W-N-8001-optimized

| 6/22/2021 | XHEZ7.W-N-8001 - Through-penetration Firestop Systems Certified for Canada | UL Product iQ |
|—|—|

XHEZ7.W-N-8001 - Through-penetration Firestop

Systems Certified for Canada

Design/System/Construction/Assembly Usage Disclaimer
Authorities Having Jurisdiction should be consulted in all cases as to the particular requirements covering the installation and
use of UL Certified products, equipment, system, devices, and materials.
Authorities Having Jurisdiction should be consulted before construction.
Fire resistance assemblies and products are developed by the design submitter and have been investigated by UL for
compliance with applicable requirements. The published information cannot always address every construction nuance

encountered in the field.

When field issues arise, it is recommended the first contact for assistance be the technical service staff provided by the product
manufacturer noted for the design. Users of fire resistance assemblies are advised to consult the general Guide Information for
each product category and each group of assemblies. The Guide Information includes specifics concerning alternate materials

and alternate methods of construction.

Only products which bear UL’s Mark are considered Certified.

Through-penetration Firestop Systems Certified for Canada

XHEZ - Through-penetration Firestop Systems

XHEZ7 - Through-penetration Firestop Systems Certified for

Canada

See General Information for Through-penetration Firestop Systems

See General Information for Through-penetration Firestop Systems Certified for Canada

System No. W-N-8001
June 16, 2021

ANSI/UL1479 (ASTM E814) CAN/ULC S115

| F Rating — 2 Hr | F Rating — 2 Hr |

| T Ratings — 0, 1 and 1-1/4 Hr (See Items 2 and 3A) | FT Ratings — 0, 1 and 1-1/4 Hr (See Items 2 and 3A) |

| L Rating At Ambient — Less Than 1 CFM per Device | FH Rating — 2 Hr |

| L Rating At 400°F — Less Than 1 CFM per Device | FTH Ratings — 0, 1 and 1-1/4 Hr (See Items 2 and 3A) |

L Rating At Ambient — Less Than 0.5 L/s Per Device

L Rating At 204°C — Less Than 0.5 L/s Per Device

https://iq.ulprospector.com/en/profile?e=3896887 1/3
6/22/2021 XHEZ7.W-N-8001 - Through-penetration Firestop Systems Certified for Canada
  1. Partition Panel Units* — The 2 hr fire rated composite wall assembly shall be constructed of nom 6 in. (152 mm) thick coated steel faced
    Partition Panel Units* (CJMR) installed in the manner specified in Wall and Partition Design No. U059 in the Fire Resistance Directory. Panel
    cutout sized to fit OD and depth of recessed device sleeve. Max diam of panel cutout is 9-1/64 in. (229 mm). Panel cutout of steel skin is required
    at both sides of opening. As an option, the steel skin cutout on side of wall opposite firestop device can be smaller and of sufficient size to
    accommodate the passing of the through penetrant. Panel cutout shall extend into the insulation core of the panel at one side of wall to
    accommodate the depth of the recessed firestop device sleeve. Opening can be located on or off panel unit joints. After installation of firestop
    device and through penetrant, retained cutout pieces of the insulation core are used to fill any visible voids between and around the penetrant to

be flush with face of wall.

DURASYSTEMS BARRIERS INC — DuraWall Panels

  1. Through-Penetrants — Within the loading area for the firestop device, the penetrants may represent a 0 to 100 percent visual fill, with max
    one penetrant installed through each elastomeric module within the device. Penetrants to be installed through the firestop device and the
    insulation core of the partition panel to pass through the opening. Penetrants to be rigidly supported on both sides of wall assembly.

A. Cables — The following cable types may be used:

A1. Max 350 kcmil (or smaller) copper conductor shielded or unshielded power cable with polyvinyl chloride (PVC) jacket and
ethylene-propylene rubber (EPR) insulation. When this cable is used, the T, FT and FTH Ratings are 1 hr.

