - 205 0 68 50
*Definition filing ratio:
Cable filing ratio = (The sum cross section of the cables) / (the inside cross section area of Coaming)
*Cross sectional of the cable=R2 x3.14
*R=Radius of Cable and the Seal.
Water- / Gas- tightness: Not applicable
Approved for use as a blank, single or multiple cables penetration system (combined in one or more cable bundles) in
class A-60 aluminium bulkheads and decks. Other applications are subject to case-by-case approval. Approved for use
in class A-0, A-15 and A-30 when the penetration system is insulated as A-60. In addition the division is to be insulated
with A-60 insulation at least 200 mm around the penetration.
Conformity. Each product is to be supplied with its actual manual for installation and use.
Maximum filling ratio of 68%.
In general approved maximum cable diameter: 50 mm.
The bolted sleeves shall be installed with screws + spring washer.
Sleeves with lengths L=105 to 205mm with or without intumescent strips can be used.
The systems must not be installed in bulkheads and decks if water- and gas- tightness is required.
Form code: TA 251 Revision: 2021-03 www.dnv.com Page 2 of 3
Each product is to be supplied with its manual for installation, use and maintenance.
Test Reports A60 Fire Class:
PGB10016A - A60 Aluminium Deck, date 2020-06-03, DBI Copenhagen Denmark,
RS-20/B-082/E – A60 Aluminium Bulkhead, Date 2020-04-21, CTO Gdansk, Poland
Test Reports Cold Smoke:
Roxtec No. 29092016-01, dated 2016-09-29; No. 22032017-01, dated 2017-03-22; No. 14122016-01,
dated 2016-12-14, 8P07092 A-class steel deck, SP Technical Research Institute of Sweden, 8P07094 A-class steel
Bulkhead, SP Technical Research Institute of Sweden
Installation Drawings:
Roxtec No. S1566086 dated 2021-04-14, S1566087 dated 2021-11-24
General Arrangement Drawings:
Roxtec No. S1543766 dated 2019-10-23, S1535797 dated 2019-10-22
Sleeve Drawings:
Roxtec No. S1535700 dated 2020-02-13, S1550433 dated 2019-12-17, S1540158 dated 2019-12-20
Fire Test acc. 2010 FTP Code, Annex 1: Part 3, IMO Resolution MSC.307(88)
DNV’s surveyor is to be given permission to perform Periodical Assessments at any time during the
validity of this certificate and at least every second year. The arrangement is to be in accordance with
procedure described in DNV-CP-0338 Section 4.
Form code: TA 251 Revision: 2021-03 www.dnv.com Page 3 of 3