Certificate no.:
TAF00001X6
that the Class H Penetration
Roxtec sealing system with multidiameter technology: RS-series (Sandwich panel)
issued to
DNV offshore standards
Application:
Approved for use as pipe penetration system in H-60 and H-120 class bulkheads.
Issued at Høvik on 2024-07-10
This Certificate is valid until 2029-07-09.
DNV local unit: Sweden CMC
Jowita Permoda
Approval Engineer: Marcin Tobiasz
| Form code: TA 251 | Revision: 2023-09 | www.dnv.com | Page 1 of 2 |
| Job ID: | 262.1-030113-3 | ||
| Certificate no.: | TAF00001X6 |
The RS pipe penetration seal consist of two halves with removable layers making it adaptable to pipes of different
diameters. It is available in different versions, RS, RS OMD, RS EMC or RS EX, depending on application.
The RS-seal is installed into a steel sleeve with flange, the sleeve is attached with self-drilling screws with washers to
the sandwich panel bulkhead together with counter frame. The steel sleeve is sealed with Roxtec Fire Sealant around
the perimeter.
For further details, see approved drawing listed below.
Additional Place of Production:
Roxtec Sealing System (Shanghai) Co,.Ltd Lingang Branch
Ground Floor A, No.875 QiuXin Road Zhongqilian (Lingang) Global Auto Parts Innovation Center, Shanghai, China.
Roxtec Saudi Arabia for Manufacturing LLC, 2634 - Ibn Sina Dist., Al Khobar 34627 – 6245, Al Khobar, Saudi Arabia
Approved for use as pipe penetration system in H-60 and H-120 class bulkheads. Other applications are subject to
case-by-case approval.
Approved for installation in H-60 and H-120 bulkhead sandwich panel type G21 (manufactured by InterDam) or similar
constructed H-class rated panels. The sandwich panel G21 was constructed with 170 mm thick insulation core (density
120 kg/m3) and 0.6 mm galvanized steel.
Table 1: Approved pipe penetration in H-120 bulkhead sandwich panels
| Pipes | Sleeve | Sleeve |
| Pipe | Sleeve | |
| Type | Size | diameter |
| type | position1) | |
| [mm] | [mm] | [mm] |
| Fully insulated on unexposed side | ||
| RS | 25 – 150 | Steel |
| (S1590730, No.2) | ||
| Fully insulated on one side and | ||
| RS | 25 | Steel |
| (S1590730, No.1) |
1) The steel sleeve is inserted into panel.
2) Restricted application: sleeve inserted from fire hazard side.
Table 2: Approved pipe penetration in H-60 bulkhead sandwich panels
| Pipe | Sleeve | |
| (S1590730, No.3) |
Test report No. RS-22/B-244/E dated 11 August 2022 from CTO, Gdansk, Poland
Drawing No. S1590730 Rev A dated 11 April 2023 from maker.
Tested according to IMO 2010 FTP Code Part 3 with the hydrocarbon time-temperature curve specified in EN 1363-2.
DNV surveyor is to be given permission to perform Periodical Assessments at any time during the validity of this
CP-0338 Section 4.
| Form code: TA 251 | Revision: 2023-09 | www.dnv.com | Page 2 of 2 |