A2. Max 24 pr 16 AWG (or smaller) copper conductor communication cable with polyvinyl chloride insulation and jacket
materials. When this cable is used, the T, FT and FTH Ratings are 1 hr.

B. Metallic Penetrants — The following types and sizes of metallic penetrants may be used:

B1. Nom 3/4 in. (19 mm) diam (or smaller) Sch 40 steel conduit. When this conduit is used, the T, FT and FTH Ratings are 1-

1/4 hr.

  1. Firestop System — The firestop system shall consist of the following:

A. Firestop Device* — Circular firestop device for use in precut or preformed openings, sized to the ID and depth of the recessed device
sleeve. The device is intended to be installed into the panel cutout at one side of wall with the circular flange of device installed flush
against steel skin of partition panel. Each device consists of an elastomeric insert, steel compression plates and multi diameter sealing
module(s). The square packing space of each device shall be filled with one or multiple rows of multi diameter elastomeric sealing
modules. The layers of the module are removed one by one until a max gap of 0.04 (1 mm) is formed between the two modules halves.
After installation of the device into the precut opening, the nuts of the compression plate are tightened to form an effective seal around

https://iq.ulprospector.com/en/profile?e=3896887 2/3
6/22/2021 XHEZ7.W-N-8001 - Through-penetration Firestop Systems Certified for Canada

the penetrating item Firestop device secured in place with min 1/4 in. (6 mm) diam by min 6-1/2 in. (165 mm) long washer head lag
screws within each preformed hole in device flange around periphery of opening and extending through full thickness of partition panel.
Firestop device installed in accordance with the accompanying installation instructions.

ROXTEC INTERNATIONAL AB — Types R-70, R-75, R-100, R-125, R-127, R-150, R-200 and their corresponding sleeves SLFR70, SLFR75,

SLFR100, SLFR125, SLFR127, SLFR150 and SLFR200.

ROXTEC INTERNATIONAL AB — Types R-70 ES, R-75 ES, R-100 ES, R-125 ES, R-127 ES, R-150 ES, R-200 ES and their corresponding
sleeves SLFR70, SLFR75, SLFR100, SLFR125, SLFR127, SLFR150 and SLFR200.

ROXTEC INC — Types R-100, R-127, R-150, R-200 and their corresponding sleeves SLFR100, SLFR127, SLFR150 and SLFR200.

Where RM EM B or RM PE B elastomeric sealing modules are used, T, FT and FTH Ratings are 0 Hr.

B. Fill, Void or Cavity Material* — Sealant — Nom 3/8 in. (10 mm) bead of fill material applied around the periphery of the firestop
device sleeve flange at the interface with the steel skin of the partition panel. In addition, for L Rating, sealant shall be applied on the
device sleeve flange to seal each screw head location.

See Fill, Void or Cavity Material (XHHW) category in the Fire Resistance Directory for the names of manufacturers. Any sealant or caulk
material meeting the above specification and bearing the UL Classification Marking may be used.

  • Indicates such products shall bear the UL or cUL Certification Mark for jurisdictions employing the UL or cUL Certification (such as
    Canada), respectively.

Last Updated on 2021-06-16

The appearance of a company’s name or product in this database does not in itself assure that products so identified have been manufactured
under UL’s Follow-Up Service. Only those products bearing the UL Mark should be considered to be Certified and covered under UL’s Follow-Up

Service. Always look for the Mark on the product.

UL permits the reproduction of the material contained in the Online Certification Directory subject to the following conditions: 1. The Guide
Information, Assemblies, Constructions, Designs, Systems, and/or Certifications (files) must be presented in their entirety and in a non-misleading
manner, without any manipulation of the data (or drawings). 2. The statement “Reprinted from the Online Certifications Directory with permission
from UL” must appear adjacent to the extracted material. In addition, the reprinted material must include a copyright notice in the following

format: “© 2021 UL LLC”